>>> - Which NIC driver do you use?
>>
>> root at rtai:~/ethercat-default/examples/dc_rtai# lspci
>> ...
>> ___01:01.0 Ethernet controller: Intel Corporation 82547GI Gigabit   
>> Ethernet Controller___
>> 02:08.0 Ethernet controller: Intel Corporation 82801EB/ER   
>> (ICH5/ICH5R) integrated LAN Controller (rev 02)
>> ...
>>
> If you have the possibility please take a Realtec NIC
I'm looking for even though I have not
>
>
>>> - Which etherlab master version do you use?
>>
>> root at rtai:~/ethercat-default/examples/dc_rtai# ethercat version
>> IgH EtherCAT master devel afb40fd6018e
>>
>> after this commit:
>> author    Florian Pose <fp at igh-essen.com>
>> Thu Sep 22 16:52:54 2011 +0200 (7 weeks ago)
>
> Please take the stable branch
>
> do a hg clone of the reposiroy
>
> hg up stable-1.5
> ./boostrap
> ./configure .........
Now work with the stable version (1.5), kernel 2.6.28, rtai 3.8.1
>
>>> - Which slave do you want to use?
>>
>> I tried with 4 slaves, EL2004, EL1004, EL3102 and EL4132
>>
> Please note, these slave does not support DC, That is the reason for OP Mode.
Now only test with EL3102 and EL4132
>>>
>>> About OP State
>>>
>>> try to set
>>>
>>> ethercat debug 1
>>>
>>> and start your application and post the dmesg output.
I'm still having problems. I configure dc_rtai example with the  
modules EL3102 and EL4132 (Beckhoff according to whether they support  
DC), and only one set to OP state.
dmesg output:
EtherCAT 0: Slave states: PREOP.
ec_dc_rtai_sample: Starting...
EtherCAT: Requesting master 0...
EtherCAT DEBUG 0: IDLE -> OPERATION.
EtherCAT: Successfully requested master 0.
EtherCAT DEBUG 0: ecrt_master_callbacks(master = 0xf71e7800, send_cb =  
0xf881b020, receive_cb = 0xf881b000, cb_data = 0xf71e7800)
ec_dc_rtai_sample: Registering domain...
EtherCAT DEBUG 0: ecrt_master_create_domain(master = 0xf71e7800)
EtherCAT DEBUG 0: Created domain 0.
ec_dc_rtai_sample: Configuring PDOs...
EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xf71e7800, alias  
= 0, position = 0, vendor_id = 0x00000002, product_code = 0x044d2c52)
EtherCAT DEBUG 0: Creating slave configuration for 0:0, 0x00000002/0x044D2C52.
EtherCAT DEBUG 0 0:0: Attached slave 0.
EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xf71e7800, alias  
= 0, position = 3, vendor_id = 0x00000002, product_code = 0x0c1e3052)
EtherCAT DEBUG 0: Creating slave configuration for 0:3, 0x00000002/0x0C1E3052.
EtherCAT DEBUG 0 0:3: Attached slave 3.
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdos(sc = 0xf72a5400, n_syncs  
= 4294967295, syncs = 0xf881c320)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_sync_manager(sc = 0xf72a5400,  
sync_index = 2, dir = 1, watchdog_mode = 0)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_sync_manager(sc = 0xf72a5400,  
sync_index = 3, dir = 2, watchdog_mode = 0)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_assign_clear(sc =  
0xf72a5400, sync_index = 3)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_assign_add(sc =  
0xf72a5400, sync_index = 3, pdo_index = 0x1A00)
EtherCAT DEBUG 0 0:3: Loading default mapping for PDO 0x1A00.
EtherCAT DEBUG 0 0:3: Found PDO name "TxPDO-Map Channel 1".
EtherCAT DEBUG 0 0:3: Entry 0x3101:01.
EtherCAT DEBUG 0 0:3: Entry 0x3101:02.
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_clear(sc =  
0xf72a5400, pdo_index = 0x1A00)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5400, pdo_index = 0x1A00, entry_index = 0x3101, entry_subindex =  
0x01, entry_bit_length = 8)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5400, pdo_index = 0x1A00, entry_index = 0x3101, entry_subindex =  
0x02, entry_bit_length = 16)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_assign_add(sc =  
0xf72a5400, sync_index = 3, pdo_index = 0x1A01)
EtherCAT DEBUG 0 0:3: Loading default mapping for PDO 0x1A01.
EtherCAT DEBUG 0 0:3: Found PDO name "TxPDO-Map Channel 2".
EtherCAT DEBUG 0 0:3: Entry 0x3102:01.
