Hi,

First off, my understanding of setting up the DC system is that each slave that wants a Distributed Clock setup calls ecrt_slave_config_dc() specifying the sync0_cycle time and the sync0_shift time (and sync1).  The sync0_shift time should be specified as the offset from the nominal start of cycle time, which is specified by the very fist call to ecrt_master_application_time().

Therefore your cycles should always start at: initial_master_application_time + cycle_count * cycle_time
Where you start counting cycles as soon as the first ecrt_master_application_time() call is made.

I set my sync0_cycle to 1000000 (1ms) and sync0_shift to 500000 (0.5ms).  After waking up at the beginning of the cycle I then have 0.5ms to send my EtherCAT frames and have them be processed by all slaves.


As to answering "To solve the problem i have to know the systemtime, the next sync0-signal is generated in the slave. Does anybody know if this time is available in a slave with dc-support ?":

If the slave has a 64bit DC you should be able to calculate the next sync time as "initial_master_application_time + cycle_count * cycle_time + sync_shift".
If the slave has a 32bit DC its more annoying reading the clock but it should be the same calculation, but then remove the top 4 bytes.  (You get 4.2 odd seconds before the clock rolls over.)


Looking at the ET1100 datasheet document there is a register 0x0990:0x0997 which says it is the "SYNC0 Start Time" - Local copy of System Time (T_localtime + T_offset) (From Section 9.1.5).


Regards,
Graeme Foot.



________________________________
From: etherlab-users-bounces at etherlab.org [mailto:etherlab-users-bounces at etherlab.org] On Behalf Of WIEGAND Ralf
Sent: Wednesday, 2 April 2014 05:23
To: etherlab-users at etherlab.org
Subject: [etherlab-users] DC-Synchronization - Sync signal generation

Hello,

first of all, thanks to all etherlab-developers for their great job.

I have a question about the activation of the sync-signal generation with distributed clocks.  I use the ethercatmaster 1.5.1 with the dc-patches from Graeme Foot, kernel 2.6.32.11 with rtai 3.8.1. The application is running over the rtdm-interface and the masterclock is synchronized to the reference clock in slave 1. The slaves are particular developed for us from external companies (FPGA-based designs with Beckhoff IP-Core). The synchronization of the masterclock with the reference clock, like the patches from Graeme Foot, works very well. But i see a constant phase offset between the sync0-signal and the incoming frame (SOF). With every restart of the application the offset is constant during runtime, but with another value. If the value is in a special range, i read  the same input pdo values between two cycle times from the slave. To solve the problem i have to know the systemtime, the next sync0-signal is generated in the slave. Does anybody know if this time is available in a slave with dc-support ?

Thank you in advance,

Ralf Wiegand

Ralf Wiegand


T: +49 6441 207-410  F: +49 6441 207-387
E: Ralf.Wiegand at hexagonmetrology.com <mailto:Ralf.Wiegand at hexagonmetrology.com%20>

Hexagon Metrology GmbH
Siegmund-Hiepe-Str. 2-12
DE-35578 Wetzlar
www.hexagonmetrology.de<http://www.hexagonmetrology.de/> | LinkedIn<http://www.linkedin.com/company/hexagon-metrology> | Facebook<http://www.facebook.com/hex.metrology> | Twitter<http://twitter.com/hexmetrology>
<www.hexagonmetrology.de>
Hauptgeschäftsführer: Holger Fritze