> It just means, that if you send a command to a slave at cycle n, the
> response to this command is visible in the process data in cycle n + 2,
> because reading and writing is done together at the beginning of each
> cycle.
>
Then again, if I understand correctly, the values should be available
at n+1, not n+2?
But I think the n+2 is exactly as we detected it.
When the loop was working at uniform 1kHz there was a delay ~3ms => 1
ms input delay due to sampling + 2 ms output delays. This is the
correct math?
This would indicate two options:
1. One has benefit to always run the I/O blocks at the maximum
possible sampling rate to minimize such delays.
2. One can make a double quick sample to get minimum output delay and
then wait for the normal "long" sampling rate. Such is the approach
for example in ADC in hard disk drive firmware.
>From Simulink point of view the first option is more simple perhaps,
but has slight overhead.
--
Julian Stoev, PhD.