EtherCAT DEBUG 0 0:3: Entry 0x3102:02.
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_clear(sc =  
0xf72a5400, pdo_index = 0x1A01)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5400, pdo_index = 0x1A01, entry_index = 0x3102, entry_subindex =  
0x01, entry_bit_length = 8)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5400, pdo_index = 0x1A01, entry_index = 0x3102, entry_subindex =  
0x02, entry_bit_length = 16)
EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xf71e7800, alias  
= 0, position = 4, vendor_id = 0x00000002, product_code = 0x10243052)
EtherCAT DEBUG 0: Creating slave configuration for 0:4, 0x00000002/0x10243052.
EtherCAT DEBUG 0 0:4: Attached slave 4.
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdos(sc = 0xf72a5000, n_syncs  
= 4294967295, syncs = 0xf881c360)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_sync_manager(sc = 0xf72a5000,  
sync_index = 2, dir = 1, watchdog_mode = 0)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_assign_clear(sc =  
0xf72a5000, sync_index = 2)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_assign_add(sc =  
0xf72a5000, sync_index = 2, pdo_index = 0x1600)
EtherCAT DEBUG 0 0:4: Loading default mapping for PDO 0x1600.
EtherCAT DEBUG 0 0:4: Found PDO name "RxPDO 01 mapping".
EtherCAT DEBUG 0 0:4: Entry 0x3001:01.
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_mapping_clear(sc =  
0xf72a5000, pdo_index = 0x1600)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5000, pdo_index = 0x1600, entry_index = 0x3001, entry_subindex =  
0x01, entry_bit_length = 16)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_assign_add(sc =  
0xf72a5000, sync_index = 2, pdo_index = 0x1601)
EtherCAT DEBUG 0 0:4: Loading default mapping for PDO 0x1601.
EtherCAT DEBUG 0 0:4: Found PDO name "RxPDO 02 mapping".
EtherCAT DEBUG 0 0:4: Entry 0x3002:01.
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_mapping_clear(sc =  
0xf72a5000, pdo_index = 0x1601)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_pdo_mapping_add(sc =  
0xf72a5000, pdo_index = 0x1601, entry_index = 0x3002, entry_subindex =  
0x01, entry_bit_length = 16)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_sync_manager(sc = 0xf72a5000,  
sync_index = 3, dir = 2, watchdog_mode = 0)
ec_dc_rtai_sample: Registering PDO entries...
EtherCAT DEBUG 0: ecrt_domain_reg_pdo_entry_list(domain = 0xf726dfc0,  
regs = 0xf881b400)
EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xf71e7800, alias  
= 0, position = 3, vendor_id = 0x00000002, product_code = 0x0c1e3052)
EtherCAT DEBUG 0 0:3: ecrt_slave_config_reg_pdo_entry(sc = 0xf72a5400,  
index = 0x3101, subindex = 0x02, domain = 0xf726dfc0, bit_position =  
0x00000000)
EtherCAT DEBUG 0: Domain 0: Added 6 bytes, total 6.
EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xf71e7800, alias  
= 0, position = 4, vendor_id = 0x00000002, product_code = 0x10243052)
EtherCAT DEBUG 0 0:4: ecrt_slave_config_reg_pdo_entry(sc = 0xf72a5000,  
index = 0x3001, subindex = 0x01, domain = 0xf726dfc0, bit_position =  
0x00000000)
EtherCAT DEBUG 0: Domain 0: Added 4 bytes, total 10.
EtherCAT DEBUG 0 0:4: ecrt_slave_config_dc(sc = 0xf72a5000,  
assign_activate = 0x0700, sync0_cycle = 1000000, sync0_shift = 440000,  
sync1_cycle = 0, sync1_shift = 0
ec_dc_rtai_sample: Activating master...
EtherCAT DEBUG 0: ecrt_master_activate(master = 0xf71e7800)
EtherCAT 0: Domain0: Logical address 0x00000000, 10 byte, expected  
working counter 3.
EtherCAT 0:   Datagram domain0-0: Logical offset 0x00000000, 10 byte,  
type LRW.
EtherCAT DEBUG 0: Stopping master thread.
EtherCAT DEBUG 0: Master IDLE thread exiting...
EtherCAT 0: Master thread exited.
EtherCAT DEBUG 0: FSM datagram is f71e7be0.
EtherCAT 0: Starting EtherCAT-OP thread.
ec_dc_rtai_sample: Starting cyclic sample thread...
ec_dc_rtai_sample: RT timer started with 8333/8334 ticks.
ec_dc_rtai_sample: Initialized.
