Once again, for 0x8000 use the ecrt_slave_config_sdo*() set and not the 
_complete()! Yes, subindex 0 does have a special meaning and I don't 
recall ever having the need to set subindex 0.

Then, try to reduce your SDO's to a bare minimum, leaving default values 
alone. There is a special startup tab in TwinCAT where you can see how 
and in which order TwinCAT configures the slave. Try to copy those 
commands -- only  those for 0x8000 and 0xf800, especially leaving out 
0x1C12 & 0x1C13 (which the master does for you).

Maybe try to start the slave without any SDO. Check the defaults and 
configure the DeviceNet Bus so that it fits the default values (128k 
baud, node 63, etc).

On 09/15/2014 04:12 PM, Carlos Herkt wrote:
> Hi,
> the documentation seems inconsistent. f800:10 and f800:11 are shown in
> TwinCATs CoE tab (see attachment) but not in the documentation.
> Anyway, we tried not to set f800:0,11,12: the result is another error
> message while writing 8000:0 :
>
> SDO download 0x8000 (110 bytes) aborted.
> SDO abort message 0x08000021: "Data cannot be transferred or stored to
> the application beaucse of local control".
> SDO configuration failed.
>
> and the green MNS led is not starting to blink. (When writing 0x0b to
> f800:0 the led starts blinking, but we are getting the timeout message)
>
> If we set the 8000:XY fields manually and not setting 8000:0, we're not
> getting the "cannot be transferred..." error but later the pdo
> assignment fails.
>
> It seems the subindex 0 has a "special" meaning for both of them.
>
> Even, when downloading values to 0x8000 with the ethercat tool, the
> device seems to not keep the values. See an example:
>
> [etherlab at EtherLab ~]$ sudo ./ethercat-tool -p5 --type uint16 download
> 0x8000 1 0x3f
> [etherlab at EtherLab ~]$ sudo ./ethercat-tool -p5 --type uint16 upload
> 0x8000 1
> 0x0000 0
>
>
> Kind regards
>
>
> Codesnippet:
> /**************************************************************************
> //ecrt_slave_config_sdo8(sc, 0xf800,  0, 0x0b);
>      ecrt_slave_config_sdo16(sc, 0xf800, 1, 0x003f);
>      ecrt_slave_config_sdo16(sc, 0xf800, 2, 0x0003);
>      ecrt_slave_config_sdo16(sc, 0xf800, 3, 0x006c);
>      ecrt_slave_config_sdo16(sc, 0xf800, 4, 0x000c);
>      ecrt_slave_config_sdo16(sc, 0xf800, 5, 0x0060);
>      ecrt_slave_config_sdo16(sc, 0xf800, 6, 0x1a01);
>      ecrt_slave_config_sdo32(sc, 0xf800, 7, 0x01785634);
>      //ecrt_slave_config_sdo8(sc, 0xf800, 8, 0x0b); //octet_string
> BECKHOFF EL6752-0000
>      ecrt_slave_config_sdo16(sc, 0xf800, 9, 0x0000);
>      //ecrt_slave_config_sdo8(sc, 0xf800, 10, 0x00);
>      //ecrt_slave_config_sdo8(sc, 0xf800, 11, 0x00);
>
>
>      //ecrt_slave_config_complete_sdo(sc, 0xf800, sdo_config_0xf800,
> sizeof(sdo_config_0xf800));
>      ecrt_slave_config_complete_sdo(sc, 0x8000, sdo_config_0x8000,
> sizeof(sdo_config_0x8000));
>
>      // ecrt_slave_config_sdo16(sc, 0x8000, 1, 0x003f);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x0D, 2);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x0E, 0x0064);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x10, 0x0064);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x11, 0x0014);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x17, 0x0014);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x1E, 0x0010);
>      // ecrt_slave_config_sdo16(sc, 0x8000, 0x1F, 0x0001);
>      // ecrt_slave_config_sdo8(sc, 0x8000, 0, 0x36);
> *************************************************************************/
