[etherlab-users] Distributed Clocks

Richard Hacker ha at igh.de
Mon Feb 22 10:52:16 CET 2016


I do not have the patience to look into your code in detail to find out 
what you're doing wrong, but here is an excerpt of my code I use in 
etherlab Simulink Coder (ecrt_support.c):

void
ecs_send()
{
     //...

     list_for_each(master, &ecat_data.master_list, list) {
         list_for_each(domain, &master->domain_list, list) {
             // ...

             ecrt_domain_queue(domain->handle);
         }

         if (/* send frames */) {
             struct timespec tp;

             clock_gettime(CLOCK_MONOTONIC, &tp);
             ecrt_master_application_time(master->handle,
                     EC_TIMESPEC2NANO(tp));

             if (/* sync_clocks */)) {
                 ecrt_master_sync_reference_clock(master->handle);
                 //...
             }

             ecrt_master_sync_slave_clocks(master->handle);
             ecrt_master_send(master->handle);
         }
     }
}

void
ecs_receive()
{
     //...

     list_for_each(master, &ecat_data.master_list, list) {

         if (/* receive frames */) {
             ecrt_master_receive(master->handle);
         }

         list_for_each(domain, &master->domain_list, list) {

             ecrt_domain_process(domain->handle);
             ecrt_domain_state(domain->handle, &domain->state);

         }
     }
}

void
calculate()
{
     while (forever) {
         ecs_receive();
         // do calculations
         ecs_send();
         sleep();
     }
}

Some of this is pseudo code, but I trust in your programming 
capabilities to be able to adapt this to your code ;)

It is very important to call clock_gettime() and 
ecrt_master_application_time() as close to ecrt_master_send() as possible.

As you can see, it is not necessary to call 
ecrt_master_sync_reference_clock() with every ecrt_master_send(). In 
fact, ~100Hz of syncing should be enough, provided that your call to 
clock_gettime() is accurate. On the other hand, if clock_gettime() is 
inaccurate, you're in trouble when using DC anyway!

