[etherlab-users] Metronix controller's sync manager address same with PDO index
Zhiyong Weng
zhiyong.weng at gmail.com
Wed Feb 12 04:49:20 CET 2014
Hi Jun Yuan,
Thank you so much for sharing the knowledge about ethercat. It means a
lot for me.
Now I can get the PDO data as expected.
Here is what happened yesterday:
The codes your gave are correct. My vendor also did some configuration
using twincat.
so the whole story is,before the vendor use twincat, the code still get
zero data of pdo.
but after twincat config, same code return correct data.
Two thing changed I notice:
1. now can not change PDO index (0x1600,0x1A00),I mean reset the
number of mapped object and the PDO mapping.
before that, I can use SDO to write data to adress,like 0x1600:0
,0x1600:1.
In the log, can see the "WARNING 0-0: Failed to clear PDO
mapping."
2. now the value in PDO index changed. for example, I check 0x1A00:1
as below. It is 0x60610008. I notice the byte order of the value is diff.
according to vendor's xml file, it shall be 0x08006160.
/opt/etherlab/bin$ sudo ./ethercat upload --type=uint32 6656 1
0x60610008 1616969736
<InitCmd>
<Transition>PS</Transition>
<Index>#x1A00</Index>
<SubIndex>3</SubIndex>
<Data>08006160</Data>
<Comment>TxPDO1,Obj.3: mode of operation display</Comment>
</InitCmd>
I am not sure what vendor do with twincat. Anyway it works.
Thank you again. Happy New Year.
Regards,
Max
Feb 11 20:14:09 MAX dhclient: DHCPDISCOVER on eth0 to 255.255.255.255 port
67 interval 8
Feb 11 20:14:09 MAX kernel: [37974.854663] EtherCAT: Requesting master 0...
Feb 11 20:14:09 MAX kernel: [37974.854669] EtherCAT DEBUG 0: IDLE ->
OPERATION.
Feb 11 20:14:09 MAX kernel: [37974.854672] EtherCAT: Successfully requested
master 0.
Feb 11 20:14:09 MAX kernel: [37974.854677] EtherCAT DEBUG 0:
ecrt_master_create_domain(master = 0xffff88019fbae000)
Feb 11 20:14:09 MAX kernel: [37974.854680] EtherCAT DEBUG 0: Created domain
0.
Feb 11 20:14:09 MAX kernel: [37974.854683] EtherCAT DEBUG 0:
ecrt_master_create_domain(master = 0xffff88019fbae000)
Feb 11 20:14:09 MAX kernel: [37974.854685] EtherCAT DEBUG 0: Created domain
1.
Feb 11 20:14:09 MAX kernel: [37974.854689] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854693] EtherCAT DEBUG 0: Creating slave
configuration for 0:0, 0x000000E4/0x00001133.
Feb 11 20:14:09 MAX kernel: [37974.854699] EtherCAT DEBUG 0 0:0: Attached
slave 0.
Feb 11 20:14:09 MAX kernel: [37974.854757] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_sync_manager(sc = 0xffff880106d3d000, sync_index = 0, dir
= 1, watchdog_mode = 2)
Feb 11 20:14:09 MAX kernel: [37974.854761] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_sync_manager(sc = 0xffff880106d3d000, sync_index = 1, dir
= 2, watchdog_mode = 2)
Feb 11 20:14:09 MAX kernel: [37974.854764] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_sync_manager(sc = 0xffff880106d3d000, sync_index = 2, dir
= 1, watchdog_mode = 2)
Feb 11 20:14:09 MAX kernel: [37974.854769] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_assign_clear(sc = 0xffff880106d3d000, sync_index = 2)
Feb 11 20:14:09 MAX kernel: [37974.854774] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_assign_add(sc = 0xffff880106d3d000, sync_index = 2,
pdo_index = 0x1600)
Feb 11 20:14:09 MAX kernel: [37974.854777] EtherCAT DEBUG 0 0:0: Loading
default mapping for PDO 0x1600.
Feb 11 20:14:09 MAX kernel: [37974.854780] EtherCAT DEBUG 0 0:0: Found PDO
name "Outputs".
Feb 11 20:14:09 MAX kernel: [37974.854782] EtherCAT DEBUG 0 0:0: Entry
0x6040:00.
Feb 11 20:14:09 MAX kernel: [37974.854784] EtherCAT DEBUG 0 0:0: Entry
0x6060:00.
Feb 11 20:14:09 MAX kernel: [37974.854786] EtherCAT DEBUG 0 0:0: Entry
0x6098:00.
Feb 11 20:14:09 MAX kernel: [37974.854787] EtherCAT DEBUG 0 0:0: Entry
0x607A:00.
Feb 11 20:14:09 MAX kernel: [37974.854789] EtherCAT DEBUG 0 0:0: Entry
0x60FF:00.
Feb 11 20:14:09 MAX kernel: [37974.854790] EtherCAT DEBUG 0 0:0: Entry
0x6071:00.
Feb 11 20:14:09 MAX kernel: [37974.854794] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_clear(sc = 0xffff880106d3d000, pdo_index =
0x1600)
Feb 11 20:14:09 MAX kernel: [37974.854800] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1600, entry_index = 0x6040, entry_subindex = 0x00, entry_bit_length = 16)
Feb 11 20:14:09 MAX kernel: [37974.854805] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1600, entry_index = 0x6060, entry_subindex = 0x00, entry_bit_length = 8)
Feb 11 20:14:09 MAX kernel: [37974.854809] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_sync_manager(sc = 0xffff880106d3d000, sync_index = 3, dir
= 2, watchdog_mode = 2)
Feb 11 20:14:09 MAX kernel: [37974.854812] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_assign_clear(sc = 0xffff880106d3d000, sync_index = 3)
Feb 11 20:14:09 MAX kernel: [37974.854815] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_assign_add(sc = 0xffff880106d3d000, sync_index = 3,
pdo_index = 0x1A00)
Feb 11 20:14:09 MAX kernel: [37974.854818] EtherCAT DEBUG 0 0:0: Loading
default mapping for PDO 0x1A00.
Feb 11 20:14:09 MAX kernel: [37974.854820] EtherCAT DEBUG 0 0:0: Found PDO
name "Inputs".
Feb 11 20:14:09 MAX kernel: [37974.854822] EtherCAT DEBUG 0 0:0: Entry
0x6041:00.
Feb 11 20:14:09 MAX kernel: [37974.854824] EtherCAT DEBUG 0 0:0: Entry
0x6064:00.
Feb 11 20:14:09 MAX kernel: [37974.854825] EtherCAT DEBUG 0 0:0: Entry
0x6061:00.
Feb 11 20:14:09 MAX kernel: [37974.854827] EtherCAT DEBUG 0 0:0: Entry
0x1001:00.
Feb 11 20:14:09 MAX kernel: [37974.854829] EtherCAT DEBUG 0 0:0: Entry
0x606C:00.
Feb 11 20:14:09 MAX kernel: [37974.854831] EtherCAT DEBUG 0 0:0: Entry
0x6077:00.
Feb 11 20:14:09 MAX kernel: [37974.854833] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_clear(sc = 0xffff880106d3d000, pdo_index =
0x1A00)
Feb 11 20:14:09 MAX kernel: [37974.854837] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1A00, entry_index = 0x6041, entry_subindex = 0x00, entry_bit_length = 16)
Feb 11 20:14:09 MAX kernel: [37974.854841] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1A00, entry_index = 0x6064, entry_subindex = 0x00, entry_bit_length = 32)
Feb 11 20:14:09 MAX kernel: [37974.854845] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1A00, entry_index = 0x6061, entry_subindex = 0x00, entry_bit_length = 8)
Feb 11 20:14:09 MAX kernel: [37974.854849] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_pdo_mapping_add(sc = 0xffff880106d3d000, pdo_index =
0x1A00, entry_index = 0x1001, entry_subindex = 0x00, entry_bit_length = 8)
Feb 11 20:14:09 MAX kernel: [37974.854854] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854860] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x6040,
subindex = 0x00, domain = 0xffff8801597f3d00, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854865] EtherCAT DEBUG 0: Domain 1:
Added 3 bytes, total 3.