EtherCAT DEBUG 0: Operation thread running with fsm interval = 4000  
us, max data size=45000
EtherCAT WARNING 0: 1 datagram UNMATCHED!
ec_dc_rtai_sample: 5 slave(s).
ec_dc_rtai_sample: AL states: 0x02.
ec_dc_rtai_sample: Link is up.
EtherCAT DEBUG 0: Configuration changed.
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0-0: DC system time offset calculation:  
system_time=690111306919 (corrected with 4000000),  
app_time=374670051569305000, diff=374669361457998081
EtherCAT DEBUG 0-0: Setting time offset to 374669361457998081 (was 0)
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0-1: DC system time offset calculation:  
system_time=690119275624 (corrected with 4000000),  
app_time=374670051577305000, diff=374669361458029376
EtherCAT DEBUG 0-1: Setting time offset to 374669361458029376 (was 0)
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0-2: DC system time offset calculation:  
system_time=690127578636 (corrected with 4000000),  
app_time=374670051585305000, diff=374669361457726364
EtherCAT DEBUG 0-2: Setting time offset to 374669361457726364 (was 0)
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0-3: DC system time offset calculation:  
system_time=690017575368 (corrected with 4000000),  
app_time=374670051593305000, diff=374669361575729632
EtherCAT DEBUG 0-3: Setting time offset to 374669361575729632 (was 0)
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0-4: DC system time offset calculation:  
system_time=690143304364 (corrected with 4000000),  
app_time=374670051601305000, diff=374669361458000636
EtherCAT DEBUG 0-4: Setting time offset to 374669361458000636 (was 0)
EtherCAT DEBUG 0: Writing system time offsets...
EtherCAT DEBUG 0: Requesting OP...
EtherCAT DEBUG 0-0: Changing state from PREOP to OP.
EtherCAT DEBUG 0-0: Configuring...
EtherCAT DEBUG 0-0: Now in INIT.
EtherCAT DEBUG 0-0: Clearing FMMU configurations...
EtherCAT DEBUG 0-0: Clearing sync manager configurations...
EtherCAT DEBUG 0-0: Clearing DC assignment...
EtherCAT DEBUG 0-0: Slave does not support mailbox communication.
EtherCAT DEBUG 0-0: Now in PREOP.
EtherCAT DEBUG 0-0: SM0: Addr 0x1000, Size   2, Ctrl 0x00, En 0
EtherCAT DEBUG 0-0: Now in SAFEOP.
EtherCAT DEBUG 0-0: Now in OP. Finished configuration.
EtherCAT DEBUG 0-3: Changing state from PREOP to OP.
EtherCAT DEBUG 0-3: Configuring...
EtherCAT DEBUG 0-3: Now in INIT.
EtherCAT DEBUG 0-3: Clearing FMMU configurations...
EtherCAT DEBUG 0-3: Clearing sync manager configurations...
EtherCAT DEBUG 0-3: Clearing DC assignment...
EtherCAT DEBUG 0-3: Configuring mailbox sync managers...
EtherCAT DEBUG 0-3: SM0: Addr 0x1000, Size 128, Ctrl 0x26, En 1
EtherCAT DEBUG 0-3: SM1: Addr 0x1080, Size 128, Ctrl 0x22, En 1
EtherCAT DEBUG 0-3: Now in PREOP.
EtherCAT DEBUG 0-3: Setting PDO assignment of SM2:
EtherCAT DEBUG 0-3: Currently assigned PDOs: (none). PDOs to assign: (none)
EtherCAT DEBUG 0-3: Setting number of assigned PDOs to zero.
EtherCAT DEBUG 0-3: Downloading SDO 0x1C12:00.
EtherCAT DEBUG: 00
EtherCAT DEBUG 0-3: Expedited download request:
EtherCAT DEBUG: 00 20 2F 12 1C 00 00 00 00 00
EtherCAT DEBUG 0-3: Download response:
EtherCAT DEBUG: 00 30 60 12 1C 00 00 00 00 00
EtherCAT DEBUG 0-3: Setting PDO assignment of SM3:
EtherCAT DEBUG 0-3: Currently assigned PDOs: 0x1A00 0x1A01. PDOs to  
assign: 0x1A00 0x1A01
EtherCAT DEBUG 0-3: Setting number of assigned PDOs to zero.
EtherCAT DEBUG 0-3: Downloading SDO 0x1C13:00.
EtherCAT DEBUG: 00
EtherCAT DEBUG 0-3: Expedited download request:
EtherCAT DEBUG: 00 20 2F 13 1C 00 00 00 00 00
EtherCAT DEBUG 0-3: Download response:
EtherCAT DEBUG: 00 30 60 13 1C 00 00 00 00 00
EtherCAT DEBUG 0-3: Assigning PDO 0x1A00 at position 1.