- Richard

Am 2016-02-22 um 04:23 schrieb Thomas Bitsky Jr:
> Ok, after following all your advice, plus the clock adjustment from
> Mattieu, I’m pretty close. I enable the DC on the drive, get everything
> into op, the domains all come up and it would appear that the clocks are
> syncing. Except for one thing:
>
> [10248.633619] EtherCAT 0: Domain 0: Working counter changed to 1/17.
> [10249.535776] EtherCAT WARNING 0: 3989 datagrams UNMATCHED!
> [10249.539861] EtherCAT WARNING: Datagram f3bf2d0c (domain0-0-main) was
> SKIPPED 1 time.
> [10249.539887] EtherCAT WARNING: Datagram f3bf2a8c (domain2-120-main)
> was SKIPPED 1 time.
> [10249.539918] EtherCAT WARNING: Datagram f3bf2e8c (domain1-114-main)
> was SKIPPED 1 time.
> [10249.635934] EtherCAT 0: Domain 0: 9 working counter changes - now 17/17.
> [10249.919163] EtherCAT 0: Domain 2: Working counter changed to 1/1.
> [10250.018245] EtherCAT 0: Domain 1: Working counter changed to 1/1.
> [10250.040259] EtherCAT 0: Slave states on main device: OP.
> [10250.536654] EtherCAT WARNING 0: 4001 datagrams UNMATCHED!
> [10251.537469] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10252.538282] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10252.538296] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10253.539097] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10254.539909] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10255.540723] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
> [10256.541537] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!<— This
> continues indefinitely
>
>
> Everything else seems okay:
>
> user at core:~/dist$ ethercat slaves
> 0  0:0  OP  +  EK1100 EtherCAT-Koppler (2A E-Bus)
> 1  0:1  OP  +  EL1104 4K. Dig. Eingang 24V, 3ms, Sensorversorgung
> 2  0:2  OP  +  EL1104 4K. Dig. Eingang 24V, 3ms, Sensorversorgung
> 3  0:3  OP  +  EL5101 1K. Inc. Encoder 5V
> 4  0:4  OP  +  EL7041 1K. Schrittmotor-Endstufe (50V, 5A)
> 5  0:5  OP  +  EL7041 1K. Schrittmotor-Endstufe (50V, 5A)
> 6  0:6  OP  +  EL2004 4K. Dig. Ausgang 24V, 0.5A
> 7  0:7  OP  +  EL2004 4K. Dig. Ausgang 24V, 0.5A
> 8  0:8  OP  +  EL4001 1K. Ana. Ausgang 0-10V, 12bit
> 9  1:0  OP  +  0x00000539:0x02200001
> user at core:~/dist$ ethercat master
> Master0
>    Phase: Operation
>    Active: yes
>    Slaves: 10
>    Ethernet devices:
>      Main: 00:30:18:c8:d4:92 (attached)
>        Link: UP
>        Tx frames:   5204542
>        Tx bytes:    733318966
>        Rx frames:   5204539
>        Rx bytes:    733318636
>        Tx errors:   0
>        Tx frame rate [1/s]:   4000   3944   2090
>        Tx rate [KByte/s]:    823.7  811.9  412.9
>        Rx frame rate [1/s]:   4000   3944   2090
>        Rx rate [KByte/s]:    823.7  811.9  412.9
>      Common:
>        Tx frames:   5204542
>        Tx bytes:    733318966
>        Rx frames:   5204539
>        Rx bytes:    733318636
>        Lost frames: 3
>        Tx frame rate [1/s]:   4000   3944   2090
>        Tx rate [KByte/s]:    823.7  811.9  412.9
>        Rx frame rate [1/s]:   4000   3944   2090
>        Rx rate [KByte/s]:    823.7  811.9  412.9
>        Loss rate [1/s]:          0      0      0
>        Frame loss [%]:         0.0    0.0    0.0
>    Distributed clocks:
>      Reference clock: Slave 0
>      Application time: 509424243322706771
>                        2016-02-22 02:44:03.322706771
>
>
>
>
>
>
> I must have something out of sync. Is there something more I’m supposed
> to do to adjust the clock? I can make the number of dropped packets
> worse by simplifying the time adjustment, but I can’t seem to get it any
> better. I think I’m not understanding something about the clock
> adjustment. Can you see what I’m doing wrong?
>
> Thanks!
>
> My cyclic task:
>
>
> static void
> sync_distributed_clocks(void)
> {
>      uint32_t ref_time = 0;
>      uint64_t prev_app_time = dc_time_ns;
>
>      dc_time_ns = system_time_ns();
>
>      // set master time in nano-seconds
>      ecrt_master_application_time(master_, dc_time_ns);
>
>      // get reference clock time to synchronize master cycle
>      ecrt_master_reference_clock_time(master_, &ref_time);
>      dc_diff_ns = (uint32_t) prev_app_time - ref_time;
>
>
>      // call to sync slaves to ref slave
>      ecrt_master_sync_slave_clocks(master_);
> }
>
> static unsigned int cycle_ns = 1000000;  // 1 millisecond
>
> void update_master_clock(void)
> {
>      // calc drift (via un-normalised time diff)
>      int32_t delta = dc_diff_ns - prev_dc_diff_ns;
>      prev_dc_diff_ns = dc_diff_ns;
>
>      // normalise the time diff
>      dc_diff_ns =
>          ((dc_diff_ns + (cycle_ns / 2)) % cycle_ns) - (cycle_ns / 2);
>
>      // only update if primary master
>      if (dc_started)
> {
>
>          // add to totals
>          dc_diff_total_ns += dc_diff_ns;
>          dc_delta_total_ns += delta;
>          dc_filter_idx++;
>
>          if (dc_filter_idx >= DC_FILTER_CNT)
> {
>              // add rounded delta average
>              dc_adjust_ns +=
>                  ((dc_delta_total_ns + (DC_FILTER_CNT / 2)) /
> DC_FILTER_CNT);
>
>              // and add adjustment for general diff (to pull in drift)
>              dc_adjust_ns += sign(dc_diff_total_ns / DC_FILTER_CNT);
>
>              // limit crazy numbers (0.1% of std cycle time)
>              if (dc_adjust_ns < -1000) {
>                  dc_adjust_ns = -1000;
>              }
>              if (dc_adjust_ns > 1000) {
>                  dc_adjust_ns =  1000;
>              }
>
>              // reset
>              dc_diff_total_ns = 0LL;
>              dc_delta_total_ns = 0LL;
