Am 31. März um 17:22 schrieb Günter Hammer:
> Thank you for your quick answer.
>
> It seems to work with the alias adressing.
> But there is a strange behaviour with the command line tool.
>
> If I call "ethercat config", i got the output i expected:
> # ethercat config
> 0:1 0x000012ad/0x03f03052 1 OP
> 0:2 0x000012ad/0x07d83052 2 OP
> 0:3 0x000012ad/0x04562c52 3 OP
> 1:0 0x000012ad/0x044c2c52 4 OP
> 1:1 0x000012ad/0x03f03052 5 OP
> 1:2 0x000012ad/0x07d83052 6 OP
> 1:3 0x000012ad/0x04562c52 7 OP
> 1:4 0x000012ad/0x044c2c52 8 OP
> 1:5 0x000012ad/0x03f03052 9 OP
> 1:6 0x000012ad/0x07d83052 10 OP
> 2:0 0x000012ad/0x044c2c52 11 OP
> 2:1 0x000012ad/0x03f03052 12 OP
> 2:2 0x000012ad/0x07d83052 13 OP
>
>
> But if i call "ethercat sl", i got the following output:
> # ethercat sl
> 0 0:0 OP + cEA70A EBus-Adapter (2A E-Bus)
> 1 0:1 OP + cDI73A 8K. Dig. Eingang 24V, 3ms
> 2 0:2 OP + cDO73A 8K. Dig. Ausgang 24V, 0.5A
> 3 0:3 OP + cEE70A EtherCAT-Verlaengerung
> 4 1:0 OP + cEC71A EtherCAT-Koppler (2A E-Bus)
> 5 1:0 OP + cDI73A 8K. Dig. Eingang 24V, 3ms
> 6 1:1 OP + cDO73A 8K. Dig. Ausgang 24V, 0.5A
> 7 1:2 OP + cEE70A EtherCAT-Verlaengerung
> 8 1:3 OP + cEC71A EtherCAT-Koppler (2A E-Bus)
> 9 1:4 OP + cDI73A 8K. Dig. Eingang 24V, 3ms
> 10 1:5 OP + cDO73A 8K. Dig. Ausgang 24V, 0.5A
> 11 2:0 OP + cEC71A EtherCAT-Koppler (2A E-Bus)
> 12 2:1 OP + cDI73A 8K. Dig. Eingang 24V, 3ms
> 13 2:2 OP + cDO73A 8K. Dig. Ausgang 24V, 0.5A
>
> Slave 4 and 5 have the same alias and position and the following slaves of
> alias 1 are
> 1 position below the expected.
> Perhaps only an output error.
It looks as slave 4 and 5 both have the alias 1 programmed. Have a look
at the output of 'ethercat sii_read', word 4.
--
Best regards,
Florian Pose