EtherCAT DEBUG 0-3: Downloading SDO 0x1C13:01.
EtherCAT DEBUG: 00 1A
EtherCAT DEBUG 0-3: Expedited download request:
EtherCAT DEBUG: 00 20 2B 13 1C 01 00 1A 00 00
EtherCAT DEBUG 0-3: Download response:
EtherCAT DEBUG: 00 30 60 13 1C 01 00 1A 00 00
EtherCAT DEBUG 0-3: Assigning PDO 0x1A01 at position 2.
EtherCAT DEBUG 0-3: Downloading SDO 0x1C13:02.
EtherCAT DEBUG: 01 1A
EtherCAT DEBUG 0-3: Expedited download request:
EtherCAT DEBUG: 00 20 2B 13 1C 02 01 1A 00 00
EtherCAT DEBUG 0-3: Download response:
EtherCAT DEBUG: 00 30 60 13 1C 02 01 1A 00 00
EtherCAT DEBUG 0-3: Setting number of assigned PDOs to 2.
EtherCAT DEBUG 0-3: Downloading SDO 0x1C13:00.
EtherCAT DEBUG: 02
EtherCAT DEBUG 0-3: Expedited download request:
EtherCAT DEBUG: 00 20 2F 13 1C 00 02 00 00 00
EtherCAT DEBUG 0-3: Download response:
EtherCAT DEBUG: 00 30 60 13 1C 00 02 00 00 00
EtherCAT DEBUG 0-3: Successfully configured PDO assignment of SM3.
EtherCAT DEBUG 0-3: SM2: Addr 0x1100, Size   0, Ctrl 0x04, En 0
EtherCAT DEBUG 0-3: SM3: Addr 0x1180, Size   6, Ctrl 0x20, En 1
EtherCAT DEBUG 0 0:3: FMMU: LogAddr 0x00000000, Size   6, PhysAddr  
0x1180, SM3, Dir in
EtherCAT 0: Domain 0: Working counter changed to 1/3.
ec_dc_rtai_sample: Domain1: WC 1.
ec_dc_rtai_sample: Domain1: State 1.
EtherCAT DEBUG 0-3: Now in SAFEOP.
EtherCAT DEBUG 0-3: Now in OP. Finished configuration.
EtherCAT DEBUG 0-4: Changing state from PREOP to OP.
EtherCAT DEBUG 0-4: Configuring...
EtherCAT DEBUG 0-4: Now in INIT.
EtherCAT DEBUG 0-4: Clearing FMMU configurations...
EtherCAT DEBUG 0-4: Clearing sync manager configurations...
EtherCAT DEBUG 0-4: Clearing DC assignment...
EtherCAT DEBUG 0-4: Configuring mailbox sync managers...
EtherCAT DEBUG 0-4: SM0: Addr 0x1800, Size 246, Ctrl 0x26, En 1
EtherCAT DEBUG 0-4: SM1: Addr 0x18F6, Size 246, Ctrl 0x22, En 1
EtherCAT DEBUG 0-4: Now in PREOP.
EtherCAT DEBUG 0-4: Setting PDO assignment of SM2:
EtherCAT DEBUG 0-4: Currently assigned PDOs: 0x1600 0x1601. PDOs to  
assign: 0x1600 0x1601
EtherCAT DEBUG 0-4: Setting number of assigned PDOs to zero.
EtherCAT DEBUG 0-4: Downloading SDO 0x1C12:00.
EtherCAT DEBUG: 00
EtherCAT DEBUG 0-4: Expedited download request:
EtherCAT DEBUG: 00 20 2F 12 1C 00 00 00 00 00
EtherCAT DEBUG 0-4: Download response:
EtherCAT DEBUG: 00 30 60 12 1C 00 00 00 00 00
EtherCAT DEBUG 0-4: Assigning PDO 0x1600 at position 1.
EtherCAT DEBUG 0-4: Downloading SDO 0x1C12:01.
EtherCAT DEBUG: 00 16
EtherCAT DEBUG 0-4: Expedited download request:
EtherCAT DEBUG: 00 20 2B 12 1C 01 00 16 00 00
EtherCAT DEBUG 0-4: Download response:
EtherCAT DEBUG: 00 30 60 12 1C 01 00 16 00 00
EtherCAT DEBUG 0-4: Assigning PDO 0x1601 at position 2.
EtherCAT DEBUG 0-4: Downloading SDO 0x1C12:02.