Feb 11 20:14:09 MAX kernel: [37974.854867] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854871] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x6060,
subindex = 0x00, domain = 0xffff8801597f3d00, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854875] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854879] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x6041,
subindex = 0x00, domain = 0xffff8801597f3900, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854883] EtherCAT DEBUG 0: Domain 0:
Added 8 bytes, total 8.
Feb 11 20:14:09 MAX kernel: [37974.854885] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854889] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x6064,
subindex = 0x00, domain = 0xffff8801597f3900, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854893] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854897] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x6061,
subindex = 0x00, domain = 0xffff8801597f3900, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854901] EtherCAT DEBUG 0:
ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
0, vendor_id = 0x000000e4, product_code = 0x00001133)
Feb 11 20:14:09 MAX kernel: [37974.854904] EtherCAT DEBUG 0 0:0:
ecrt_slave_config_reg_pdo_entry(sc = 0xffff880106d3d000, index = 0x1001,
subindex = 0x00, domain = 0xffff8801597f3900, bit_position =
0xffff8801b2f4bca4)
Feb 11 20:14:09 MAX kernel: [37974.854941] EtherCAT DEBUG 0:
ecrt_domain_external_memory(domain = 0xffff8801597f3900, mem =
0xffffc90018eb4000)
Feb 11 20:14:09 MAX kernel: [37974.854944] EtherCAT DEBUG 0:
ecrt_domain_external_memory(domain = 0xffff8801597f3d00, mem =
0xffffc90018eb4008)
Feb 11 20:14:09 MAX kernel: [37974.854947] EtherCAT DEBUG 0:
ecrt_master_callbacks(master = 0xffff88019fbae000, send_cb =
0xffffffffa056c8f0, receive_cb = 0xffffffffa056d020, cb_data =
0xffff88019fbae000)
Feb 11 20:14:09 MAX kernel: [37974.854951] EtherCAT DEBUG 0:
ecrt_master_activate(master = 0xffff88019fbae000)
Feb 11 20:14:09 MAX kernel: [37974.854955] EtherCAT DEBUG 0: Adding
datagram pair with expected WC 1.
Feb 11 20:14:09 MAX kernel: [37974.854958] EtherCAT 0: Domain0: Logical
address 0x00000000, 8 byte, expected working counter 1.
Feb 11 20:14:09 MAX kernel: [37974.854961] EtherCAT 0: Datagram
domain0-0-main: Logical offset 0x00000000, 8 byte, type LRD.
Feb 11 20:14:09 MAX kernel: [37974.854963] EtherCAT DEBUG 0: Adding
datagram pair with expected WC 1.
Feb 11 20:14:09 MAX kernel: [37974.854965] EtherCAT 0: Domain1: Logical
address 0x00000008, 3 byte, expected working counter 1.
Feb 11 20:14:09 MAX kernel: [37974.854968] EtherCAT 0: Datagram
domain1-8-main: Logical offset 0x00000008, 3 byte, type LWR.
Feb 11 20:14:09 MAX kernel: [37974.854971] EtherCAT DEBUG 0: Stopping
master thread.
Feb 11 20:14:09 MAX kernel: [37974.855023] EtherCAT DEBUG 0: Master IDLE
thread exiting...
Feb 11 20:14:09 MAX kernel: [37974.855091] EtherCAT 0: Master thread exited.
Feb 11 20:14:09 MAX kernel: [37974.855096] EtherCAT DEBUG 0: FSM datagram
is ffff88019fbae678.
Feb 11 20:14:09 MAX kernel: [37974.855099] EtherCAT 0: Starting EtherCAT-OP
thread.
Feb 11 20:14:09 MAX kernel: [37974.855224] EtherCAT DEBUG 0: mmap()
Feb 11 20:14:09 MAX kernel: [37974.855233] EtherCAT DEBUG 0: Vma fault,
virtual_address = 00007f1ecc8a6000, offset = 0, page = ffffea0006c1be00
Feb 11 20:14:09 MAX kernel: [37974.855247] EtherCAT DEBUG 0: Operation
thread running with fsm interval = 4000 us, max data size=45000
Feb 11 20:14:09 MAX kernel: [37974.855252] EtherCAT WARNING 0: 77 datagrams
TIMED OUT!
Feb 11 20:14:09 MAX kernel: [37974.856731] EtherCAT DEBUG 0: Configuration
changed (aborting state check).
Feb 11 20:14:09 MAX kernel: [37974.856763] EtherCAT WARNING 0: No app_time
received up to now, but master already active.
Feb 11 20:14:09 MAX kernel: [37974.856776] EtherCAT DEBUG 0: Requesting
OP...
Feb 11 20:14:09 MAX kernel: [37974.872760] EtherCAT DEBUG 0-0: Changing
state from PREOP to OP.
Feb 11 20:14:09 MAX kernel: [37974.872770] EtherCAT DEBUG 0-0:
Configuring...
Feb 11 20:14:09 MAX kernel: [37974.879615] EtherCAT DEBUG 0-0: Now in INIT.
Feb 11 20:14:09 MAX kernel: [37974.879617] EtherCAT DEBUG 0-0: Clearing
FMMU configurations...
Feb 11 20:14:09 MAX kernel: [37974.886326] EtherCAT DEBUG 0-0: Clearing
sync manager configurations...
Feb 11 20:14:09 MAX kernel: [37974.892941] EtherCAT DEBUG 0-0: Configuring
mailbox sync managers...
Feb 11 20:14:09 MAX kernel: [37974.892944] EtherCAT DEBUG 0-0: SM0: Addr
0x1800, Size 16, Ctrl 0x26, En 1
Feb 11 20:14:09 MAX kernel: [37974.892946] EtherCAT DEBUG 0-0: SM1: Addr
0x1900, Size 16, Ctrl 0x12, En 1
Feb 11 20:14:09 MAX kernel: [37974.906270] EtherCAT DEBUG 0-0: Now in PREOP.
Feb 11 20:14:09 MAX kernel: [37974.906277] EtherCAT DEBUG 0-0: Changing
mapping of PDO 0x1600.
Feb 11 20:14:09 MAX kernel: [37974.906278] EtherCAT DEBUG 0-0: Currently
mapped PDO entries: 0x6040:00/16 0x6060:00/8 0x6098:00/8 0x607A:00/32
0x60FF:00/32 0x6071:00/16. Entries to map: 0x6040:00/16 0x6060:00/8
Feb 11 20:14:09 MAX kernel: [37974.906294] EtherCAT DEBUG 0-0: Setting
entry count to zero.
Feb 11 20:14:09 MAX kernel: [37974.906296] EtherCAT DEBUG 0-0: Downloading
SDO 0x1600:00.
Feb 11 20:14:09 MAX kernel: [37974.906305] EtherCAT DEBUG: 00
Feb 11 20:14:09 MAX kernel: [37974.906308] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:09 MAX kernel: [37974.906309] EtherCAT DEBUG: 00 20 2F 00 16
00 00 00 00 00
Feb 11 20:14:09 MAX kernel: [37974.919597] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:09 MAX kernel: [37974.919599] EtherCAT DEBUG: 00 30 80 00 16
00 22 00 00 08
Feb 11 20:14:09 MAX kernel: [37974.919603] EtherCAT DEBUG 0-0: Invalid SDO
download response! Retrying...
