Are you using the dc_clock_adjust to modify your sleep time? ie.
something like
clock_nanosleep(CLOCK_MONOTONIC,TIMER_ABSTIME,&inst->wakeupTime,NULL);
TIMESPEC_ADD_NS(inst->wakeupTime,1000000 + dc_clock_adjust);
Does your inst->cycleNs include the clock adjustement?
I have found the best debug tool for DC is an oscilloscope and a board
that you probe the SOF and sync0 . If you see SOF wander with respect
to sync0 it won't work correctly. If they don't you are good.
On Wed, 2016-03-02 at 14:47 +0000, Thomas Bitsky Jr wrote:
> Thanks for the response, Richard.
>
> CyclicTest on the hardware:
> user at core:~$ sudo cyclictest --smp -p95 -m
> # /dev/cpu_dma_latency set to 0us
> policy: fifo: loadavg: 0.01 0.04 0.04 1/162 1547
>
> T: 0 ( 1543) P:95 I:1000 C: 26093 Min: 6 Act: 30 Avg: 25 Max: 56
> T: 1 ( 1544) P:95 I:1500 C: 17386 Min: 6 Act: 14 Avg: 23 Max: 66
> T: 2 ( 1545) P:95 I:2000 C: 13036 Min: 5 Act: 28 Avg: 29 Max: 57
> T: 3 ( 1546) P:95 I:2500 C: 10424 Min: 6 Act: 30 Avg: 29 Max: 58
>
>
>
> So, the max latency is definitely in the ballpark of what I was saying last night.
>
> Setting cylictest with a break value fails almost instantly.
>
> root at core:/sys/kernel/debug/tracing# cyclictest --smp -p95 -f -b 200
> # /dev/cpu_dma_latency set to 0us
> INFO: debugfs mountpoint: /sys/kernel/debug/tracing/
> policy: fifo: loadavg: 0.00 0.01 0.05 3/165 1703
>
> T: 0 ( 1700) P:95 I:1000 C: 0 Min:1000000 Act: 0 Avg: 0 Max: 0
> T: 1 ( 1701) P:95 I:1500 C: 0 Min:1000000 Act: 0 Avg: 0 Max: 0
> T: 2 ( 0) P:95 I:2000 C: 0 Min:1000000 Act: 0 Avg: 0 Max: 0
> T: 3 ( 1703) P:95 I:2500 C: 0 Min:1000000 Act: 0 Avg: 0 Max: 0
> # Thread Ids: 01700 01701 01702 01703
> # Break thread: 1702
> # Break value: 217
>
>
>
> [snip]
> First things first: when you are running RT proggies, you need a stable
> clock source and a preemptable kernel!
> [/snip]
>
>
> I am using RT Preempt:
> # uname -a
> Linux core 3.12.50-rt68 #1 SMP PREEMPT RT Mon Nov 23 18:17:14 CST 2015 i686 i686 i686 GNU/Linux
>
>
> Thanks!
> Thomas C. Bitsky Jr. | Lead Developer
> ADC | automateddesign.com <http://automateddesign.com/>
> P: 630-783-1150 F: 630-783-1159 M: 630-632-6679
>
> Follow ADC news and media:
> Facebook <https://facebook.com/automateddesigncorp> | Twitter <https://twitter.com/ADCSportsLogic> | YouTube <https://www.youtube.com/user/ADCSportsLogic>
>
>
>
>
>
>
>
>
> On 3/2/16, 5:30 AM, "etherlab-users on behalf of Richard Hacker" <etherlab-users-bounces at etherlab.org on behalf of ha at igh.de> wrote:
>
> >Hi John,
> >
> >Skipped frames are either a timing or a hardware problem (faulty
> >EtherCAT slaves, cabling, noise). Some slaves don't care, DC slaves puke!
> >
> >First things first: when you are running RT proggies, you need a stable
> >clock source and a preemptable kernel! Even more so when you're running
> >at 250us cycle time. Your jitter of 50us is roughly 20% of your cycle
> >time, definitely not a neglegible fraction! So tackle that first.
> >
> >Download cyclictest and test that first:
> >https://rt.wiki.kernel.org/index.php/Cyclictest
> >
> >Once your cyclic test is stable (~10us max jitter), you may start
> >looking for delays in your code.