EtherCAT DEBUG: 01 16
EtherCAT DEBUG 0-4: Expedited download request:
EtherCAT DEBUG: 00 20 2B 12 1C 02 01 16 00 00
EtherCAT DEBUG 0-4: Download response:
EtherCAT DEBUG: 00 30 60 12 1C 02 01 16 00 00
EtherCAT DEBUG 0-4: Setting number of assigned PDOs to 2.
EtherCAT DEBUG 0-4: Downloading SDO 0x1C12:00.
EtherCAT DEBUG: 02
EtherCAT DEBUG 0-4: Expedited download request:
EtherCAT DEBUG: 00 20 2F 12 1C 00 02 00 00 00
EtherCAT DEBUG 0-4: Download response:
EtherCAT DEBUG: 00 30 60 12 1C 00 02 00 00 00
EtherCAT DEBUG 0-4: Successfully configured PDO assignment of SM2.
EtherCAT DEBUG 0-4: Setting PDO assignment of SM3:
EtherCAT DEBUG 0-4: Currently assigned PDOs: (none). PDOs to assign: (none)
EtherCAT DEBUG 0-4: Setting number of assigned PDOs to zero.
EtherCAT DEBUG 0-4: Downloading SDO 0x1C13:00.
EtherCAT DEBUG: 00
EtherCAT DEBUG 0-4: Expedited download request:
EtherCAT DEBUG: 00 20 2F 13 1C 00 00 00 00 00
EtherCAT DEBUG 0-4: Download response:
EtherCAT DEBUG: 00 30 60 13 1C 00 00 00 00 00
EtherCAT DEBUG 0-4: SM2: Addr 0x1000, Size   4, Ctrl 0x24, En 1
EtherCAT DEBUG 0-4: SM3: Addr 0x1100, Size   0, Ctrl 0x20, En 0
EtherCAT DEBUG 0 0:4: FMMU: LogAddr 0x00000006, Size   4, PhysAddr  
0x1000, SM2, Dir out
EtherCAT DEBUG 0-4: Setting DC cycle times to 1000000 / 0.
EtherCAT DEBUG 0-4: Checking for synchrony.
EtherCAT DEBUG 0-4: Sync after    0 ms:      61880 ns
EtherCAT DEBUG 0-4: Sync after    0 ms:      55294 ns
EtherCAT DEBUG 0-4: Sync after    4 ms:      49503 ns
EtherCAT DEBUG 0-4: Sync after    4 ms:      44413 ns
EtherCAT DEBUG 0-4: Sync after    8 ms:      39938 ns
EtherCAT DEBUG 0-4: Sync after    8 ms:      36001 ns
EtherCAT DEBUG 0-4: Sync after   12 ms:      32542 ns
EtherCAT DEBUG 0-4: Sync after   12 ms:      29500 ns
EtherCAT DEBUG 0-4: Sync after   16 ms:      26825 ns
EtherCAT DEBUG 0-4: Sync after   16 ms:      24472 ns
EtherCAT DEBUG 0-4: Sync after   20 ms:      22403 ns
EtherCAT DEBUG 0-4: Sync after   20 ms:      20583 ns
EtherCAT DEBUG 0-4: Sync after   24 ms:      18982 ns
EtherCAT DEBUG 0-4: Sync after   24 ms:      17574 ns
EtherCAT DEBUG 0-4: Sync after   28 ms:      16334 ns
EtherCAT DEBUG 0-4: Sync after   28 ms:      15244 ns
EtherCAT DEBUG 0-4: Sync after   32 ms:      14283 ns
EtherCAT DEBUG 0-4: Sync after   32 ms:      13438 ns
EtherCAT DEBUG 0-4: Sync after   36 ms:      12694 ns
EtherCAT DEBUG 0-4: Sync after   36 ms:      12038 ns
EtherCAT DEBUG 0-4: Sync after   40 ms:      11460 ns
EtherCAT DEBUG 0-4: Sync after   40 ms:      10951 ns
EtherCAT DEBUG 0-4: Sync after   44 ms:      10502 ns
EtherCAT DEBUG 0-4: Sync after   44 ms:      10106 ns
EtherCAT DEBUG 0-4: Sync after   48 ms:       9755 ns
EtherCAT DEBUG 0-4: Sync after   48 ms:       9447 ns
EtherCAT DEBUG 0-4: Sync after   52 ms:       9174 ns
EtherCAT DEBUG 0-4: Sync after   52 ms:       8933 ns
EtherCAT DEBUG 0-4: Sync after   56 ms:       8718 ns
EtherCAT DEBUG 0-4: Sync after   56 ms:       8529 ns
EtherCAT DEBUG 0-4: Sync after   60 ms:       8361 ns
EtherCAT DEBUG 0-4: Sync after   60 ms:       8212 ns
EtherCAT DEBUG 0-4: Sync after   64 ms:       8079 ns
