Hi,

Yes I have thanks.  My cycle time is 1ms.  I have set:
0x60C2, 0x01 = 1
0x60C2, 0x02 = -3


Graeme.


-----Original Message-----
From: Henry Bausley [mailto:hbausley at deltatau.com] 
Sent: Wednesday, 1 February 2012 05:01
To: Graeme Foot
Cc: etherlab-users at etherlab.org
Subject: Re: [etherlab-users] Distributed Clock with Yaskawa SGDV drives

Did you try changing the interpolation time period, index 0x60C2 sub
indexes 1 and 2 to match your cycle time?



On Tue, 2012-01-31 at 20:03 +1300, Graeme Foot wrote:
> Hi,
> 
> I have been playing with various options but I'm still getting a drift on my slave relative to the master.
> 
> 
> What I have found so far:
> 
> 1) It looks like my slave requires no other frames on the ring when first setting up the distributed clocks (thanks for pointing that out George).
> - I now run only the distributed clock functions for 1 second before adding in the polling pdos.
> - This seems to make the System Time Diff (0x092C:0x092F) value remain small, but the Speed Counter Diff (0x0932:0x0933) remains at zero.
> 
> 
> 2) The System Time Delay (0x0928:0x092B) is a negative number.  The reported slave delays are:
>   Slave 0  (CX1100-0004)  0 ns
>   Slave 1  (EK1110)       140 ns
>   Slave 2  (EK1100)       2670 ns
>   Slave 3  (EL2602)       2815 ns
>   Slave 4  (EL2008)       2960 ns
>   Slave 5  (EL1008)       3100 ns
>   Slave 6  (EL1018)       3240 ns
>   Slave 7  (EL3162)       3385 ns
>   Slave 8  (EL4132)       3530 ns
>   Slave 9  (Yaskawa SGDV) 2147486168 ns  (-2520)
>   Slave 10 (Yaskawa SGDV) 2147487253 ns  (-3605)
> 
> The last two being the ones with the problems.  I still need to look into how the calculations are working with 32 bit dc.
> 
> 
> 3) The System Time Diff (0x092C:0x092F) is jumping around small -ve and positive numbers but the Speed Counter Diff (0x0932:0x0933) is remaining at zero.  If there was drift in the local clock I would have expected the System Time Diff to get bigger or the Speed Counter Diff to become non-zero to compensate for the drift.  Some example values:
>   Recieve Time Port 0 (0x0900:0x0903):  0x6c18cae8 1813564136
>   Recieve Time Port 1 (0x0904:0x0907):  0x6c18d362 1813566306
>   Recieve EPU         (0x0918:0x091F):  0x000000006c18cae8 1813564136
>   System Time         (0x0910:0x0917):  0x00000000e7ce6469 3889063017
>   System Time Offset  (0x0920:0x0927):  0x0000000048df3bfd 1222589437
>   System Time Delay   (0x0928:0x092B):  0x800009d8 -2520
>   System Time Diff    (0x092C:0x092F):  0x00000003 3
>   Speed Counter Start (0x0930:0x0931):  0x1001 4097
>   Speed Counter Diff  (0x0932:0x0933):  0x0000 0
> 
> 
> 4) In the examples there are two methods used to pass the time to ecrt_ master_application_time:
> a) in the kernel space example it is just adding the scan time to the current time, eg:
>   dcTime += 1000000;
>   ecrt_master_application_time(master, dcTime);
> b) in the user space example it gets the time every cycle, eg:
>   clock_gettime(CLOCK_TO_USE, &time);
>   ecrt_master_application_time(master, TIMESPEC2NS(time));
> 
> I'm using RTAI LXRT with rtdm.  I have confirmed that my cycle times are consistent and when using rt_get_cpu_time_ns (with method b) I am not getting drift at the master.  I've also tried method a with no different result.  I still need to match the slave time against the master time, but I'll need to read the register (via rtdm) to do that
> 
> 
> 5) I'm calling ecrt_slave_config_dc on the SGDV drives after the system is up and running but the sync Cyclic Unit Control and Activation (0x0980:0x0981) bytes remain zero as does the SYNC 0 Cycle Time (0x09A0:0x09A3).  eg:
>   ecrt_slave_config_dc(slave->sc, 0x0300, g_app.scanTimeNS, 500000, 0, 0);
> 
> Results in:
>   SYNC 0 Start Time   (0x0990:0x0997):  0x0000000048df3ad1 1222589137
>   SYNC 0 Pulse Length (0x0982:0x0983):  0x03e8 1000
>   SYNC 0 Cycle Time   (0x09A0:0x09A3):  0x00000000 0
>   Sync activation     (0x0980:0x0981):  0x0000 0
> 
> I still need to look at the code as to why this might be happening.
> 
> If I fill in these values manually, the start time starts ticking away as it should, but I still get drift.  (ie setting SYNC 0 Cycle Time (0x09A0:0x09A3) to 1000000; Sync activation (0x0980:0x0981) to 0x0300)
> 
> 
> 
> Apart from a couple of things mentioned above that I still need to look into, does anyone have anything else I should consider?
> 
> Also a couple of questions:
> - The first slave with a distributed clock becomes the reference slave.  Is there any way to find out which slave that is?  (I haven't looked into the code yet.)
> - Does the slave that is being used as the reference clock need to have its distributed clock enabled (with ecrt_slave_config_dc)?
> 
> 
> 
> I am using the latest 1.5.0 stable master:
>   # ethercat version