>              dc_filter_idx = 0;
>          }
>
>          // add cycles adjustment to time base (including a spot adjustment)
>          system_time_base += dc_adjust_ns + sign(dc_diff_ns);
>      }
>      else
> {
>          dc_started = (dc_diff_ns != 0);
>
>          if (dc_started)
> {
>              // output first diff
>              PRINT("First master diff: %d.\n", dc_diff_ns);
>
>              // record the time of this initial cycle
>              dc_start_time_ns = dc_time_ns;
>          }
>      }
>
> }
>
>
> int
>
> ecatMain_process(void* lp)
>
> {
>
>
> sync_distributed_clocks();
>
> update_master_clock();
>
>
> ecrt_master_receive(master_);
>
> ecrt_domain_process(lrwDomainMgr_.domain);
>
> ecrt_domain_process(noLrwWriteDomainMgr_.domain);
>
> ecrt_domain_process(noLrwReadDomainMgr_.domain);
>
> … // handle my business
>
>
> // send process data
>
> ecrt_domain_queue(lrwDomainMgr_.domain);
>
> ecrt_domain_queue(noLrwWriteDomainMgr_.domain);
>
> ecrt_domain_queue(noLrwReadDomainMgr_.domain);
>
> // send EtherCAT data
>
> ecrt_master_send(master_);
>
> return 1;
>
> }
>
>
>
>
> I made my sync0 time half of the can rate, as you prescribed:
>
> void
> ecatModule_registerDcClock( Slave* slave, uint16_t addr )
> {
> struct timespec cur_time;
> clock_gettime(CLOCK_REALTIME, &cur_time);
> uint16_t sync0time = (uint16_t)((globalScanRate_us * 1000) / 2);
> ecrt_slave_config_dc(
> slave->sc,
> addr,
> (globalScanRate_us * 1000),
> sync0time,
> 0,
> 0);
> }
>
>
>
>
>
> From: Graeme Foot <Graeme.Foot at touchcut.com
> <mailto:Graeme.Foot at touchcut.com>>
> Date: Sunday, February 21, 2016 at 4:07 PM
> To: Thomas Bitsky <tbj at automateddesign.com <mailto:tbj at automateddesign.com>>
> Cc: "etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>"
> <etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>>
> Subject: RE: Distributed Clocks
>
> Hi,
>
> I build and patch against revision 2526, so don’t know what patches /
> fixes have made it through to the latest release.  However for my
> revision I need fixes for reference clock selections and dc
> synchronization issues.
>
> I’ve attached the dc related patches I use, but these are applied after
> some other patches so you may get some conflicts or offsetting.
>
> *01 - Distributed Clock fixes and helpers.patch*
>
> This sorts out some ref slave issues, allowing a user selected ref
> slave.  It also adds some helper functions:
>
> - ecrt_master_setup_domain_memory() : this allows me to set up the
> domain memory and do stuff with it before calling ecrt_master_activate()
> (for user space apps)
>
> - ecrt_master_deactivate_slaves() : this lets me deactivate the slaves
> while still in realtime to avoid the slaves getting some shutdown sync
> errors
>
> *02 - Distributed Clock fixes from Jun Yuan - dc sync issues.patch*
>
> This sorts out some timing issues to do with slave dc syncing.  Without
> it they can start syncing from one cycle out causing a large syncing
> time overhead, one slave at a time.
>
> Regards,
>
> Graeme.
>
> *From:*Thomas Bitsky Jr [mailto:tbj at automateddesign.com]
> *Sent:* Sunday, 21 February 2016 10:27 a.m.
> *To:* Graeme Foot
> *Cc:* etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>
> *Subject:* Re: Distributed Clocks
>
> Graeme,
>
> Thank you so much for the detailed response. I'm away from my computer
> right now, so I can't try out your advice, but I noticed you asked about
> patches. I am not running any patches; which should I get?
>
> Thanks!
> Thomas Bitsky Jr
>
> On Feb 20, 2016, at 3:04 PM, Graeme Foot <Graeme.Foot at touchcut.com
> <mailto:Graeme.Foot at touchcut.com>> wrote:
>
>     Hi,
>
>     The slave clocks get synced via the distributed clock system using
>     the master methods: ecrt_master_reference_clock_time(),
>     ecrt_master_sync_slave_clocks(), ecrt_master_application_time(),
>     ecrt_master_sync_reference_clock().
>
>     However each individual slave can choose (if it is capable of it)
>     whether to synchronize its reading and writing of data to a
>     particular point in time within the dc cycle.  If that slave does
>     not choose to do so then the reading and writing of the data occurs
>     at the time the EtherCAT frame goes past, resulting in a progressive
>     update and application of data as the frame progresses through all
>     of the slaves.
>
>     If a slave is registered to use the dc clock then it caches the
>     frame data until the sync0 interrupt so in theory all dc slaves
>     apply the data at the same time.  It also means you don’t have to
>     worry about jitter as to the time the frame is sent over the wire.
>     The only thing is to choose a good sync0 time to ensure your frames
>     are always sent out and have reached all of the slaves before the
>     sync0 time occurs, and that the next frame is not sent out before
>     the previous sync0 time occurs.
>
>     In my application my cycle time is 1000us.  I choose a sync0 time of
>     500us.  I also send my frame as close as possible to the beginning
>     of the cycle. This gives the frame up to half the cycle time to
>     reach all of the slaves and then the other half of the cycle for the
>     frame to return in time for the master receive call.  I could choose
>     a sync0 time later than 500us but I want it processed as soon as
>     possible after the frame is received while still allowing for a bus
>     with a large number of terminals.
>
>     So below where you are calculating loop_shift based on the current
>     time is wrong.  Just choose a time within the dc cycle and use that