EtherCAT DEBUG 0-4: Sync after   64 ms:       7960 ns
EtherCAT DEBUG 0-4: Sync after   68 ms:       7854 ns
EtherCAT DEBUG 0-4: Sync after   68 ms:       7760 ns
EtherCAT DEBUG 0-4: Sync after   72 ms:       7675 ns
EtherCAT DEBUG 0-4: Sync after   72 ms:       7599 ns
EtherCAT DEBUG 0-4: Sync after   76 ms:       7531 ns
EtherCAT DEBUG 0-4: Sync after   76 ms:       7469 ns
EtherCAT DEBUG 0-4: Sync after   80 ms:       7414 ns
EtherCAT DEBUG 0-4: Sync after   80 ms:       7362 ns
EtherCAT DEBUG 0-4: Sync after   84 ms:       7316 ns
EtherCAT DEBUG 0-4: Sync after   84 ms:       7274 ns
EtherCAT DEBUG 0-4: Sync after   88 ms:       7236 ns
EtherCAT DEBUG 0-4: Sync after   88 ms:       7199 ns
EtherCAT DEBUG 0-4: Sync after   92 ms:       7166 ns
EtherCAT DEBUG 0-4: Sync after   92 ms:       7136 ns
EtherCAT DEBUG 0-4: Sync after   96 ms:       7106 ns
EtherCAT DEBUG 0-4: Sync after   96 ms:       7079 ns
EtherCAT DEBUG 0-4: Sync after  100 ms:       7053 ns
EtherCAT DEBUG 0-4: Sync after  100 ms:       7029 ns
EtherCAT DEBUG 0-4: Sync after  104 ms:       7006 ns
EtherCAT DEBUG 0-4: Sync after  104 ms:       6984 ns
EtherCAT DEBUG 0-4: Sync after  108 ms:       6963 ns
EtherCAT DEBUG 0-4: Sync after  108 ms:       6943 ns
EtherCAT DEBUG 0-4: Sync after  112 ms:       6923 ns
EtherCAT DEBUG 0-4: Sync after  112 ms:       6904 ns
EtherCAT DEBUG 0-4: Sync after  116 ms:       6885 ns
EtherCAT DEBUG 0-4: Sync after  116 ms:       6867 ns
EtherCAT DEBUG 0-4: Sync after  120 ms:       6849 ns
EtherCAT DEBUG 0-4: Sync after  120 ms:       6832 ns
EtherCAT DEBUG 0-4: Sync after  124 ms:       6814 ns
EtherCAT DEBUG 0-4: Sync after  124 ms:       6798 ns
EtherCAT DEBUG 0-4: Sync after  128 ms:       6781 ns
EtherCAT DEBUG 0-4: Sync after  128 ms:       6764 ns
EtherCAT DEBUG 0-4: Sync after  132 ms:       6747 ns
EtherCAT DEBUG 0-4: Sync after  132 ms:       6731 ns
EtherCAT DEBUG 0-4: Sync after  136 ms:       6715 ns
EtherCAT DEBUG 0-4: Sync after  136 ms:       6699 ns
EtherCAT DEBUG 0-4: Sync after  140 ms:       6682 ns
EtherCAT DEBUG 0-4: Sync after  140 ms:       6667 ns
EtherCAT DEBUG 0-4: Sync after  144 ms:       6650 ns
EtherCAT DEBUG 0-4: Sync after  144 ms:       6635 ns
EtherCAT DEBUG 0-4: Sync after  148 ms:       6618 ns
EtherCAT DEBUG 0-4: Sync after  148 ms:       6602 ns
EtherCAT DEBUG 0-4: Sync after  152 ms:       6585 ns
EtherCAT DEBUG 0-4: Sync after  152 ms:       6569 ns
EtherCAT DEBUG 0-4: Sync after  156 ms:       6553 ns
EtherCAT DEBUG 0-4: Sync after  156 ms:       6536 ns
EtherCAT DEBUG 0-4: Sync after  160 ms:       6521 ns
EtherCAT DEBUG 0-4: Sync after  160 ms:       6505 ns
EtherCAT DEBUG 0-4: Sync after  164 ms:       6488 ns
EtherCAT DEBUG 0-4: Sync after  164 ms:       6472 ns
EtherCAT DEBUG 0-4: Sync after  168 ms:       6455 ns
EtherCAT DEBUG 0-4: Sync after  168 ms:       6438 ns
EtherCAT DEBUG 0-4: Sync after  172 ms:       6422 ns
EtherCAT DEBUG 0-4: Sync after  172 ms:       6405 ns
EtherCAT DEBUG 0-4: Sync after  176 ms:       6389 ns
EtherCAT DEBUG 0-4: Sync after  176 ms:       6372 ns