Feb 11 20:14:09 MAX kernel: [37974.919604] EtherCAT DEBUG: 00 30 80 00 16
00 22 00 00 08
Feb 11 20:14:10 MAX kernel: [37975.909187] EtherCAT ERROR 0-0: Timeout
after 1000 ms while waiting for SDO 0x1600:0 download response.
Feb 11 20:14:10 MAX kernel: [37975.909191] EtherCAT WARNING 0-0: Failed to
clear PDO mapping.
Feb 11 20:14:10 MAX kernel: [37975.909192] EtherCAT WARNING 0-0: Currently
mapped PDO entries: 0x6040:00/16 0x6060:00/8 0x6098:00/8 0x607A:00/32
0x60FF:00/32 0x6071:00/16. Entries to map: 0x6040:00/16 0x6060:00/8
Feb 11 20:14:10 MAX kernel: [37975.909202] EtherCAT WARNING 0-0: Failed to
configure mapping of PDO 0x1600.
Feb 11 20:14:10 MAX kernel: [37975.909212] EtherCAT DEBUG 0-0: Setting PDO
assignment of SM2:
Feb 11 20:14:10 MAX kernel: [37975.909214] EtherCAT DEBUG 0-0: Currently
assigned PDOs: 0x1600. PDOs to assign: 0x1600
Feb 11 20:14:10 MAX kernel: [37975.909217] EtherCAT DEBUG 0-0: Setting
number of assigned PDOs to zero.
Feb 11 20:14:10 MAX kernel: [37975.909220] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C12:00.
Feb 11 20:14:10 MAX kernel: [37975.909221] EtherCAT DEBUG: 00
Feb 11 20:14:10 MAX kernel: [37975.909223] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:10 MAX kernel: [37975.909224] EtherCAT DEBUG: 00 20 2F 12 1C
00 00 00 00 00
Feb 11 20:14:10 MAX kernel: [37975.922511] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:10 MAX kernel: [37975.922513] EtherCAT DEBUG: 00 30 60 12 1C
00 00 00 00 00
Feb 11 20:14:10 MAX kernel: [37975.922519] EtherCAT DEBUG 0-0: Assigning
PDO 0x1600 at position 1.
Feb 11 20:14:10 MAX kernel: [37975.922520] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C12:01.
Feb 11 20:14:10 MAX kernel: [37975.922521] EtherCAT DEBUG: 00 16
Feb 11 20:14:10 MAX kernel: [37975.922523] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:10 MAX kernel: [37975.922524] EtherCAT DEBUG: 00 20 2B 12 1C
01 00 16 00 00
Feb 11 20:14:10 MAX kernel: [37975.935852] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:10 MAX kernel: [37975.935855] EtherCAT DEBUG: 00 30 60 12 1C
01 00 00 00 00
Feb 11 20:14:10 MAX kernel: [37975.935862] EtherCAT DEBUG 0-0: Setting
number of assigned PDOs to 1.
Feb 11 20:14:10 MAX kernel: [37975.935864] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C12:00.
Feb 11 20:14:10 MAX kernel: [37975.935865] EtherCAT DEBUG: 01
Feb 11 20:14:10 MAX kernel: [37975.935868] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:10 MAX kernel: [37975.935869] EtherCAT DEBUG: 00 20 2F 12 1C
00 01 00 00 00
Feb 11 20:14:11 MAX kernel: [37975.949171] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:11 MAX kernel: [37975.949175] EtherCAT DEBUG: 00 30 60 12 1C
00 00 00 00 00
Feb 11 20:14:11 MAX kernel: [37975.949184] EtherCAT DEBUG 0-0: Successfully
configured PDO assignment of SM2.
Feb 11 20:14:11 MAX kernel: [37975.949191] EtherCAT DEBUG 0-0: Changing
mapping of PDO 0x1A00.
Feb 11 20:14:11 MAX kernel: [37975.949193] EtherCAT DEBUG 0-0: Currently
mapped PDO entries: 0x6041:00/16 0x6064:00/32 0x6061:00/8 0x1001:00/8
0x606C:00/32 0x6077:00/16. Entries to map: 0x6041:00/16 0x6064:00/32
0x6061:00/8 0x1001:00/8
Feb 11 20:14:11 MAX kernel: [37975.949208] EtherCAT DEBUG 0-0: Setting
entry count to zero.
Feb 11 20:14:11 MAX kernel: [37975.949211] EtherCAT DEBUG 0-0: Downloading
SDO 0x1A00:00.
Feb 11 20:14:11 MAX kernel: [37975.949212] EtherCAT DEBUG: 00
Feb 11 20:14:11 MAX kernel: [37975.949215] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:11 MAX kernel: [37975.949217] EtherCAT DEBUG: 00 20 2F 00 1A
00 00 00 00 00
Feb 11 20:14:11 MAX kernel: [37975.962495] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:11 MAX kernel: [37975.962497] EtherCAT DEBUG: 00 30 80 00 1A
00 22 00 00 08
Feb 11 20:14:11 MAX kernel: [37975.962501] EtherCAT DEBUG 0-0: Invalid SDO
download response! Retrying...
Feb 11 20:14:11 MAX kernel: [37975.962502] EtherCAT DEBUG: 00 30 80 00 1A
00 22 00 00 08
Feb 11 20:14:12 MAX kernel: [37976.952110] EtherCAT ERROR 0-0: Timeout
after 1000 ms while waiting for SDO 0x1a00:0 download response.
Feb 11 20:14:12 MAX kernel: [37976.952113] EtherCAT WARNING 0-0: Failed to
clear PDO mapping.
Feb 11 20:14:12 MAX kernel: [37976.952115] EtherCAT WARNING 0-0: Currently
mapped PDO entries: 0x6041:00/16 0x6064:00/32 0x6061:00/8 0x1001:00/8
0x606C:00/32 0x6077:00/16. Entries to map: 0x6041:00/16 0x6064:00/32
0x6061:00/8 0x1001:00/8
Feb 11 20:14:12 MAX kernel: [37976.952126] EtherCAT WARNING 0-0: Failed to
configure mapping of PDO 0x1A00.
Feb 11 20:14:12 MAX kernel: [37976.952128] EtherCAT DEBUG 0-0: Setting PDO
assignment of SM3:
Feb 11 20:14:12 MAX kernel: [37976.952129] EtherCAT DEBUG 0-0: Currently
assigned PDOs: 0x1A00. PDOs to assign: 0x1A00
Feb 11 20:14:12 MAX kernel: [37976.952133] EtherCAT DEBUG 0-0: Setting
number of assigned PDOs to zero.
Feb 11 20:14:12 MAX kernel: [37976.952135] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C13:00.
Feb 11 20:14:12 MAX kernel: [37976.952137] EtherCAT DEBUG: 00
Feb 11 20:14:12 MAX kernel: [37976.952139] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:12 MAX kernel: [37976.952140] EtherCAT DEBUG: 00 20 2F 13 1C
00 00 00 00 00
Feb 11 20:14:12 MAX kernel: [37976.965410] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:12 MAX kernel: [37976.965413] EtherCAT DEBUG: 00 30 60 13 1C
00 00 00 00 00
Feb 11 20:14:12 MAX kernel: [37976.965419] EtherCAT DEBUG 0-0: Assigning
PDO 0x1A00 at position 1.
Feb 11 20:14:12 MAX kernel: [37976.965422] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C13:01.