>     value for all slaves.  Note: the beginning of the dc cycle is in
>     phase with the first call to ecrt_master_application_time(), so all
>     of your realtime looping should also be in phase with that initial time.
>
>     Note, when selecting a slave to be the DC reference slave you should
>     generally choose the first slave on your bus, regardless of whether
>     it will be (or can be) registered to use the dc synchronization.  At
>     the very least it must be before, or be the, first slave that will
>     be registered as a dc slave.
>
>     Also note that some slaves clocks are not very stable and shouldn’t
>     be used as the DC reference slave.  My original testing was on a
>     Beckhoff CX1020 with a CX1100-0004, this could not be used as a
>     reference slave as its clock was not stable.
>
>     I see you are configuring the slaves via ecrt_slave_config_*()then
>     calling ecrt_slave_config_pdos()at the end.  If you call
>     ecrt_slave_config_pdos() at the beginning you don’t need all the
>     other config calls. However I hear AKD drives and some other slaves
>     prefer explicit slave config calls but most slaves are happy with
>     just the ecrt_slave_config_reg_pdo_entry()methods.
>
>     This also leads to another issue.  One of the configured PDO items
>     is the “mode of operation” value (0x6060 0x00).  You are also
>     configuring this with: ecrt_slave_config_sdo8( sc, 0x6060, 0, 8 ).
>     This value should be instead be set via the PDO value.  Use
>     ecrt_slave_config_reg_pdo_entry()to get the offset to the value and
>     set the value there.
>
>     Sorry if that was a bit long but DC’s is not an easy topic to get
>     your head around.  Here’s a bit of a summary:
>
>     - You can choose which slaves get registered with
>     ecrt_slave_config_dc(). But each slave you want synced must get its
>     own call to ecrt_slave_config_dc().
>
>     - If your yaskawa drives get to OP without
>     ecrt_slave_config_dc()then they should get to OP with
>     ecrt_slave_config_dc().
>
>     - The yaskawa drives require a very stable reference slave time,
>     which is why we sync the EtherCAT master to the reference slave
>     rather than the other way around.
>
>     And some other comments:
>
>     - Never use anEL9010 endcap module.  These break the distributed
>     clock calculations.  I don’t think they are available anymore though.
>
>     - There are some patches out there that fix various DC clock issues,
>     are you using any of these?
>
>     Regards,
>
>     Graeme.
>
>     *From:*Thomas Bitsky Jr [mailto:tbj at automateddesign.com]
>     *Sent:* Sunday, 21 February 2016 7:15 a.m.
>     *To:* Graeme Foot; etherlab-users at etherlab.org
>     <mailto:etherlab-users at etherlab.org>
>     *Subject:* Re: Distributed Clocks
>
>     [snip]
>
>     I’ve never been able to get the EL7041 stepper modules to work in dc
>     mode.
>
>     [/snip]
>
>     Is it all or nothing? I need the servo drives, the LVDT and the
>     EL3356 tied to a distributed clock. The EL7041 is optional for me.
>
>     [snip]
>
>     I don’t see in your code calls to ecrt_slave_config_dc().
>
>     For the yaskawa drive, during the config stage, I use the following
>     calls…
>
>     [/snip]
>
>     Forgot to put that part; my bad. This is what I had for the
>     Yaskawa/AKD, although I was only doing it to one of the drives. I
>     thought I was supposed to set up one distributed clock, and it
>     became the master and handled the rest. Am I supposed to do this for
>     all the cards, or do I select?
>
>     Yaskawa(AKD drive code is pretty much the same):
>
>        if (!(sc = ecrt_master_slave_config(
>
>                          master,
>
>     slavePosDomain,
>
>     slavePosIndex,
>
>     vendorId, productCode)))
>
>     {
>
>     return FALSE;
>
>          }
>
>     ecrt_slave_config_sdo8( sc, 0x1C12, 0, 0 ); /* clear sm pdo 0x1c12 */
>
>     ecrt_slave_config_sdo8( sc, 0x1C13, 0, 0 ); /* clear sm pdo 0x1c12 */
>
>     ecrt_slave_config_sdo8( sc, 0x1A00, 0, 0 ); /* clear TxPDO0 */
>
>     ecrt_slave_config_sdo8( sc, 0x1A01, 0, 0 ); /* clear TxPDO1 */
>
>     ecrt_slave_config_sdo8( sc, 0x1A02, 0, 0 ); /* clear TxPDO2 */
>
>     ecrt_slave_config_sdo8( sc, 0x1A03, 0, 0 ); /* clear TxPDO3 */
>
>     ecrt_slave_config_sdo8( sc, 0x1600, 0, 0 ); /* number of var in this
>     PDO */
>
>     ecrt_slave_config_sdo8( sc, 0x1601, 0, 0 ); /* clear RxPdo 0x1601 */
>
>          ecrt_slave_config_sdo8( sc, 0x1602, 0, 0 ); /* clear RxPdo
>     0x1602 */
>
>          ecrt_slave_config_sdo8( sc, 0x1603, 0, 0 ); /* clear RxPdo
>     0x1603 */
>
>     ecrt_slave_config_sdo8( sc, 0x1A00, 0, 0 ); /* clear TxPDO0 */
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 1, 0x60410010 ); // Status word
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 2,0x60640020 );// Position
>     actual value, per encoder
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 3,0x60770010 );// Torque,
>     actual value
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 4,0x60F40020 );// Following
>     error, actual value
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 5,0x60610008 );// Modes of
>     operation display
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 6,0x00000008 );// GAP
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 7,0x60B90010 );// Touch probe
>     status
>
>     ecrt_slave_config_sdo32( sc, 0x1A00, 8, 0x60BA0020 ); // Touch probe
>     1 position
>