>   IgH EtherCAT master 1.5.0 ec8e1151b8a7+
> 
> 
> 
> Regards,
> Graeme.
> 
> 
> 
> 
> 
> -----Original Message-----
> From: etherlab-users-bounces at etherlab.org [mailto:etherlab-users-bounces at etherlab.org] On Behalf Of George Broz
> Sent: Saturday, 28 January 2012 14:36
> To: Graeme Foot
> Cc: etherlab-users at etherlab.org
> Subject: Re: [etherlab-users] Distributed Clock with Yaskawa SGDV drives
> 
> Hi,
> 
> It looks like the propagation (transmission) delay determination 
> is failing. That algorithm runs on driver insertion, if there is 
> a bus change, or if you use the command line tool and issue 
> 'ethercat rescan'. You can see the result (its register is 
> 0x0x928) using:
> 
> ethercat -p $1 -t uint32 reg_read 2344 4
> (where $1 is your slave position.)
> 
> The number returned is in nanoseconds.
> 
> It should return with something that's a couple of 
> hundred or a few thousand nanoseconds. This is then
> used with the the System offset register (0x920) to
> produce a System time from the slave's local time.
> 
> For starters, I'd try to write directly to the 
> 0x928 register supplying something reasonable. For example:
> 
> ethercat -p $1 -t uint32 reg_write 2344 1300
> 
> That value will stay in there as long as your bus configuration
> does not change or is not scanned. That's just to make sure
> the slave takes a value. 
> 
> If that works, you can take a quick look at the receive times 
> for each port. These will change whenever the propagation delay
> algorithm is run (e.g. ethercat rescan). These are what make 
> the propagation measurement possible. Only pay attention to the 
> ones where you have a physically connected slave (unconnected 
> ports return a number - something that looks uninitialized, 
> perhaps down at the slave?).
> 
> echo "Receive Time Port 0 - 0x0900:0x0903:" `ethercat -p $1 -t uint32 reg_read 2304 4`
> echo "Receive Time Port 1 - 0x0904:0x0907:" `ethercat -p $1 -t uint32 reg_read 2308 4`
> echo "Receive Time Port 2 - 0x0908:0x090B:" `ethercat -p $1 -t uint32 reg_read 2312 4`
> echo "Receive Time Port 4 - 0x090C:0x090F:" `ethercat -p $1 -t uint32 reg_read 2316 4`
> (where $1 is the slave position).
> 
> The difference between the numbers returned for connected ports
> should be small (thousands of nanoseconds). 
> 
> There is a note in the EtherCAT spec that states that for some 
> slaves the ring has to be empty of all other frames before the 
> broadcast write packet associated with this measurment can work 
> (see Beckhoff EtherCAT ET1100 datasheet section 9.1.2, just above 
> table 26.) That would require support from the master. Perhaps 
> your Yaskawa drives fall into that category. 
> 
> I have no experience with 32 bit DC slaves. Maybe there is a 
> bug there?
> 
> 
> BTW - if you want to view 0x92c (or others like it) with sign 
> bit removed use -
> 
> ethercat -p $1 -t sm32 reg_read 2348 4
> 
> 
> Best regards,
> 
> --George Broz
> Moog, Inc. Industrial Group
> 
> -----<etherlab-users-bounces at etherlab.org> wrote: -----
> To: <etherlab-users at etherlab.org>
> From: Graeme Foot 
> Sent by: 
> Date: 01/26/2012 06:38PM
> Subject: [etherlab-users] Distributed Clock with Yaskawa SGDV drives
> 
> 
> Hi,
>  
> I'm having a problem with my Yaskawa SGCV drives.  I am using them with Cyclic Synchronous Position Mode.  The problems is that while moving they frequently get an unstable position error.  The unstable position errors last for about ΒΌ of a second and occur regularly every 4 (approx) seconds.
>  
> The position error is always less than the cycle delta position.  I am setting up the drives to use the distributed clock but I am suspecting that something is not set up correctly and the position error is occurring due to a drift in cycle relative to the master.
>  
>  The "DC system time transmission delay" (from the "ethercat slaves -v" command) for the drives are:
> drive 1 (slave 9): 2147486148 ns
> drive 2 (slave 10): 2147487218 ns
> They are being reported as 32bit distributed clocks.
>  
> 
> When doing the "ethercat reg_read -p<slave> -tint32 0x092C" command on each of the slaves then the slaves prior to the yaskawa drives get numbers such as:
> 0x00000010 16
> 0x00000024 36
> 0x80000011 -2147483631
> 0x80000004 -2147483644
>  
> Where the low order bytes contain low numbers but the sign bit may be on or off.
>  
> However, the yaskawa slaves are more like:
> 0x66a32ed9 1721970393
> 0x669f8483 1721730179
> 0x669d0223 1721565731
> 0x669b553f 1721455935
>  
> 
> If I disconnect the drives then the rest of the slaves still behave the same (where the sign bit may be on or off).
>  
> 
> Does anyone have any ideas what I should be looking at next?
>  
> 
> Regards,
> Graeme Foot
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users






Outbound scan for Spam or Virus by Barracuda at Delta Tau