Feb 11 20:14:12 MAX kernel: [37976.965423] EtherCAT DEBUG: 00 1A
Feb 11 20:14:12 MAX kernel: [37976.965425] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:12 MAX kernel: [37976.965426] EtherCAT DEBUG: 00 20 2B 13 1C
01 00 1A 00 00
Feb 11 20:14:12 MAX kernel: [37976.978737] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:12 MAX kernel: [37976.978738] EtherCAT DEBUG: 00 30 60 13 1C
01 00 00 00 00
Feb 11 20:14:12 MAX kernel: [37976.978743] EtherCAT DEBUG 0-0: Setting
number of assigned PDOs to 1.
Feb 11 20:14:12 MAX kernel: [37976.978745] EtherCAT DEBUG 0-0: Downloading
SDO 0x1C13:00.
Feb 11 20:14:12 MAX kernel: [37976.978746] EtherCAT DEBUG: 01
Feb 11 20:14:12 MAX kernel: [37976.978747] EtherCAT DEBUG 0-0: Expedited
download request:
Feb 11 20:14:12 MAX kernel: [37976.978748] EtherCAT DEBUG: 00 20 2F 13 1C
00 01 00 00 00
Feb 11 20:14:12 MAX kernel: [37976.992064] EtherCAT DEBUG 0-0: Download
response:
Feb 11 20:14:12 MAX kernel: [37976.992065] EtherCAT DEBUG: 00 30 60 13 1C
00 00 00 00 00
Feb 11 20:14:12 MAX kernel: [37976.992071] EtherCAT DEBUG 0-0: Successfully
configured PDO assignment of SM3.
Feb 11 20:14:12 MAX kernel: [37976.992075] EtherCAT DEBUG 0-0: SM2: Addr
0x1600, Size 3, Ctrl 0x24, En 1
Feb 11 20:14:12 MAX kernel: [37976.992077] EtherCAT DEBUG 0-0: SM3: Addr
0x1A00, Size 8, Ctrl 0x10, En 1
Feb 11 20:14:12 MAX kernel: [37976.998730] EtherCAT DEBUG 0 0:0: FMMU:
LogAddr 0x00000008, Size 3, PhysAddr 0x1600, SM2, Dir out
Feb 11 20:14:12 MAX kernel: [37976.998732] EtherCAT DEBUG 0 0:0: FMMU:
LogAddr 0x00000000, Size 8, PhysAddr 0x1A00, SM3, Dir in
Feb 11 20:14:12 MAX kernel: [37977.008725] EtherCAT 0: Domain 1: Working
counter changed to 1/1.
Feb 11 20:14:12 MAX kernel: [37977.012054] EtherCAT DEBUG 0-0: Now in
SAFEOP.
Feb 11 20:14:12 MAX kernel: [37977.018719] EtherCAT DEBUG 0-0: Now in OP.
Finished configuration.
Feb 11 20:14:12 MAX kernel: [37977.022173] EtherCAT 0: Domain 0: Working
counter changed to 1/1.
Feb 11 20:14:12 MAX kernel: [37977.028095] EtherCAT 0: Slave states on main
device: OP.
Feb 11 20:14:17 MAX dhclient: DHCPDISCOVER on eth0 to 255.255.255.255 port
67 interval 14
Feb 11 20:14:31 MAX dhclient: DHCPDISCOVER on eth0 to 255.255.255.255 port
67 interval 12
2014-02-11 19:14 GMT+08:00 Jun Yuan <j.yuan at rtleaders.com>:
> Hi Zhiyong,
>
> about the SII:
> When the slave only have a EEPROM of 128 byte, it is impossible to write
> the whole SII to the slave. You've done a great job by hardcoding the SII
> to the source code.
> If you need to have it more flexible in the future, I once tried the patch
> from Jesper Smith
> http://lists.etherlab.org/pipermail/etherlab-users/2011/001458.html,
> which load the SII file from your file system as a firmware, and it worked
> nice.
>
> To your question:
> The SyncManager StartAddress is its physical address in the ESC's memory.
> And the object index is only an index for the object retrieval, though
> sometimes people call it object address, but basically it has nothing to do
> with physical address.
>
> It is unusual that the engineer from Metronix pick up exactly the same
> number 0x1600 and 0x1a00 for as the physical address of SyncM in ESC, but
> yes they can do that. I think either they didn't understand the meaning of
> StartAddress when they design the ESC, or they just want to make a joke.
>
> To the problem you have:
> Your slave is in OP. Domain 1 has data exchange. But the domain0 is
> missing. Did you forget to send the domain0 frame out in your loop?
> And the source code in your last email makes the pdo data only sending out
> every 1 second. This is too slow for the EtherLab master, which would
> complain if it can't receive the PDO data in 1 second. Change your code
> back like the following
>
> void cyclic_task()
> {
> // receive process data
> ecrt_master_receive(master);
> ecrt_domain_process(domain0);
> ecrt_domain_process(domain1);
>
> // check process data state (optional)
> check_domain1_state();
>
> if (counter) {
> counter--;
> } else { // do this at 1 Hz
> counter = FREQUENCY;
>
> // check for master state (optional)
> check_master_state();
>
> // check for islave configuration state(s) (optional)
> check_slave_config_states();
>
> #if SDO_ACCESS
> // read process data SDO
> read_sdo();
> #endif
>
> }
>
> // send process data
> ecrt_domain_queue(domain0);
> ecrt_domain_queue(domain1);
> ecrt_master_send(master);
> }
>
>
>
> Regards,
> Jun
>
> <http://lists.etherlab.org/pipermail/etherlab-users/2011/001458.html>
>
>
> On Tue, Feb 11, 2014 at 3:40 AM, Zhiyong Weng <zhiyong.weng at gmail.com>wrote:
>
>> Hi ALL,
>>
>> The problem is : no PDO data exchanged.
>>
>> I find in esi file, the sync manager 2 and 3 address are same with
>> PDO index. Is it normal?
>>
>> I attached logs and esi xml.
>>
>> Thanks.
>>
>> Regards,
>> Max
>>
>> Feb 11 09:24:15 MAX kernel: [ 2867.475505] EtherCAT 0: Releasing master...
>> Feb 11 09:24:15 MAX kernel: [ 2867.475519] EtherCAT DEBUG 0:
>> ecrt_master_deactivate(master = 0xffff88019fbae000)
>> Feb 11 09:24:15 MAX kernel: [ 2867.475527] EtherCAT DEBUG 0: Stopping
>> master thread.
>> Feb 11 09:24:15 MAX kernel: [ 2867.475551] EtherCAT DEBUG 0: Master OP
>> thread exiting...
>> Feb 11 09:24:15 MAX kernel: [ 2867.475603] EtherCAT 0: Master thread
>> exited.
>> Feb 11 09:24:15 MAX kernel: [ 2867.475627] EtherCAT 0: Starting
>> EtherCAT-IDLE thread.
>> Feb 11 09:24:15 MAX kernel: [ 2867.475750] EtherCAT DEBUG 0: OPERATION ->
>> IDLE.
>> Feb 11 09:24:15 MAX kernel: [ 2867.475755] EtherCAT 0: Released.
>> Feb 11 09:24:15 MAX kernel: [ 2867.475810] EtherCAT DEBUG 0: Idle thread
>> running with send interval = 4000 us, max data size=45000
>> Feb 11 09:24:15 MAX kernel: [ 2867.475829] EtherCAT DEBUG 0: UNMATCHED
>> datagram:
>> Feb 11 09:24:15 MAX kernel: [ 2867.475833] EtherCAT DEBUG: 0B 7C 08 00 00
>> 00 08 80 00 00 00 00 00 00 00 00
>> Feb 11 09:24:15 MAX kernel: [ 2867.475853] EtherCAT DEBUG: 00 00 01 00
>> Feb 11 09:24:15 MAX kernel: [ 2867.475861] EtherCAT DEBUG 0: UNMATCHED
>> datagram:
>> Feb 11 09:24:15 MAX kernel: [ 2867.475864] EtherCAT DEBUG: 0A 7D 00 00 00
>> 00 08 80 00 00 00 00 00 00 00 00
>> Feb 11 09:24:15 MAX kernel: [ 2867.475883] EtherCAT DEBUG: 00 00 00 00
>> Feb 11 09:24:15 MAX kernel: [ 2867.475896] EtherCAT DEBUG 0-0: Changing
>> state from OP to PREOP (forced).