>     ecrt_slave_config_sdo8( sc, 0x1A00, 0, 8 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1A01, 0, 0 ); /* clear TxPDO1 */
>
>     ecrt_slave_config_sdo32( sc, 0x1A01,1,0x60410010 ); // Status word
>
>     ecrt_slave_config_sdo32( sc, 0x1A01,2,0x60640020 );// Position
>     actual value, per encoder
>
>     ecrt_slave_config_sdo8( sc, 0x1A01, 0, 2 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1A02, 0, 0 ); /* clear TxPDO2 */
>
>     ecrt_slave_config_sdo32( sc, 0x1A02,1,0x60410010 ); // Status word
>
>     ecrt_slave_config_sdo32( sc, 0x1A02,2,0x60640020 );// Position
>     actual value, per encoder
>
>     ecrt_slave_config_sdo8( sc, 0x1A02, 0, 2 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1A03, 0, 0 ); /* clear TxPDO2 */
>
>     ecrt_slave_config_sdo32( sc, 0x1A03,1,0x60410010 ); // Status word
>
>     ecrt_slave_config_sdo32( sc, 0x1A03,2,0x60640020 );// Position
>     actual value, per encoder
>
>     ecrt_slave_config_sdo32( sc, 0x1A03,3,0x60770010 );// Torque, actual
>     value
>
>     ecrt_slave_config_sdo8( sc, 0x1A03, 0, 3 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1600, 0, 0 ); /* clear entries */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 1, 0x60400010  ); /* control
>     word */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 2, 0x607A0020  ); /* target
>     position */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 3, 0x60FF0020  ); /* target
>     velocity */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 4, 0x60710010  ); /* target
>     torque */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 5, 0x60720010  ); /* max torque */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 6, 0x60600008  ); /* modes of
>     operation */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 7, 0x00000008  ); /* gap */
>
>     ecrt_slave_config_sdo32( sc, 0x1600, 8, 0x60B80010  ); /* touch
>     probe function */
>
>     ecrt_slave_config_sdo8(sc, 0x1600, 0, 8 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1601, 0, 0 ); /* clear entries */
>
>     ecrt_slave_config_sdo32( sc, 0x1601, 1, 0x60400010  ); /* control
>     word */
>
>     ecrt_slave_config_sdo32( sc, 0x1601, 2, 0x607A0020  ); /* target
>     position */
>
>     ecrt_slave_config_sdo8( sc, 0x1601, 0, 2 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1602, 0, 0 ); /* clear entries */
>
>     ecrt_slave_config_sdo32( sc, 0x1602, 1, 0x60400010  ); /* control
>     word */
>
>     ecrt_slave_config_sdo32( sc, 0x1602, 2, 0x60FF0020  ); /* target
>     position */
>
>     ecrt_slave_config_sdo8( sc, 0x1602, 0, 2 ); /* pdo entries */
>
>     ecrt_slave_config_sdo8( sc, 0x1603, 0, 0 ); /* clear entries */
>
>     ecrt_slave_config_sdo32( sc, 0x1603, 1, 0x60400010  ); /* control
>     word */
>
>     ecrt_slave_config_sdo32( sc, 0x1603, 2, 0x60710020  ); /* target
>     position */
>
>     ecrt_slave_config_sdo8( sc, 0x1603, 0, 2 ); /* pdo entries */
>
>     ecrt_slave_config_sdo16( sc, 0x1C12, 1, 0x1601 ); /* download pdo
>     1C12 index */
>
>     ecrt_slave_config_sdo8( sc, 0x1C12, 0, 1 ); /* set number of RxPDO */
>
>     ecrt_slave_config_sdo16( sc, 0x1C13, 1, 0x1A01 ); /* download pdo
>     1C13 index */
>
>     ecrt_slave_config_sdo8( sc, 0x1C13, 0, 1 ); /* set number of TxPDO */
>
>     // OPMODE
>
>     // Yaskawa recommends 8
>
>     ecrt_slave_config_sdo8( sc, 0x6060, 0, 8 );
>
>     unsigned char interpolationTime = 0xFF;
>
>     // 250
>
>     unsigned char cycleExponent = 0xFA;
>
>     // microseconds
>
>     // globalSCanRate_us equals either 250 or 125.
>
>     unsigned int us = globalScanRate_us;
>
>     size_t i;
>
>     for ( i=0;i<6, us > 0xFF;++i )
>
>     {
>
>     us /= 10;
>
>     cycleExponent += 1;
>
>     }
>
>     interpolationTime = us;
>
>     ecrt_slave_config_sdo8( akd->sc_akd, 0x60C2, 1, interpolationTime );
>     /* Interpolation time */
>
>     ecrt_slave_config_sdo8( akd->sc_akd, 0x60C2, 2, cycleExponent ); /*
>     Cycle exponent */
>
>          PRINT("Configuring PDOs...\n");
>
>          if (ecrt_slave_config_pdos(sc, EC_END, slave_syncs))
>
>     {
>
>     PRINT("Failed to configure Yaskawa Sigma PDOs.\n");
>
>              return FALSE;
>
>          }
>
>     *struct timespec cur_time;*
>
>     *clock_gettime(CLOCK_REALTIME, &cur_time);*
>
>     *size_t loop_period = globalScanRate_us * 1000;*
>
>     *if ( loop_period == 0 ) loop_period = 1;*
>
>     *size_t loop_shift *
>
>     *= loop_period - (cur_time.tv_nsec % loop_period);*
>
>     *ecrt_slave_config_dc(*
>
>     *sc, *
>
>     *0x0300, *
>
>     *loop_period, *
>
>     *loop_shift, *
>
>     *0, *
>
>     *0);*
>
>     For the EL3356, would I then?
>
>     KL3356StrainGauge* sg = (KL3356StrainGauge*)slave->instance;
>
>     printf( "Begin kl3356_ecConfigure...\n");
>
>     //
>
>     // Create the slave configuration
>
>     //
>
>     if (!(sg->sc = ecrt_master_slave_config(
>
>     master,
>
>     slavePosDomain, slavePosIndex, // Bus position
>
>     vendorId, productCode
>
>     // Slave type
>
>     )))
>
>     {
>
>     printf(
>
>     "kl3356_ecConfigure -- Failed to get slave configuration.\n");
>
>         return FALSE;
>
>     }
>
>     //
>
>     // Register startup configuration for the hardware
>
>     //
>
>     ecrt_slave_config_sdo8( sg->sc, 0x1C12, 0, 0 ); /* clear sm pdo
>     0x1c12 */
>
>     ecrt_slave_config_sdo8( sg->sc, 0x1C13, 0, 0 ); /* clear sm pdo
>     0x1c12 */
>
>     ecrt_slave_config_sdo16( sg->sc, 0x1C12, 1, 0x1600 ); /* download
>     pdo 1C12 index */
>
>     ecrt_slave_config_sdo8( sg->sc, 0x1C12, 0, 1 ); /* set number of
>     RxPDO */
>
