[etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
j.sikorski at utwente.nl
j.sikorski at utwente.nl
Thu Jun 16 11:56:24 CEST 2016
Dear Gavin and other EtherLAB users
Thanks for your e-mail. It made everything more clear, as the documentation is not very obvious about the precise action of those functions.
Indeed I did not call ecrt_master_activate - and that was one of my mistakes.
Another thing that confused me was, that even if I called it after all the configs, the state of PDO mapping objects did not change. Setting the "ethercat debug 1" helped there.
It turns out that I have a steady 4 seconds delay between SDO download request, and the confirmation. Hence , when I now call ecrt_master_activate, it takes the master a total of few minutes to run through the entire config. Thus, I was just too impatient to see the effects of this function.
I do not know yet the reason for that delay, but I will be digging further. I will reply in this topic once I have it done, so it is saved in the archive forever for others who may stumble upon those issues. :)
Thank you very much for all your assistance once again.
Yours sincerely,
Jakub Sikorski
________________________________
From: Gavin Lambert <gavinl at compacsort.com>
Sent: 16 June 2016 00:11
To: Sikorski, J. (CTW)
Cc: etherlab-users at etherlab.org
Subject: RE: [etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
Well, of course. Unless otherwise indicated by the device vendor, PDOs and SDOs are both in RAM only so will naturally revert to defaults if you reboot the device.
Regarding your other issue, does your program actually exit immediately after calling ecrt_slave_config_pdos? I assumed that you had a complete application and you had just edited the rest out.
If so, that won’t work. The various ecrt_slave_config_* functions just specify to the master library what you would like the configuration to be – nothing actually changes on the network until you call ecrt_master_activate afterwards. Additionally, PDOs are only actually exchanged while you have a master loop running. Have a look at the example programs included with EtherLab.
(If you just want to verify the configuration manually without actually running an application loop, then you can call ecrt_master_activate and then immediately release the master and exit if you like, but to actually accomplish anything useful you need an application loop.)
From: j.sikorski at utwente.nl [mailto:j.sikorski at utwente.nl]
Sent: Thursday, 16 June 2016 00:06
To: Gavin Lambert <gavin.lambert at compacsort.com>
Cc: etherlab-users at etherlab.org
Subject: Re: [etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
Dear Gavin,
Oh, and I forgot. Any changes I introduce using "sudo ethercat download" are reverted once the I reboot (power off - power on) my controllers.
Yours sincerely,
Jakub Sikorski
________________________________
From: etherlab-users <etherlab-users-bounces at etherlab.org<mailto:etherlab-users-bounces at etherlab.org>> on behalf of j.sikorski at utwente.nl<mailto:j.sikorski at utwente.nl> <j.sikorski at utwente.nl<mailto:j.sikorski at utwente.nl>>
Sent: 15 June 2016 13:59
To: gavinl at compacsort.com<mailto:gavinl at compacsort.com>
Cc: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: Re: [etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
Dear Gavin,
Thank you very, very much for your help!
According to the manual of my slave I should be able to map 0x2058 to PDO. What is puzzling me is that it seems that I have done that, using the following series of console commands:
sudo ethercat download -a 0 0x1a00 00 0x00
sudo ethercat download -a 0 0x1a00 01 0x20580010
sudo ethercat download -a 0 0x1a00 00 0x02
Now polling the slave with:
sudo ethercat upload -a 0 0x1a00 01
gives me:
0x20580010 542638096
However, if I execute ethercat cstruct -a 0, the field corresponding to 0x1a00 01 is still:
{0x6041, 0x00, 16}
which was the previous value.
Running the ecrt_slave_config_pdos changes nothing in the slave config, as inspected later on by sudo ethercat upload.
But do I understand correctly, that it should alter the configuration of the slave automatically, using the slave config, to the mapping I specified ealier in the file? Or do I have to run ecrt_master_activate(master) first so that all my actions are implemented?
I thought that all of this might also be caused by ec_slave_config_t passed on to ecrt_slave_config_pdos not being correct. I tried to dereference and output it, after it was generated by ecrt_master_slave_config, but I failed to compile such code.
This realisation was brought to me, as command:
sudo ethercat config
gives no visible output for any for my slaves.
I will be grateful for any more feedback.
Yours sincerely,
Jakub Sikorski
From: Gavin Lambert [mailto:gavinl at compacsort.com]
Sent: woensdag 15 juni 2016 1:31
To: Sikorski, J. (CTW) <j.sikorski at utwente.nl<mailto:j.sikorski at utwente.nl>>
Cc: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: RE: [etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
Hi Jakub,
Most EtherCAT slaves do not allow you to arbitrarily remap the contents of PDOs (the entries in the ec_pdo_entry_info_t); only to select between different predefined groups of PDOs via the ec_pdo_info_t. Some don’t support even that and just have a fixed layout (especially devices that don’t support CoE).
Have a look in the manual for your slave device to see what combinations it supports. Also note that indexes outside the 0x6000 or 0xA000 range are rarely available to be mapped as PDOs; you may need to access it as an SDO instead. If this is for a one-time startup configuration setting rather than for cyclic data, then look at the ecrt_slave_config_sdo* family of functions.
Another thing that you can look at is to look in the syslog after running your application; if you’re trying to change a PDO and the device does not support this then it should log a warning. You might need to set “ethercat debug 1” before running your application – this includes quite a bit of extra detail about the slave configuration process.
From: etherlab-users [mailto:etherlab-users-bounces at etherlab.org] On Behalf Of j.sikorski at utwente.nl<mailto:j.sikorski at utwente.nl>
Sent: Wednesday, 15 June 2016 06:40
To: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: [etherlab-users] I cannot proceed with configuration of PDOs using Libethercat.