>> Feb 11 09:24:15 MAX kernel: [ 2867.475901] EtherCAT DEBUG 0-0:
>> Configuring...
>> Feb 11 09:24:15 MAX kernel: [ 2867.476155] EtherCAT DEBUG 0-0: Now in
>> INIT.
>> Feb 11 09:24:15 MAX kernel: [ 2867.476160] EtherCAT DEBUG 0-0: Clearing
>> FMMU configurations...
>> Feb 11 09:24:15 MAX kernel: [ 2867.476304] EtherCAT DEBUG 0-0: Clearing
>> sync manager configurations...
>> Feb 11 09:24:15 MAX kernel: [ 2867.476455] EtherCAT DEBUG 0-0:
>> Configuring mailbox sync managers...
>> Feb 11 09:24:15 MAX kernel: [ 2867.476463] EtherCAT DEBUG 0-0: SM0: Addr
>> 0x1800, Size 16, Ctrl 0x26, En 1
>> Feb 11 09:24:15 MAX kernel: [ 2867.476469] EtherCAT DEBUG 0-0: SM1: Addr
>> 0x1900, Size 16, Ctrl 0x12, En 1
>> Feb 11 09:24:15 MAX kernel: [ 2867.476886] EtherCAT DEBUG 0-0: Now in
>> PREOP.
>> Feb 11 09:24:15 MAX kernel: [ 2867.476890] EtherCAT DEBUG 0-0: Finished
>> configuration.
>> Feb 11 09:24:15 MAX kernel: [ 2867.479134] EtherCAT 0: Slave states on
>> main device: PREOP.
>> Feb 11 09:24:16 MAX kernel: [ 2868.275983] EtherCAT: Requesting master
>> 0...
>> Feb 11 09:24:16 MAX kernel: [ 2868.275993] EtherCAT DEBUG 0: IDLE ->
>> OPERATION.
>> Feb 11 09:24:16 MAX kernel: [ 2868.275999] EtherCAT: Successfully
>> requested master 0.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276007] EtherCAT DEBUG 0:
>> ecrt_master_create_domain(master = 0xffff88019fbae000)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276013] EtherCAT DEBUG 0: Created
>> domain 0.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276019] EtherCAT DEBUG 0:
>> ecrt_master_create_domain(master = 0xffff88019fbae000)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276024] EtherCAT DEBUG 0: Created
>> domain 1.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276033] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276042] EtherCAT DEBUG 0: Creating
>> slave configuration for 0:0, 0x000000E4/0x00001133.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276050] EtherCAT DEBUG 0 0:0: Attached
>> slave 0.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276127] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_sync_manager(sc = 0xffff880175cd6800, sync_index = 0, dir
>> = 1, watchdog_mode = 2)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276136] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_sync_manager(sc = 0xffff880175cd6800, sync_index = 1, dir
>> = 2, watchdog_mode = 2)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276144] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_sync_manager(sc = 0xffff880175cd6800, sync_index = 2, dir
>> = 1, watchdog_mode = 2)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276155] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_assign_clear(sc = 0xffff880175cd6800, sync_index = 2)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276166] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_assign_add(sc = 0xffff880175cd6800, sync_index = 2,
>> pdo_index = 0x1600)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276173] EtherCAT DEBUG 0 0:0: Loading
>> default mapping for PDO 0x1600.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276178] EtherCAT DEBUG 0 0:0: No
>> default mapping found.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276186] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_clear(sc = 0xffff880175cd6800, pdo_index =
>> 0x1600)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276197] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1600, entry_index = 0x607A, entry_subindex = 0x00, entry_bit_length = 32)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276208] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1600, entry_index = 0x60FF, entry_subindex = 0x00, entry_bit_length = 32)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276218] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_sync_manager(sc = 0xffff880175cd6800, sync_index = 3, dir
>> = 2, watchdog_mode = 2)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276226] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_assign_clear(sc = 0xffff880175cd6800, sync_index = 3)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276234] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_assign_add(sc = 0xffff880175cd6800, sync_index = 3,
>> pdo_index = 0x1A00)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276241] EtherCAT DEBUG 0 0:0: Loading
>> default mapping for PDO 0x1A00.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276245] EtherCAT DEBUG 0 0:0: No
>> default mapping found.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276251] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_clear(sc = 0xffff880175cd6800, pdo_index =
>> 0x1A00)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276259] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1A00, entry_index = 0x6041, entry_subindex = 0x00, entry_bit_length = 16)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276270] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1A00, entry_index = 0x6064, entry_subindex = 0x00, entry_bit_length = 32)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276280] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1A00, entry_index = 0x6061, entry_subindex = 0x00, entry_bit_length = 8)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276289] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff880175cd6800, pdo_index =
>> 0x1A00, entry_index = 0x1001, entry_subindex = 0x00, entry_bit_length = 8)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276302] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276314] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x607A,
>> subindex = 0x00, domain = 0xffff8801b52bb700, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276323] EtherCAT DEBUG 0: Domain 1:
>> Added 8 bytes, total 8.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276330] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276340] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x60FF,
>> subindex = 0x00, domain = 0xffff8801b52bb700, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276349] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276359] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x6041,
>> subindex = 0x00, domain = 0xffff8801b52bbd00, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276368] EtherCAT DEBUG 0: Domain 0:
>> Added 8 bytes, total 8.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276373] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276383] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x6064,
>> subindex = 0x00, domain = 0xffff8801b52bbd00, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276392] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276402] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x6061,
>> subindex = 0x00, domain = 0xffff8801b52bbd00, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276411] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff88019fbae000, alias = 0, position =
>> 0, vendor_id = 0x000000e4, product_code = 0x00001133)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276421] EtherCAT DEBUG 0 0:0:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff880175cd6800, index = 0x1001,
>> subindex = 0x00, domain = 0xffff8801b52bbd00, bit_position =
>> 0xffff880151691ca4)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276469] EtherCAT DEBUG 0:
>> ecrt_domain_external_memory(domain = 0xffff8801b52bbd00, mem =
>> 0xffffc900193c4000)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276476] EtherCAT DEBUG 0:
>> ecrt_domain_external_memory(domain = 0xffff8801b52bb700, mem =
>> 0xffffc900193c4008)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276483] EtherCAT DEBUG 0:
>> ecrt_master_callbacks(master = 0xffff88019fbae000, send_cb =
>> 0xffffffffa056c8f0, receive_cb = 0xffffffffa056d020, cb_data =
>> 0xffff88019fbae000)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276491] EtherCAT DEBUG 0:
>> ecrt_master_activate(master = 0xffff88019fbae000)
>> Feb 11 09:24:16 MAX kernel: [ 2868.276499] EtherCAT DEBUG 0: Adding
>> datagram pair with expected WC 1.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276505] EtherCAT 0: Domain0: Logical
>> address 0x00000000, 8 byte, expected working counter 1.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276511] EtherCAT 0: Datagram
>> domain0-0-main: Logical offset 0x00000000, 8 byte, type LRD.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276518] EtherCAT DEBUG 0: Adding
>> datagram pair with expected WC 1.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276523] EtherCAT 0: Domain1: Logical
>> address 0x00000008, 8 byte, expected working counter 1.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276529] EtherCAT 0: Datagram
>> domain1-8-main: Logical offset 0x00000008, 8 byte, type LWR.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276534] EtherCAT DEBUG 0: Stopping
>> master thread.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276550] EtherCAT DEBUG 0: Master IDLE
>> thread exiting...