>
>
>
> Am 15.09.2014 08:30, schrieb Richard Hacker:
>> The first thing is to try to get the slave into OP somehow: do not set
>> 0xf800:0, as well as subindices 10,11!! I do not see the latter in the
>> documentation!
>>
>> Then:
>> Have you tried to get the device running without using 0xF800? As far
>> as I can read from the documentation, it may be possible - the slave
>> address can also be set in 0x8000:there. Maybe that works (although I
>> am not a specialist in DeviceNet)
>>
>>
>>
>> On 09/12/2014 01:23 PM, Carlos Herkt wrote:
>>> Ok, we set the SDO's with the ecrt_slave_config_sdo8/16/32()
>>> functions...:
>>>
>>> //**************************************************************************
>>>
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  1, 0x003c);//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  2, 0x0003);//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  3, 0x006c);//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  4, 0x000c);//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  5, 0x0060);//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  6, 0x1a01);//
>>> //ecrt_slave_config_sdo32(sc, 0xf800,  7, 0x01785634);//
>>> ////ecrt_slave_config_sdo8(sc, 0xf800,  8, 0x0b); //octet_string
>>> BECKHOFF EL6752-0000//
>>> //ecrt_slave_config_sdo16(sc, 0xf800,  9, 0x0000);//
>>> //ecrt_slave_config_sdo8(sc, 0xf800,  10, 0x00);//
>>> //ecrt_slave_config_sdo8(sc, 0xf800,  11, 0x00);
>>> ///ecrt_slave_config_sdo8(sc, 0xf800,  0, 0x0b);//
>>> /***************************************************************************/
>>>
>>> /
>>> ...but still get the timeout error.
>>>
>>>> Try to set SDO's explicitly using Index:SubIndex by using the
>>>> ecrt_slave_config_sdo8/16/32() family of functions instead of complete
>>>> access. In fact this the preferred method of setting SDO's.
>>>>
>>>> On 09/11/2014 05:25 PM, Carlos Herkt wrote:
>>>>> Hello,
>>>>>
>>>>> referring to
>>>>> http://lists.etherlab.org/pipermail/etherlab-users/2014/002613.html we
>>>>> managed to set up our devices properly.
>>>>> We can communicate with our slaves on both devices (EL6631 &&
>>>>> EL66731)!
>>>>>
>>>>> Now we're trying to initialize the Beckhoff EL6752 the same way we
>>>>> did.
>>>>> But another error arose:
>>>>> /
>>>>> dmesg: "Timeout after 1000 ms while  waiting for SDO 0xf800:0 download
>>>>> response." /
>>>>>
>>>>> We doublechecked our configuration and everything seems alright.
>>>>>
>>>>> What does cause this failure?
>>>>>
>>>>> Is there a way to change that timeout?
>>>>>
>>>>> Any help is greatly appreciated.
>>>>>
>>>>> Best regards
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> etherlab-users mailing list
>>>>> etherlab-users at etherlab.org
>>>>> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>>>>>
>>>>
>>>> Mit freundlichem Gruß
>>>>
>>>> Richard Hacker
>>>>
>>>
>>
>> Mit freundlichem Gruß
>>
>> Richard Hacker
>>
>

Mit freundlichem Gruß

Richard Hacker

-- 
------------------------------------------------------------------------

Richard Hacker M.Sc.
richard.hacker at igh-essen.com
Tel.: +49 201 / 36014-16

Ingenieurgemeinschaft IgH
Gesellschaft für Ingenieurleistungen mbH
Heinz-Bäcker-Str. 34
D-45356 Essen

Amtsgericht Essen HRB 11500
USt-Id.-Nr.: DE 174 626 722
Geschäftsführung:
- Dr.-Ing. T. Finke,
- Dr.-Ing. W. Hagemeister
Tel.: +49 201 / 360-14-0
http://www.igh-essen.com

------------------------------------------------------------------------



More information about the Etherlab-users mailing list