>     ecrt_slave_config_sdo16( sg->sc, 0x1C13, 1, 0x1A00 ); /* download
>     pdo 1C13 index */
>
>     ecrt_slave_config_sdo16( sg->sc, 0x1C13, 2, 0x1A02 ); /* download
>     pdo 1C13 index */
>
>     ecrt_slave_config_sdo8( sg->sc, 0x1C13, 0, 2 ); /* set number of
>     TxPDO */
>
>     //
>
>     // Configure the hardware's PDOs
>
>     //
>
>     if (ecrt_slave_config_pdos(sg->sc, EC_END, kl3356_syncs))
>
>     {
>
>         printf(
>
>     "kl3356_ecConfigure -- Failed to configure PDOs.\n");
>
>         return FALSE;
>
>          }
>
>     *struct timespec cur_time;*
>
>     *clock_gettime(CLOCK_REALTIME, &cur_time);*
>
>     *size_t loop_period = globalScanRate_us * 1000;*
>
>     *if ( loop_period == 0 ) loop_period = 1;*
>
>     *size_t loop_shift *
>
>     *= loop_period - (cur_time.tv_nsec % loop_period);*
>
>     *ecrt_slave_config_dc(*
>
>     *s**g->sc, *
>
>     *0x0300, *
>
>     *loop_period, *
>
>     *loop_shift, *
>
>     *0, *
>
>     *0);*
>
>     Thanks!
>
>     Thomas C. Bitsky Jr. | Lead Developer
>
>     ADC | automateddesign.com <http://automateddesign.com/>
>
>     P: 630-783-1150 F: 630-783-1159 M: 630-632-6679
>
>     Follow ADC news and media:
>
>     Facebook <https://facebook.com/automateddesigncorp> | Twitter
>     <https://twitter.com/ADCSportsLogic> | YouTube
>     <https://www.youtube.com/user/ADCSportsLogic>
>
>     *From: *Graeme Foot <Graeme.Foot at touchcut.com
>     <mailto:Graeme.Foot at touchcut.com>>
>     *Date: *Friday, February 19, 2016 at 7:24 PM
>     *To: *Thomas Bitsky <tbj at automateddesign.com
>     <mailto:tbj at automateddesign.com>>, "etherlab-users at etherlab.org
>     <mailto:etherlab-users at etherlab.org>" <etherlab-users at etherlab.org
>     <mailto:etherlab-users at etherlab.org>>
>     *Subject: *RE: Distributed Clocks
>
>     Hi,
>
>     I don’t see in your code calls to ecrt_slave_config_dc().
>
>     For the yaskawa drive, during the config stage, I use the following
>     calls:
>
>          // set interpolation time period (free run mode)
>
>          // where 0x60C2 is time in seconds = (0x60C2, 0x01) x
>     10^(0x60C2, 0x02)
>
>          // eg period of 1ms:
>
>          //   (0x60C2, 0x01) = 1
>
>          //   (0x60C2, 0x02) = -3
>
>          // => 1 x 10^(-3) = 0.001s
>
>          ecrt_slave_config_sdo8(dev->slaveConfig, 0x60C2, 0x01,
>     (uint8_t)g_app.scanTimeMS);
>
>          ecrt_slave_config_sdo8(dev->slaveConfig, 0x60C2, 0x02,
>     (int8_t)(-3));
>
>          // set up the distributed clock
>
>          // 0x0000 = free run, 0x0300 = dc
>
>          // (Supported DC cycle: 125us to 4ms (every 125us cycle))
>
>          ecrt_slave_config_dc(dev->slaveConfig, 0x0300,
>     g_app.scanTimeNS, 500000, 0, 0);
>
>     0x60C2 shouldn’t be necessary for dc mode, but I used it before I
>     had dc mode working and have never tried it without and it doesn’t
>     harm anything having it in.
>
>     The second value that is being passed to the
>     ecrt_slave_config_dcmethod is a value that is written to the ESC
>     register 0x980. The Yaskawa SGDV doco says this value should be
>     0x0000 for free run mode and 0x0300 for dc mode.  Other ESC’s may
>     required different values.
>
>     I’ve never been able to get the EL7041 stepper modules to work in dc
>     mode.
>
>     Graeme.
>
>     *From:*etherlab-users [mailto:etherlab-users-bounces at etherlab.org]
>     *On Behalf Of *Thomas Bitsky Jr
>     *Sent:* Saturday, 20 February 2016 1:09 p.m.
>     *To:* etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>
>     *Subject:* [etherlab-users] Distributed Clocks
>
>     Hello.
>
>     I’ve been using the EtherCAT master for years to great success, but
>     I’m stuck on a problem I can’t figure out that I think several
>     people here are doing successfully. I can’t implement distributed
>     clocks in my application.
>
>     I am having the same problem on two systems I have up and running:
>
>     SYSTEM ONE:
>
>     EtherLAB Master 1.52, E1000E Driver, Scan Rate 4Khz, Ubuntu Server
>     14.04LTS, RT-PREEMPT 3.12.50-rt68
>
>     alias=0, position=0, device=EK1100
>
>     alias=0, position=1, device=EL1104
>
>     alias=0, position=2, device=EL2004
>
>     alias=0, position=3, device=EL9510
>
>     alias=0, position=4, device=EL3356
>
>     alias=0, position=5, device=Kollmorgen AKD
>
>     alias=0, position=6, device=MTS LVDT
>
>     SYSTEM TWO:
>
>     EtherLAB Master 1.52, E1000E Driver, Scan Rate 8Khz, Ubuntu Server
>     14.04LTS, RT-PREEMPT 3.12.50-rt68
>
>     alias=0, position=0, device=EK1100
>
>     alias=0, position=1, device=EL3001
>
>     alias=0, position=2, device=EL1104
>
>     alias=0, position=3, device=EL1104
>
>     alias=0, position=4, device=EL1104
>
>     alias=0, position=5, device=EL2004
>
>     alias=0, position=6, device=EL2004
>
>     alias=0, position=7, device=EL9505
>
>     alias=0, position=8, device=EL7041
>
>     alias=0, position=9, device=EL7041
>
>     alias=0, position=10, device=EL7041
>
>     alias=0, position=11, device=EL7041
>
>     alias=0, position=12, device=EL7041
>
>     alias=0, position=13, device=EL7041
>
>     alias=0, position=14, device=EK1110
>
>     alias=1, position=0, device=SIGMA5-05
>
>     alias=2, position=0, device=Yaskawa SIGMA5-05
>
>     alias=3, position=0, device=Yaskawa SIGMA5-05
>
>     Both of the system are fully operational. However, for various
>     reasons, I need to implement distributed clocks on these systems.
>     I’ve never been able to get this to work.
>
>     What follows is the code I used for both systems to try this. I read