>> Feb 11 09:24:16 MAX kernel: [ 2868.276585] EtherCAT 0: Master thread
>> exited.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276592] EtherCAT DEBUG 0: FSM datagram
>> is ffff88019fbae678.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276597] EtherCAT 0: Starting
>> EtherCAT-OP thread.
>> Feb 11 09:24:16 MAX kernel: [ 2868.276768] EtherCAT DEBUG 0: Operation
>> thread running with fsm interval = 4000 us, max data size=45000
>> Feb 11 09:24:16 MAX kernel: [ 2868.276777] EtherCAT DEBUG 0: mmap()
>> Feb 11 09:24:16 MAX kernel: [ 2868.276785] EtherCAT WARNING 0: 2
>> datagrams UNMATCHED!
>> Feb 11 09:24:16 MAX kernel: [ 2868.276792] EtherCAT DEBUG 0: Vma fault,
>> virtual_address = 00007f979608d000, offset = 0, page = ffffea000695bd00
>> Feb 11 09:24:16 MAX kernel: [ 2868.278887] EtherCAT DEBUG 0:
>> Configuration changed.
>> Feb 11 09:24:16 MAX kernel: [ 2868.278897] EtherCAT WARNING 0: No
>> app_time received up to now, but master already active.
>> Feb 11 09:24:16 MAX kernel: [ 2868.278905] EtherCAT DEBUG 0: Requesting
>> OP...
>> Feb 11 09:24:16 MAX kernel: [ 2868.318833] EtherCAT DEBUG 0-0: Changing
>> state from PREOP to OP.
>> Feb 11 09:24:16 MAX kernel: [ 2868.318840] EtherCAT DEBUG 0-0:
>> Configuring...
>> Feb 11 09:24:16 MAX kernel: [ 2868.347855] EtherCAT DEBUG 0-0: Now in
>> INIT.
>> Feb 11 09:24:16 MAX kernel: [ 2868.347857] EtherCAT DEBUG 0-0: Clearing
>> FMMU configurations...
>> Feb 11 09:24:16 MAX kernel: [ 2868.367847] EtherCAT DEBUG 0-0: Clearing
>> sync manager configurations...
>> Feb 11 09:24:16 MAX kernel: [ 2868.387835] EtherCAT DEBUG 0-0:
>> Configuring mailbox sync managers...
>> Feb 11 09:24:16 MAX kernel: [ 2868.387838] EtherCAT DEBUG 0-0: SM0: Addr
>> 0x1800, Size 16, Ctrl 0x26, En 1
>> Feb 11 09:24:16 MAX kernel: [ 2868.387840] EtherCAT DEBUG 0-0: SM1: Addr
>> 0x1900, Size 16, Ctrl 0x12, En 1
>> Feb 11 09:24:16 MAX kernel: [ 2868.427833] EtherCAT DEBUG 0-0: Now in
>> PREOP.
>> Feb 11 09:24:16 MAX kernel: [ 2868.427839] EtherCAT DEBUG 0-0: Reading
>> mapping of PDO 0x1600.
>> Feb 11 09:24:16 MAX kernel: [ 2868.427841] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1600:00.
>> Feb 11 09:24:16 MAX kernel: [ 2868.427843] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:16 MAX kernel: [ 2868.427844] EtherCAT DEBUG: 00 20 40 00 16
>> 00 00 00 00 00
>> Feb 11 09:24:16 MAX kernel: [ 2868.467812] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:16 MAX kernel: [ 2868.467814] EtherCAT DEBUG: 00 30 4F 00 16
>> 00 02 00 00 00
>> Feb 11 09:24:16 MAX kernel: [ 2868.467818] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:16 MAX kernel: [ 2868.467819] EtherCAT DEBUG: 02
>> Feb 11 09:24:16 MAX kernel: [ 2868.467821] EtherCAT DEBUG 0-0: 2 PDO
>> entries mapped.
>> Feb 11 09:24:16 MAX kernel: [ 2868.467822] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1600:01.
>> Feb 11 09:24:16 MAX kernel: [ 2868.467823] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:16 MAX kernel: [ 2868.467824] EtherCAT DEBUG: 00 20 40 00 16
>> 01 00 00 00 00
>> Feb 11 09:24:16 MAX kernel: [ 2868.507802] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:16 MAX kernel: [ 2868.507804] EtherCAT DEBUG: 00 30 43 00 16
>> 01 20 00 7A 60
>> Feb 11 09:24:16 MAX kernel: [ 2868.507808] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:16 MAX kernel: [ 2868.507809] EtherCAT DEBUG: 20 00 7A 60
>> Feb 11 09:24:16 MAX kernel: [ 2868.507812] EtherCAT DEBUG 0-0: PDO entry
>> 0x607A:00, 32 bit, "???".
>> Feb 11 09:24:16 MAX kernel: [ 2868.507814] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1600:02.
>> Feb 11 09:24:16 MAX kernel: [ 2868.507816] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:16 MAX kernel: [ 2868.507817] EtherCAT DEBUG: 00 20 40 00 16
>> 02 00 00 00 00
>> Feb 11 09:24:16 MAX kernel: [ 2868.547788] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:16 MAX kernel: [ 2868.547790] EtherCAT DEBUG: 00 30 43 00 16
>> 02 20 00 FF 60
>> Feb 11 09:24:16 MAX kernel: [ 2868.547795] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:16 MAX kernel: [ 2868.547796] EtherCAT DEBUG: 20 00 FF 60
>> Feb 11 09:24:16 MAX kernel: [ 2868.547800] EtherCAT DEBUG 0-0: PDO entry
>> 0x60FF:00, 32 bit, "???".
>> Feb 11 09:24:16 MAX kernel: [ 2868.547801] EtherCAT DEBUG 0-0: Changing
>> mapping of PDO 0x1600.
>> Feb 11 09:24:16 MAX kernel: [ 2868.547803] EtherCAT DEBUG 0-0: Currently
>> mapped PDO entries: 0x607A:00/32 0x60FF:00/32. Entries to map: 0x607A:00/32
>> 0x60FF:00/32
>> Feb 11 09:24:16 MAX kernel: [ 2868.547824] EtherCAT DEBUG 0-0: Setting
>> entry count to zero.
>> Feb 11 09:24:16 MAX kernel: [ 2868.547826] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1600:00.
>> Feb 11 09:24:16 MAX kernel: [ 2868.547827] EtherCAT DEBUG: 00
>> Feb 11 09:24:16 MAX kernel: [ 2868.547829] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:16 MAX kernel: [ 2868.547830] EtherCAT DEBUG: 00 20 2F 00 16
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.587775] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.587777] EtherCAT DEBUG: 00 30 60 00 16
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.587781] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x607A:00 (32 bit) at position 1.
>> Feb 11 09:24:17 MAX kernel: [ 2868.587783] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1600:01.
>> Feb 11 09:24:17 MAX kernel: [ 2868.587784] EtherCAT DEBUG: 20 00 7A 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.587786] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.587787] EtherCAT DEBUG: 00 20 23 00 16
>> 01 20 00 7A 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.627764] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.627766] EtherCAT DEBUG: 00 30 60 00 16
>> 01 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.627772] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x60FF:00 (32 bit) at position 2.
>> Feb 11 09:24:17 MAX kernel: [ 2868.627775] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1600:02.