EtherCAT DEBUG 0-4: Sync after  180 ms:       6355 ns
EtherCAT DEBUG 0-4: Sync after  180 ms:       6337 ns
EtherCAT DEBUG 0-4: Sync after  184 ms:       6322 ns
EtherCAT DEBUG 0-4: Sync after  184 ms:       6304 ns
EtherCAT DEBUG 0-4: Sync after  188 ms:       6288 ns
EtherCAT DEBUG 0-4: Sync after  188 ms:       6271 ns
EtherCAT DEBUG 0-4: Sync after  192 ms:       6253 ns
EtherCAT DEBUG 0-4: Sync after  192 ms:       6236 ns
EtherCAT DEBUG 0-4: Sync after  196 ms:       6219 ns
EtherCAT DEBUG 0-4: Sync after  196 ms:       6201 ns
EtherCAT DEBUG 0-4: Sync after  200 ms:       6184 ns
EtherCAT DEBUG 0-4: Sync after  200 ms:       6165 ns
EtherCAT DEBUG 0-4: Sync after  204 ms:       6148 ns
EtherCAT DEBUG 0-4: Sync after  204 ms:       6131 ns
EtherCAT DEBUG 0-4: Sync after  208 ms:       6114 ns
EtherCAT DEBUG 0-4: Sync after  208 ms:       6096 ns
EtherCAT DEBUG 0-4: Sync after  212 ms:       6078 ns
EtherCAT DEBUG 0-4: Sync after  212 ms:       6060 ns
EtherCAT DEBUG 0-4: Sync after  216 ms:       6041 ns
EtherCAT DEBUG 0-4: Sync after  216 ms:       6024 ns
EtherCAT DEBUG 0-4: Sync after  220 ms:       6005 ns
EtherCAT DEBUG 0-4: Sync after  220 ms:       5987 ns
EtherCAT DEBUG 0-4: Sync after  224 ms:       5968 ns
EtherCAT DEBUG 0-4: Sync after  224 ms:       5950 ns
EtherCAT DEBUG 0-4: Sync after  228 ms:       5932 ns
EtherCAT DEBUG 0-4: Sync after  228 ms:       5913 ns
EtherCAT DEBUG 0-4: Sync after  232 ms:       5895 ns
EtherCAT DEBUG 0-4: Sync after  232 ms:       5876 ns
EtherCAT DEBUG 0-4: Sync after  236 ms:       5857 ns
EtherCAT DEBUG 0-4: Sync after  236 ms:       5838 ns
EtherCAT DEBUG 0-4: Sync after  240 ms:       5819 ns
EtherCAT DEBUG 0-4: Sync after  240 ms:       5801 ns
EtherCAT DEBUG 0-4: Sync after  244 ms:       5781 ns
EtherCAT DEBUG 0-4: Sync after  244 ms:       5762 ns
EtherCAT DEBUG 0-4: Sync after  248 ms:       5743 ns
EtherCAT DEBUG 0-4: Sync after  248 ms:       5724 ns
EtherCAT DEBUG 0-4: Sync after  252 ms:       5705 ns
EtherCAT DEBUG 0-4: Sync after  252 ms:       5684 ns
EtherCAT DEBUG 0-4: Sync after  256 ms:       5666 ns
EtherCAT DEBUG 0-4: Sync after  256 ms:       5646 ns
EtherCAT DEBUG 0-4: Sync after  260 ms:       5627 ns
EtherCAT DEBUG 0-4: Sync after  260 ms:       5607 ns
EtherCAT DEBUG 0-4: Sync after  264 ms:       5587 ns
EtherCAT DEBUG 0-4: Sync after  264 ms:       5567 ns
EtherCAT DEBUG 0-4: Sync after  268 ms:       5548 ns
EtherCAT DEBUG 0-4: Sync after  268 ms:       5527 ns
EtherCAT DEBUG 0-4: Sync after  272 ms:       5507 ns
EtherCAT DEBUG 0-4: Sync after  272 ms:       5487 ns
EtherCAT DEBUG 0-4: Sync after  276 ms:       5468 ns
EtherCAT DEBUG 0-4: Sync after  276 ms:       5447 ns
EtherCAT DEBUG 0-4: Sync after  280 ms:       5427 ns
EtherCAT DEBUG 0-4: Sync after  280 ms:       5406 ns
EtherCAT DEBUG 0-4: Sync after  284 ms:       5385 ns
EtherCAT DEBUG 0-4: Sync after  284 ms:       5365 ns
EtherCAT DEBUG 0-4: Sync after  288 ms:       5345 ns
EtherCAT DEBUG 0-4: Sync after  288 ms:       5325 ns
EtherCAT DEBUG 0-4: Sync after  292 ms:       5303 ns