>     through examples on the mailing list, plus the examples, but I’m not
>     seeing what I’m doing wrong. The result is always the same: all the
>     fieldbus cards go into operation, but the servo drives won’t because
>     of “bad configuration.” Take out the distributed clock code, and
>     they work fine. I’m getting away with it for now, but I do need
>     better clock resolution.
>
>     The systems have an LRW domain, then a separate read domain and
>     write domain for the servo drive(s) for a total of three domains
>     (LRW, read, write). The yaskawa drives necessitate this. The scan
>     rate is usually 4Khz, but I have tried it at both 1Khz and 8Khz and
>     gotten the same results. Everything about the implementation is
>     fairly straight-forward. There’s just something fundamental about
>     the DC configuration that I’m not understanding.
>
>     Almost all the code below is taken right from the examples or the
>     message boards (thanks, everybody!). If anyone could tell me what
>     I’m going wrong or offer any insights, it’s greatly appreciated. For
>     brevity, I tried to narrow it down to relevant parts, but please let
>     me know any additional information or code I can provide.
>
>     Thank you in advance,
>
>     Tom
>
>     **********************************************************
>
>     // EtherCAT distributed clock variables
>
>     #define DC_FILTER_CNT          1024
>
>     #define SYNC_MASTER_TO_REF        1
>
>     static uint64_t dc_start_time_ns = 0LL;
>
>     static uint64_t dc_time_ns = 0;
>
>     static uint8_t  dc_started = 0;
>
>     static int32_t  dc_diff_ns = 0;
>
>     static int32_t  prev_dc_diff_ns = 0;
>
>     static int64_t  dc_diff_total_ns = 0LL;
>
>     static int64_t  dc_delta_total_ns = 0LL;
>
>     static int      dc_filter_idx = 0;
>
>     static int64_t  dc_adjust_ns;
>
>     static int64_t  system_time_base = 0LL;
>
>     static uint64_t wakeup_time = 0LL;
>
>     static uint64_t overruns = 0LL;
>
>     /** Get the time in ns for the current cpu, adjusted by
>     system_time_base.
>
>       *
>
>       * \attention Rather than calling rt_get_time_ns() directly, all
>     application
>
>       * time calls should use this method instead.
>
>       *
>
>       * \ret The time in ns.
>
>       */
>
>     uint64_t system_time_ns(void)
>
>     {
>
>     struct timespec ts;
>
>     clock_gettime(GLOBAL_CLOCK_TO_USE, &ts);
>
>     return TIMESPEC2NS(ts);
>
>     }
>
>     static
>
>     void sync_distributed_clocks(void)
>
>     {
>
>          uint32_t ref_time = 0;
>
>          uint64_t prev_app_time = dc_time_ns;
>
>          dc_time_ns = system_time_ns();
>
>          // set master time in nano-seconds
>
>          ecrt_master_application_time(master_, dc_time_ns);
>
>          // get reference clock time to synchronize master cycle
>
>          ecrt_master_reference_clock_time(master_, &ref_time);
>
>          dc_diff_ns = (uint32_t) prev_app_time - ref_time;
>
>          // call to sync slaves to ref slave
>
>          ecrt_master_sync_slave_clocks(master_);
>
>     }
>
>     /** Return the sign of a number
>
>       *
>
>       * ie -1 for -ve value, 0 for 0, +1 for +ve value
>
>       *
>
>       * \retval the sign of the value
>
>       */
>
>     #define sign(val) \
>
>          ({ typeof (val) _val = (val); \
>
>          ((_val > 0) - (_val < 0)); })
>
>     /*****************************************************************************/
>
>     /** Update the master time based on ref slaves time diff
>
>       *
>
>       * called after the ethercat frame is sent to avoid time jitter in
>
>       * sync_distributed_clocks()
>
>       */
>
>     static unsigned int cycle_ns = 1000000;  // 1 millisecond
>
>     void update_master_clock(void)
>
>     {
>
>          // calc drift (via un-normalised time diff)
>
>          int32_t delta = dc_diff_ns - prev_dc_diff_ns;
>
>          prev_dc_diff_ns = dc_diff_ns;
>
>          // normalise the time diff
>
>          dc_diff_ns =
>
>              ((dc_diff_ns + (cycle_ns / 2)) % cycle_ns) - (cycle_ns / 2);
>
>          // only update if primary master
>
>          if (dc_started) {
>
>              // add to totals
>
>              dc_diff_total_ns += dc_diff_ns;
>
>              dc_delta_total_ns += delta;
>
>              dc_filter_idx++;
>
>              if (dc_filter_idx >= DC_FILTER_CNT) {
>
>                  // add rounded delta average
>
>                  dc_adjust_ns +=
>
>                      ((dc_delta_total_ns + (DC_FILTER_CNT / 2)) /
>     DC_FILTER_CNT);
>
>                  // and add adjustment for general diff (to pull in drift)
>
>                  dc_adjust_ns += sign(dc_diff_total_ns / DC_FILTER_CNT);
>
>                  // limit crazy numbers (0.1% of std cycle time)
>
>                  if (dc_adjust_ns < -1000) {
>
>                      dc_adjust_ns = -1000;
>
>                  }
>
>                  if (dc_adjust_ns > 1000) {
>
>                      dc_adjust_ns =  1000;
>
>                  }
>
>                  // reset
>
>                  dc_diff_total_ns = 0LL;
>
>                  dc_delta_total_ns = 0LL;
>
>                  dc_filter_idx = 0;
>
>              }
>
>              // add cycles adjustment to time base (including a spot
>     adjustment)
>
>              system_time_base += dc_adjust_ns + sign(dc_diff_ns);
>
>          }
>
>          else {
>
>              dc_started = (dc_diff_ns != 0);
>
>              if (dc_started)
>
>     {
>
>                  // record the time of this initial cycle
>