>> Feb 11 09:24:17 MAX kernel: [ 2868.627776] EtherCAT DEBUG: 20 00 FF 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.627779] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.627780] EtherCAT DEBUG: 00 20 23 00 16
>> 02 20 00 FF 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.667749] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.667751] EtherCAT DEBUG: 00 30 60 00 16
>> 02 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.667755] EtherCAT DEBUG 0-0: Setting
>> number of PDO entries to 2.
>> Feb 11 09:24:17 MAX kernel: [ 2868.667756] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1600:00.
>> Feb 11 09:24:17 MAX kernel: [ 2868.667757] EtherCAT DEBUG: 02
>> Feb 11 09:24:17 MAX kernel: [ 2868.667759] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.667760] EtherCAT DEBUG: 00 20 2F 00 16
>> 00 02 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.707743] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.707745] EtherCAT DEBUG: 00 30 60 00 16
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.707749] EtherCAT DEBUG 0-0:
>> Successfully configured mapping for PDO 0x1600.
>> Feb 11 09:24:17 MAX kernel: [ 2868.707751] EtherCAT DEBUG 0-0: Setting
>> PDO assignment of SM2:
>> Feb 11 09:24:17 MAX kernel: [ 2868.707752] EtherCAT DEBUG 0-0: Currently
>> assigned PDOs: 0x1601. PDOs to assign: 0x1600
>> Feb 11 09:24:17 MAX kernel: [ 2868.707756] EtherCAT DEBUG 0-0: Setting
>> number of assigned PDOs to zero.
>> Feb 11 09:24:17 MAX kernel: [ 2868.707758] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C12:00.
>> Feb 11 09:24:17 MAX kernel: [ 2868.707759] EtherCAT DEBUG: 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.707760] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.707761] EtherCAT DEBUG: 00 20 2F 12 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.747725] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.747727] EtherCAT DEBUG: 00 30 60 12 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.747733] EtherCAT DEBUG 0-0: Assigning
>> PDO 0x1600 at position 1.
>> Feb 11 09:24:17 MAX kernel: [ 2868.747735] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C12:01.
>> Feb 11 09:24:17 MAX kernel: [ 2868.747736] EtherCAT DEBUG: 00 16
>> Feb 11 09:24:17 MAX kernel: [ 2868.747739] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.747740] EtherCAT DEBUG: 00 20 2B 12 1C
>> 01 00 16 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.787713] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.787714] EtherCAT DEBUG: 00 30 60 12 1C
>> 01 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.787719] EtherCAT DEBUG 0-0: Setting
>> number of assigned PDOs to 1.
>> Feb 11 09:24:17 MAX kernel: [ 2868.787720] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C12:00.
>> Feb 11 09:24:17 MAX kernel: [ 2868.787721] EtherCAT DEBUG: 01
>> Feb 11 09:24:17 MAX kernel: [ 2868.787723] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.787724] EtherCAT DEBUG: 00 20 2F 12 1C
>> 00 01 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.827699] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.827701] EtherCAT DEBUG: 00 30 60 12 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.827707] EtherCAT DEBUG 0-0:
>> Successfully configured PDO assignment of SM2.
>> Feb 11 09:24:17 MAX kernel: [ 2868.827710] EtherCAT DEBUG 0-0: Reading
>> mapping of PDO 0x1A00.
>> Feb 11 09:24:17 MAX kernel: [ 2868.827713] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1A00:00.
>> Feb 11 09:24:17 MAX kernel: [ 2868.827714] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.827715] EtherCAT DEBUG: 00 20 40 00 1A
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.867685] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.867686] EtherCAT DEBUG: 00 30 4F 00 1A
>> 00 04 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.867691] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:17 MAX kernel: [ 2868.867692] EtherCAT DEBUG: 04
>> Feb 11 09:24:17 MAX kernel: [ 2868.867693] EtherCAT DEBUG 0-0: 4 PDO
>> entries mapped.
>> Feb 11 09:24:17 MAX kernel: [ 2868.867694] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1A00:01.
>> Feb 11 09:24:17 MAX kernel: [ 2868.867696] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.867696] EtherCAT DEBUG: 00 20 40 00 1A
>> 01 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.907679] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.907680] EtherCAT DEBUG: 00 30 43 00 1A
>> 01 10 00 41 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.907685] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:17 MAX kernel: [ 2868.907686] EtherCAT DEBUG: 10 00 41 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.907689] EtherCAT DEBUG 0-0: PDO entry
>> 0x6041:00, 16 bit, "???".
>> Feb 11 09:24:17 MAX kernel: [ 2868.907691] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1A00:02.
>> Feb 11 09:24:17 MAX kernel: [ 2868.907692] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.907693] EtherCAT DEBUG: 00 20 40 00 1A
>> 02 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.947660] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.947662] EtherCAT DEBUG: 00 30 43 00 1A
>> 02 20 00 64 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.947667] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:17 MAX kernel: [ 2868.947668] EtherCAT DEBUG: 20 00 64 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.947672] EtherCAT DEBUG 0-0: PDO entry
>> 0x6064:00, 32 bit, "???".
>> Feb 11 09:24:17 MAX kernel: [ 2868.947674] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1A00:03.
>> Feb 11 09:24:17 MAX kernel: [ 2868.947675] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.947676] EtherCAT DEBUG: 00 20 40 00 1A
>> 03 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2868.987649] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2868.987650] EtherCAT DEBUG: 00 30 43 00 1A
>> 03 08 00 61 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.987654] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:17 MAX kernel: [ 2868.987655] EtherCAT DEBUG: 08 00 61 60
>> Feb 11 09:24:17 MAX kernel: [ 2868.987658] EtherCAT DEBUG 0-0: PDO entry
>> 0x6061:00, 8 bit, "???".
>> Feb 11 09:24:17 MAX kernel: [ 2868.987659] EtherCAT DEBUG 0-0: Uploading
>> SDO 0x1A00:04.
>> Feb 11 09:24:17 MAX kernel: [ 2868.987660] EtherCAT DEBUG 0-0: Upload
>> request:
>> Feb 11 09:24:17 MAX kernel: [ 2868.987661] EtherCAT DEBUG: 00 20 40 00 1A
>> 04 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.027635] EtherCAT DEBUG 0-0: Upload
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.027637] EtherCAT DEBUG: 00 30 43 00 1A
>> 04 08 00 01 10
>> Feb 11 09:24:17 MAX kernel: [ 2869.027642] EtherCAT DEBUG 0-0: Uploaded
>> data:
>> Feb 11 09:24:17 MAX kernel: [ 2869.027643] EtherCAT DEBUG: 08 00 01 10
>> Feb 11 09:24:17 MAX kernel: [ 2869.027647] EtherCAT DEBUG 0-0: PDO entry
>> 0x1001:00, 8 bit, "???".
>> Feb 11 09:24:17 MAX kernel: [ 2869.027649] EtherCAT DEBUG 0-0: Changing
>> mapping of PDO 0x1A00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.027650] EtherCAT DEBUG 0-0: Currently
>> mapped PDO entries: 0x6041:00/16 0x6064:00/32 0x6061:00/8 0x1001:00/8.
>> Entries to map: 0x6041:00/16 0x6064:00/32 0x6061:00/8 0x1001:00/8
>> Feb 11 09:24:17 MAX kernel: [ 2869.027659] EtherCAT DEBUG 0-0: Setting
>> entry count to zero.
>> Feb 11 09:24:17 MAX kernel: [ 2869.027661] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.027662] EtherCAT DEBUG: 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.027664] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.027666] EtherCAT DEBUG: 00 20 2F 00 1A
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.067622] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.067623] EtherCAT DEBUG: 00 30 60 00 1A
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.067627] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x6041:00 (16 bit) at position 1.