> >
> >Instrumate your loop and find out what is causing delays. Comment out
> >large sections of code to start from a known good state (maybe doing
> >EtherCAT IO exclusively and NOTHING else, no GUI, signal processing,
> >etc) and reinsert code slowly to find the error.
> >
> >Do you have ANY system calls in your RT cycle, like sockets(), read() or
> >write()? Do remember that system calls (including those to the master)
> >may cause page faults that introduce delays. Only a very small subset of
> >known and documented system calls can be used for RT. Notably read() and
> >write() to pipes, shared memory (once set up of coarse), semaphores are OK.
> >
> >BTW: Needless to say that we have paid particular attention that the
> >master does not cause any page faults or other delays once started in
> >cyclic mode ;)
> >
> >Good luck!
> >Richard
> >
> >On 02.03.2016 05:51, Thomas Bitsky Jr wrote:
> >>
> >> I’ve been continuing to work on this, but have had limited success.
> >> While a distributed clock is technically running, it’s caused a few
> >> other problems that I’ve been unable to correct. I think my main problem
> >> all stems from this:
> >>
> >> [36524.681778] EtherCAT 0: Domain 0: Working counter changed to 10/10.
> >> [36524.681787] EtherCAT 0: Domain 2: Working counter changed to 1/1.
> >> [36524.681792] EtherCAT 0: Domain 1: Working counter changed to 1/1.
> >> [36525.858760] EtherCAT 0: Domain 0: Working counter changed to 0/10.
> >> [36525.858810] EtherCAT 0: Domain 2: Working counter changed to 0/1.
> >> [36525.858827] EtherCAT 0: Domain 1: Working counter changed to 0/1.
> >> [36526.203067] EtherCAT WARNING: Datagram f185d88c (domain0-0-main) was
> >> SKIPPED 2 times.
> >> [36526.203099] EtherCAT WARNING: Datagram f185d90c (domain2-28-main) was
> >> SKIPPED 2 times.
> >> [36526.203104] EtherCAT WARNING: Datagram f185d28c (domain1-22-main) was
> >> SKIPPED 2 times.
> >> [36526.743379] EtherCAT WARNING 0: 12 datagrams UNMATCHED!
> >> [36526.863556] EtherCAT 0: Domain 0: 5 working counter changes - now 10/10.
> >> [36526.863566] EtherCAT 0: Domain 2: 5 working counter changes - now 1/1.
> >> [36526.863572] EtherCAT 0: Domain 1: 5 working counter changes - now 1/1.
> >>
> >> … and on and on and on…
> >>
> >> The AKD servo drive I’m using will run fine, no warnings, then suddenly
> >> drop to an F125 fault and shut off. The is a frame synchronization
> >> error. Basically, it’s saying that the sync0 frame isn’t received at a
> >> consistent enough rate, so it faults out.
> >>
> >> My scan rate is 250 microseconds, and I admit there is jitter. It varies
> >> from as little as +/- 50 microseconds, though I’m not sure why. The
> >> "ethercat master" command reports a steady 4000 frames/sec, but the
> >> scoping part of my project records a timestamp, and I am seeing the +/-
> >> 50 microseconds.
> >>
> >> My timing function is straight out of the EtherCAT master examples and
> >> is also similar to methods I’ve seen in other cyclic task projects. The
> >> whole cyclic task is below. Can anyone see what idiotic thing I must be
> >> doing to get unmatched datagrams?