>                  dc_start_time_ns = dc_time_ns;
>
>              }
>
>          }
>
>     }
>
>     struct timespec dcTime_;
>
>     int
>
>     ecatMain_process(void* lp)
>
>     {
>
>     ecrt_master_receive(master_);
>
>     clock_gettime(CLOCK_REALTIME, &dcTime_);
>
>     ecrt_master_application_time(master_, TIMESPEC2NS(dcTime_));
>
>     ecrt_master_sync_reference_clock(master_);
>
>     ecrt_master_sync_slave_clocks(master_);
>
>     ecrt_domain_process(lrwDomainMgr_.domain);
>
>     ecrt_domain_process(noLrwWriteDomainMgr_.domain);
>
>     ecrt_domain_process(noLrwReadDomainMgr_.domain);
>
>     … // handle my business
>
>     // write application time to master
>
>     clock_gettime(CLOCK_REALTIME, &dcTime_);
>
>     ecrt_master_application_time(master_, TIMESPEC2NS(dcTime_));
>
>     if (sync_ref_counter_)
>
>     {
>
>     sync_ref_counter_--;
>
>     }
>
>     else
>
>     {
>
>     sync_ref_counter_ = 1; // sync every cycle
>
>     ecrt_master_sync_reference_clock(master_);
>
>     }
>
>     // send process data
>
>     ecrt_domain_queue(lrwDomainMgr_.domain);
>
>     ecrt_domain_queue(noLrwWriteDomainMgr_.domain);
>
>     ecrt_domain_queue(noLrwReadDomainMgr_.domain);
>
>     // sync distributed clock just before master_send to set
>
>     // most accurate master clock time
>
>     sync_distributed_clocks();
>
>     // send EtherCAT data
>
>     ecrt_master_send(master_);
>
>     // update the master clock
>
>     // Note: called after ecrt_master_send() to reduce time
>
>     // jitter in the sync_distributed_clocks() call
>
>     update_master_clock();
>
>     return 1;
>
>     }
>
>     int
>
>     ecatMain_start(void* lp)
>
>     {
>
>     //
>
>     // domain regs must end in a null entry
>
>     //
>
>     lrwDomainMgr_.domainRegs = realloc(
>
>     lrwDomainMgr_.domainRegs,
>
>     sizeof(ec_pdo_entry_reg_t) * (lrwDomainMgr_.size + 1)  );
>
>     memset(
>
>     &(lrwDomainMgr_.domainRegs[lrwDomainMgr_.size]),
>
>     0,
>
>     sizeof(ec_pdo_entry_reg_t) );
>
>     noLrwReadDomainMgr_.domainRegs = realloc(
>
>     noLrwReadDomainMgr_.domainRegs,
>
>     sizeof(ec_pdo_entry_reg_t) * (noLrwReadDomainMgr_.size + 1)  );
>
>     memset(
>
>     &(noLrwReadDomainMgr_.domainRegs[noLrwReadDomainMgr_.size]),
>
>     0,
>
>     sizeof(ec_pdo_entry_reg_t) );
>
>     noLrwWriteDomainMgr_.domainRegs = realloc(
>
>     noLrwWriteDomainMgr_.domainRegs,
>
>     sizeof(ec_pdo_entry_reg_t) * (noLrwWriteDomainMgr_.size + 1)  );
>
>     memset(
>
>     &(noLrwWriteDomainMgr_.domainRegs[noLrwWriteDomainMgr_.size]),
>
>     0,
>
>     sizeof(ec_pdo_entry_reg_t) );
>
>     //
>
>     // NOTE: the Output Domain must be registered with
>
>     // ecrt_domain_reg_pdo_entry_list before the Input Domain otherwise you
>
>     // will not have any data exchanged even though the drive goes into OP
>
>     // mode.
>
>     //
>
>     PRINT("\nAttempting to register PDOs on WRITE ONLY domain...\n");
>
>     if (ecrt_domain_reg_pdo_entry_list(
>
>     noLrwWriteDomainMgr_.domain, noLrwWriteDomainMgr_.domainRegs))
>
>     {
>
>     PRINT("WRITE ONLY PDO entry registration failed!\n");
>
>     return FALSE;
>
>          }
>
>     PRINT("\nAttempting to register PDOs on READ ONLY domain...\n");
>
>     if (ecrt_domain_reg_pdo_entry_list(
>
>     noLrwReadDomainMgr_.domain, noLrwReadDomainMgr_.domainRegs))
>
>     {
>
>     PRINT("READ ONLY PDO entry registration failed!\n");
>
>     return FALSE;
>
>       }
>
>     //
>
>     // And now we register the bi-directional domain.
>
>     //
>
>     PRINT("\nAttempting to register PDOs on LRW domain...\n");
>
>     if (ecrt_domain_reg_pdo_entry_list(
>
>     lrwDomainMgr_.domain, lrwDomainMgr_.domainRegs))
>
>     {
>
>     PRINT("LRW PDO entry registration failed!\n");
>
>     return FALSE;
>
>          }
>
>     /*
>
>     * Finishes the configuration phase and prepares for cyclic operation.
>
>     * This function tells the master that the configuration phase
>
>     * is finished and the realtime operation will begin.
>
>     * The function allocates internal memory for the domains and calculates
>
>     * the logical FMMU addresses for domain members.
>
>     * It tells the master state machine that the bus configuration is
>
>     * now to be applied
>
>     */
>
>     PRINT("\nAttempting to activate ECAT master...\n");
>
>     if (ecrt_master_activate(master_))
>
>     {
>
>     PRINT(
>
>     "%s Failed to activate master!\n",
>
>     __FUNCTION__ );
>
>     return FALSE;
>
>     }
>
>     /*
>
>     * Returns the domain's process data.
>
>     */
>
>     PRINT( "%s getting LRW process data from master.\n", __FUNCTION__ );
>
>     if (!(lrwDomainMgr_.processData
>
>     = ecrt_domain_data(lrwDomainMgr_.domain)))
>
>     {
>
>     PRINT(
>
>     "%s set ecProcessData -- domain data is NULL!\n",
>
>     __FUNCTION__ );
>
>     return FALSE;
>
>       }
>
>     if (!(noLrwReadDomainMgr_.processData
>
>     = ecrt_domain_data(noLrwReadDomainMgr_.domain)))
>
>     {
>
>     PRINT(
>
>     "%s set read ProcessData -- domain data is NULL!\n",
>
>     __FUNCTION__ );
>
>     return FALSE;
>
>          }
>
>     if (!(noLrwWriteDomainMgr_.processData
>
>     = ecrt_domain_data(noLrwWriteDomainMgr_.domain)))
>
>     {
>
>     PRINT(
>
>     "%s set write ProcessData -- domain data is NULL!\n",
>
>     __FUNCTION__ );
>
>     return FALSE;
>
>          }
>
>     … // blah blah blah
>
>     doScan_ = TRUE;
>
>     PRINT( "%s completed successfully.\n", __FUNCTION__ );
>
>     return TRUE;
>
>     }
>
>
>
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>