>> Feb 11 09:24:17 MAX kernel: [ 2869.067629] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:01.
>> Feb 11 09:24:17 MAX kernel: [ 2869.067630] EtherCAT DEBUG: 10 00 41 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.067632] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.067633] EtherCAT DEBUG: 00 20 23 00 1A
>> 01 10 00 41 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.107614] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.107617] EtherCAT DEBUG: 00 30 60 00 1A
>> 01 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.107621] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x6064:00 (32 bit) at position 2.
>> Feb 11 09:24:17 MAX kernel: [ 2869.107623] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:02.
>> Feb 11 09:24:17 MAX kernel: [ 2869.107624] EtherCAT DEBUG: 20 00 64 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.107626] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.107627] EtherCAT DEBUG: 00 20 23 00 1A
>> 02 20 00 64 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.147593] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.147595] EtherCAT DEBUG: 00 30 60 00 1A
>> 02 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.147600] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x6061:00 (8 bit) at position 3.
>> Feb 11 09:24:17 MAX kernel: [ 2869.147602] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:03.
>> Feb 11 09:24:17 MAX kernel: [ 2869.147603] EtherCAT DEBUG: 08 00 61 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.147606] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.147607] EtherCAT DEBUG: 00 20 23 00 1A
>> 03 08 00 61 60
>> Feb 11 09:24:17 MAX kernel: [ 2869.187585] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.187586] EtherCAT DEBUG: 00 30 60 00 1A
>> 03 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.187590] EtherCAT DEBUG 0-0: Mapping
>> PDO entry 0x1001:00 (8 bit) at position 4.
>> Feb 11 09:24:17 MAX kernel: [ 2869.187592] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:04.
>> Feb 11 09:24:17 MAX kernel: [ 2869.187593] EtherCAT DEBUG: 08 00 01 10
>> Feb 11 09:24:17 MAX kernel: [ 2869.187595] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.187596] EtherCAT DEBUG: 00 20 23 00 1A
>> 04 08 00 01 10
>> Feb 11 09:24:17 MAX kernel: [ 2869.227574] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.227576] EtherCAT DEBUG: 00 30 60 00 1A
>> 04 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.227582] EtherCAT DEBUG 0-0: Setting
>> number of PDO entries to 4.
>> Feb 11 09:24:17 MAX kernel: [ 2869.227584] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1A00:00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.227585] EtherCAT DEBUG: 04
>> Feb 11 09:24:17 MAX kernel: [ 2869.227588] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.227589] EtherCAT DEBUG: 00 20 2F 00 1A
>> 00 04 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.267559] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.267560] EtherCAT DEBUG: 00 30 60 00 1A
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.267564] EtherCAT DEBUG 0-0:
>> Successfully configured mapping for PDO 0x1A00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.267566] EtherCAT DEBUG 0-0: Setting
>> PDO assignment of SM3:
>> Feb 11 09:24:17 MAX kernel: [ 2869.267568] EtherCAT DEBUG 0-0: Currently
>> assigned PDOs: 0x1A01. PDOs to assign: 0x1A00
>> Feb 11 09:24:17 MAX kernel: [ 2869.267571] EtherCAT DEBUG 0-0: Setting
>> number of assigned PDOs to zero.
>> Feb 11 09:24:17 MAX kernel: [ 2869.267573] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C13:00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.267574] EtherCAT DEBUG: 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.267575] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.267576] EtherCAT DEBUG: 00 20 2F 13 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.307546] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.307548] EtherCAT DEBUG: 00 30 60 13 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.307553] EtherCAT DEBUG 0-0: Assigning
>> PDO 0x1A00 at position 1.
>> Feb 11 09:24:17 MAX kernel: [ 2869.307555] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C13:01.
>> Feb 11 09:24:17 MAX kernel: [ 2869.307556] EtherCAT DEBUG: 00 1A
>> Feb 11 09:24:17 MAX kernel: [ 2869.307558] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.307559] EtherCAT DEBUG: 00 20 2B 13 1C
>> 01 00 1A 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.347534] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.347536] EtherCAT DEBUG: 00 30 60 13 1C
>> 01 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.347541] EtherCAT DEBUG 0-0: Setting
>> number of assigned PDOs to 1.
>> Feb 11 09:24:17 MAX kernel: [ 2869.347544] EtherCAT DEBUG 0-0:
>> Downloading SDO 0x1C13:00.
>> Feb 11 09:24:17 MAX kernel: [ 2869.347545] EtherCAT DEBUG: 01
>> Feb 11 09:24:17 MAX kernel: [ 2869.347547] EtherCAT DEBUG 0-0: Expedited
>> download request:
>> Feb 11 09:24:17 MAX kernel: [ 2869.347548] EtherCAT DEBUG: 00 20 2F 13 1C
>> 00 01 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.387521] EtherCAT DEBUG 0-0: Download
>> response:
>> Feb 11 09:24:17 MAX kernel: [ 2869.387522] EtherCAT DEBUG: 00 30 60 13 1C
>> 00 00 00 00 00
>> Feb 11 09:24:17 MAX kernel: [ 2869.387527] EtherCAT DEBUG 0-0:
>> Successfully configured PDO assignment of SM3.
>> Feb 11 09:24:17 MAX kernel: [ 2869.387532] EtherCAT DEBUG 0-0: SM2: Addr
>> 0x1600, Size 8, Ctrl 0x24, En 1
>> Feb 11 09:24:17 MAX kernel: [ 2869.387534] EtherCAT DEBUG 0-0: SM3: Addr
>> 0x1A00, Size 8, Ctrl 0x10, En 1
>> Feb 11 09:24:17 MAX kernel: [ 2869.407520] EtherCAT DEBUG 0 0:0: FMMU:
>> LogAddr 0x00000008, Size 8, PhysAddr 0x1600, SM2, Dir out
>> Feb 11 09:24:17 MAX kernel: [ 2869.407522] EtherCAT DEBUG 0 0:0: FMMU:
>> LogAddr 0x00000000, Size 8, PhysAddr 0x1A00, SM3, Dir in
>> Feb 11 09:24:17 MAX kernel: [ 2869.437507] EtherCAT 0: Domain 1: Working
>> counter changed to 1/1.
>> Feb 11 09:24:17 MAX kernel: [ 2869.447503] EtherCAT DEBUG 0-0: Now in
>> SAFEOP.
>> Feb 11 09:24:17 MAX kernel: [ 2869.477491] EtherCAT DEBUG 0-0: Now in OP.
>> Finished configuration.
>> Feb 11 09:24:17 MAX kernel: [ 2869.498564] EtherCAT 0: Slave states on
>> main device: OP.
>> Feb 11 09:24:20 MAX dhclient: DHCPDISCOVER on eth0 to 255.255.255.255
>> port 67 interval 20
>>
>> _______________________________________________
>> etherlab-users mailing list
>> etherlab-users at etherlab.org
>> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>>
>>
>
>
> --
> Jun Yuan
> [Aussprache: Djün Üän]
>
> Robotics Technology Leaders GmbH
> Am Loferfeld 58, D-81249 München
> Tel: +49 89 189 0465 24
> Mobile: +49 176 2176 5238
> Fax: +49 89 189 0465 11
> mailto: j.yuan at rtleaders.com
>
> Umlautregel in der chinesischen Lautschrift Pinyin: Nach den Anlauten y,
> j, q, und x wird u als ü ausgesprochen, z.B. yu => ü, ju => dschü, qu =>
> tschü, xu => schü.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20140212/ba74be0f/attachment-0003.htm>
More information about the Etherlab-users
mailing list