Hello,
On Mon, Feb 01, 2010 at 03:54:50PM +0100, diplomarbeiter1 wrote:
> i am trying to set an alias adresses of some Beckhoff modules. The
> Ethercat bus has got 7 slaves, all wtih alias adress 0. Now i try
> e.g. to set the alias of slave no. 4 to 3. I use the Command-line Tool
> and write: ethercat alias -p4 3 But this comand will write the alias 3
> to all slaves behind the position 4. I can change a single alias with
> following command: ethercat alias -a4 55 but only when all Slaves have
> a single alias adress.
>
> My Question now, is it possible to set a single alias if all modules
> of the bus has the alias 0 using the Command-line Tool or the
> functions of ecrth.h?
Yes, this is what you are already doing. The output of „ethercat slaves“
displays a combined alias/relative position (see „ethercat slaves -h“):
$ ethercat alias -p4 3
$ ethercat sl
0 0:0 OP + EK1100 Ethernet Kopplerklemme (2A E-Bus)
1 0:1 OP + EL6002 Schnittstelle (RS232)
2 0:2 OP + EL6002 Schnittstelle (RS232)
3 0:3 OP + EL6002 Schnittstelle (RS232)
4 3:0 OP + cSI71A 2K. Ser. Schnittstelle (RS232)
5 3:1 PREOP + cAO71B 2K. Ana. Ausgang +/-10V
Only slave 4 has an alias set, all following slaves could be addressed
relatively to that slave. The numbers around the colon are the possible
„alias“ and „position“ arguments of ecrt_master_slave_config() (see API
doc, and the section „Slave Adressing“ in the PDF doc).
--
Best regards,
Florian Pose
http://etherlab.org