Dear EtherLab Users,
I installed the IgH EtherCAT master, and to educate myself how to implement the communication, I set up a small network comprising of IgH master and one Technosoft Motion iPOS4808 drive.
The ./ethercat slaves command detects it.
The ./ethercat cstruct gives me the following configuration:
ec_pdo_entry_info_t slave_0_pdo_entries[] = {
{0x6040, 0x00, 16},
{0x607a, 0x00, 32},
{0x6041, 0x00, 16},
{0x6064, 0x00, 32},
{0x6077, 0x00, 16},
{0x60f4, 0x00, 32},
{0x60fd, 0x00, 32},
};
ec_pdo_info_t slave_0_pdos[] = {
{0x1600, 2, slave_0_pdo_entries + 0},
{0x1a00, 3, slave_0_pdo_entries + 2},
{0x1a01, 2, slave_0_pdo_entries + 5},
};
ec_sync_info_t slave_0_syncs[] = {
{0, EC_DIR_OUTPUT, 0, NULL, EC_WD_DISABLE},
{1, EC_DIR_INPUT, 0, NULL, EC_WD_DISABLE},
{2, EC_DIR_OUTPUT, 1, slave_0_pdos + 0, EC_WD_DISABLE},
{3, EC_DIR_INPUT, 2, slave_0_pdos + 1, EC_WD_DISABLE},
{0xff}
};
Now I want to use C++ functions, to change the value outputted at 0x1a00 x02 to the object 0x2058 x00 with size 16 bit.
Hence, based on the cstruct file, as well as ~/ethercat-1.5.2/example/user/main.c , I write the following code (spread over main.h and main.cpp) to achieve this.
#include "auxfun.h"
// Application parameters
#define FREQUENCY 100
#define PRIORITY 1
// Optional features
#define CONFIGURE_PDOS 1
#define SDO_ACCESS 0
// EtherCAT
static ec_master_t *master = NULL;
static ec_master_state_t master_state = {};
static ec_domain_t *domain1 = NULL;
static ec_domain_state_t domain1_state = {};
static ec_slave_config_t *sc_iPOS0 = NULL;
static ec_slave_config_state_t sc_iPOS0_state = {};
// Timer
static unsigned int sig_alarms = 0;
static unsigned int user_alarms = 0;
/****************************************************************************/
// process data
static uint8_t *domain1_pd = NULL;
#define AxisBotPos 0, 0 //Bottom frame iPOS Alias
#define IPOS4808BX_CAT 0x000001a3, 0x019f418d // Vendor ID, Product Code
const static ec_pdo_entry_reg_t domain1_regs[] = {
{AxisBotPos, IPOS4808BX_CAT, 0x6060, 0x00, &off_iPOS0_Rx},
{AxisBotPos, IPOS4808BX_CAT, 0x2058, 0x00, &off_iPOS0_Tx},
{}
};
// Analog in --------------------------
ec_pdo_entry_info_t iPOS0_pdo_entries[] = {
{0x6040, 0x00, 16},
{0x6060, 0x00, 8},
{0x6041, 0x00, 16},
{0x2058, 0x00, 16},
{0x6077, 0x00, 16},
{0x60f4, 0x00, 32},
{0x60fd, 0x00, 32},
};
ec_pdo_info_t iPOS0_pdo[] = {
{0x1600, 2, iPOS0_pdo_entries + 0},
{0x1a00, 3, iPOS0_pdo_entries + 2},
{0x1a01, 2, iPOS0_pdo_entries + 5},
};
ec_sync_info_t iPOS0_syncs[] = {
{0, EC_DIR_OUTPUT, 0, NULL, EC_WD_DISABLE},
{1, EC_DIR_INPUT, 0, NULL, EC_WD_DISABLE},
{2, EC_DIR_OUTPUT, 1, iPOS0_pdo + 0, EC_WD_DISABLE},
{3, EC_DIR_INPUT, 2, iPOS0_pdo + 1, EC_WD_DISABLE},
{0xff}
};
#include "main.h"
/****************************************************************************/
int main(int argc, char **argv)
{
struct itimerval tv;
master = ecrt_request_master(0);
if (!master)
return -1;
domain1 = ecrt_master_create_domain(master);
if (!domain1)
return -1;
if (!(sc_iPOS0 = ecrt_master_slave_config(
master, AxisBotPos, IPOS4808BX_CAT))) {
fprintf(stderr, "Failed to get slave configuration.\n");
return -1;
}
printf("Configuring PDOs...\n");
if (ecrt_slave_config_pdos(sc_iPOS0, 4, iPOS0_syncs)) {
fprintf(stderr, "Failed to configure PDOs.\n");
return -1;
}
cout << "Done" << endl;
return 0;
}
I run the code above. It executes with no problem.
Now, I checked, using:
sudo ethercat upload -a 0 0x1a00 01
whether the introduced mapping modification worked. Unfortunately it seems that it is not the case and I get the same variable that was in ./ethercat cstruct at that position.
Then I tried to change the variable manually using ./ethercat download -a 0 0x1a00 01 0x20580010. This worked, at least in the console (confirmed by ./ethercat upload). However, cstruct still outputs previous values. I also tried the same procedure with other PDO variables to the same effect, my C++ code changes nothing in the mapping.
If anyone of you could look into the code and tell me whether what I am doing is correct (or wrong), I would be exteremely grateful. I mostly do not know where even to start debugging right now.
Thank you a lot in advance.
Yours faithfully,
Jakub Sikorski
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20160616/d7fda6e9/attachment-0004.htm>
More information about the Etherlab-users
mailing list