EtherCAT DEBUG 0-4: Sync after  292 ms:       5282 ns
EtherCAT DEBUG 0-4: Sync after  296 ms:       5261 ns
EtherCAT DEBUG 0-4: Sync after  296 ms:       5240 ns
EtherCAT DEBUG 0-4: Sync after  300 ms:       5219 ns
EtherCAT DEBUG 0-4: Sync after  300 ms:       5198 ns
EtherCAT DEBUG 0-4: Sync after  304 ms:       5177 ns
EtherCAT DEBUG 0-4: Sync after  304 ms:       5156 ns
EtherCAT DEBUG 0-4: Sync after  308 ms:       5135 ns
EtherCAT DEBUG 0-4: Sync after  308 ms:       5114 ns
EtherCAT DEBUG 0-4: Sync after  312 ms:       5092 ns
EtherCAT DEBUG 0-4: Sync after  312 ms:       5070 ns
EtherCAT DEBUG 0-4: Sync after  316 ms:       5048 ns
EtherCAT DEBUG 0-4: Sync after  316 ms:       5027 ns
EtherCAT DEBUG 0-4: Sync after  320 ms:       5005 ns
EtherCAT DEBUG 0-4: 4983 ns difference after 320 ms.
EtherCAT DEBUG 0-4: app_start_time=374670051565305000
EtherCAT DEBUG 0-4:       app_time=374670052085305000
EtherCAT DEBUG 0-4:     start_time=374670052185305000
EtherCAT DEBUG 0-4:     cycle_time=1000000
EtherCAT DEBUG 0-4:     shift_time=440000
EtherCAT DEBUG 0-4:      remainder=0
EtherCAT DEBUG 0-4:          start=374670052186745000
EtherCAT DEBUG 0-4: Setting DC cyclic operation start time to  
374670052186745000.
EtherCAT DEBUG 0-4: Setting DC AssignActivate to 0x0700.
ec_dc_rtai_sample: Domain1: WC 3.
ec_dc_rtai_sample: Domain1: State 2.
EtherCAT DEBUG 0-4: Now in SAFEOP.
EtherCAT 0: Domain 0: Working counter changed to 3/3.
EtherCAT ERROR 0-4: Failed to set OP state, slave refused state change  
(SAFEOP + ERROR).
EtherCAT ERROR 0-4: AL status message 0x002D: "No Sync Error".
EtherCAT 0-4: Acknowledged state SAFEOP.
EtherCAT 0: Slave states: PREOP, SAFEOP, OP.
ec_dc_rtai_sample: AL states: 0x0E.
ec_dc_rtai_sample: Stopping...
EtherCAT 0: Releasing master...
EtherCAT DEBUG 0: ecrt_master_deactivate(master = 0xf71e7800)
EtherCAT DEBUG 0: Stopping master thread.
EtherCAT DEBUG 0: Master OP thread exiting...
EtherCAT 0: Master thread exited.
EtherCAT 0: Starting EtherCAT-IDLE thread.
EtherCAT DEBUG 0: OPERATION -> IDLE.
EtherCAT 0: Released.
ec_dc_rtai_sample: Unloading.
Thank you for your response.
-- 
Carlos Jiménez
ENCOPIM S.L.
C/. del Parc 5 (nau 13), P.I. Els Pinetons
E-08291 RIPOLLET (Barcelona)
Tel: (+34) 935 94 23 47
Fax: (+34) 935 94 64 15
==========================================================
La información contenida en la presente transmisión es confidencial y su
uso únicamente está permitido a su(s) destinatario(s). Si Ud. no es la
persona destinataria de la presente transmisión, rogamos nos lo
comunique de manera inmediata por teléfono (+34 935 942 347) y destruya
cualquier copia de la misma (tanto digitales como en papel).
The information contained in this transmission is confidential and is
intended only for the use of the addressee(s). If you are not the
designated recipient of this transmission, please advise us immediately
by telephone (+34 935 942 347) and destroy any copies (digital and
paper).
==========================================================
    
    
More information about the Etherlab-users
mailing list