> >>
> >> #define TIMESPEC_ADD_NS(TS, NS)\
> >> (TS).tv_nsec += (NS);\
> >> while ( (TS).tv_nsec >= NANOS_PER_SEC ){\
> >> (TS).tv_nsec -= NANOS_PER_SEC;\
> >> (TS).tv_sec++; }
> >>
> >> #define TIMESPEC2NSEPOCH2000(T) \
> >> ((uint64_t) (((T).tv_sec - 946684800ULL) * 1000000000ULL) + (T).tv_nsec)
> >>
> >> #define TON struct timespec
> >> #define TON_ENDTIME(MS)\
> >> time_add_ns((MS) * NANOS_PER_MILLISEC)
> >>
> >>
> >> static TON clockSyncTon_;
> >>
> >>
> >> int
> >> TON_ISDONE( struct timespec ts )
> >> {
> >> struct timespec now;
> >> clock_gettime(CLOCK_MONOTONIC, &now);
> >> if ( now.tv_sec > ts.tv_sec )
> >> return 1;
> >> else if ( now.tv_sec == ts.tv_sec
> >> && now.tv_nsec >= ts.tv_nsec )
> >> return 1;
> >> else
> >> return 0;
> >> }
> >>
> >>
> >> static bool
> >> wait_period(RtaiMain* inst)
> >> {
> >>
> >> int rc;
> >> bool done = false;
> >> while ( !done && inst->doScan && runAll_ )
> >> {
> >> rc = clock_nanosleep(CLOCK_MONOTONIC,
> >> TIMER_ABSTIME,
> >> &inst->wakeupTime,
> >> NULL );
> >>
> >>
> >> if ( rc == EFAULT )
> >> {
> >> return false;
> >> }
> >> else if ( rc == EINTR )
> >> {
> >> continue;
> >> }
> >> else if ( rc == EINVAL )
> >> {
> >> return false;
> >> }
> >> else
> >> {
> >> done = 1;
> >> }
> >> }
> >> TIMESPEC_ADD_NS(inst->wakeupTime, inst->cycleNs);
> >> return true;
> >>
> >> }
> >>
> >>
> >> static void
> >> cyclic_task(RtaiMain* inst)
> >> {
> >>
> >> clock_gettime(CLOCK_MONOTONIC ,&(inst->wakeupTime));
> >> /* start after one second */
> >> inst->wakeupTime.tv_sec++;
> >> wait_period(inst);
> >> while (runAll_ && inst->doScan)
> >> {
> >> //
> >> // Trigger Fieldbus RX here.
> >> //
> >> //
> >> ecrt_master_receive(master_);
> >>
> >> // record the time we received the data so other parts of the program
> >> // have an accurate time reading
> >> globalTickTimeNs = ton_get_ns();
> >>
> >> ecrt_domain_process(lrwDomainMgr_.domain);
> >> ecrt_domain_process(noLrwWriteDomainMgr_.domain);
> >> ecrt_domain_process(noLrwReadDomainMgr_.domain);
> >>
> >> if (counter_)
> >> {
> >>
> >> counter_—;
> >> }
> >> else
> >> {
> >> counter_ = 4000;
> >>
> >> // check for master state
> >> check_master_state();
> >> }
> >>
> >>
> >> … tick sub systems
> >>
> >>
> >> //
> >> // Trigger Fieldbus TX. This should be the last step
> >> //
> >> //
> >> ecrt_domain_queue(lrwDomainMgr_.domain);
> >> ecrt_domain_queue(noLrwWriteDomainMgr_.domain);
> >> ecrt_domain_queue(noLrwReadDomainMgr_.domain);
> >> clock_gettime(CLOCK_REALTIME, &dcTime_ );
> >> ecrt_master_application_time(
> >> master_,
> >> TIMESPEC2NSEPOCH2000(dcTime_) );
> >>
> >>
> >> if ( TON_ISDONE(clockSyncTon_) )
> >> {
> >> ecrt_master_sync_reference_clock(master_);
> >> clockSyncTon_ = TON_ENDTIME(10);// milliseconds
> >> }
> >> ecrt_master_sync_slave_clocks(master_);
> >>
> >> // send EtherCAT data
> >> ecrt_master_send(master_);
> >>
> >>
> >> if ( !wait_period(inst) )
> >> {
> >> PRINT( "%s Error with waiting! Stopping cyclic_task.\n",
> >> __FUNCTION__ );
> >> inst->doScan = false;
> >> }
> >> }
> >>
> >> }
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >> From: Graeme Foot <Graeme.Foot at touchcut.com
> >> <mailto:Graeme.Foot at touchcut.com>>
> >> Date: Sunday, February 21, 2016 at 4:07 PM
> >> To: Thomas Bitsky <tbj at automateddesign.com <mailto:tbj at automateddesign.com>>
> >> Cc: "etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>"
> >> <etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>>
> >> Subject: RE: Distributed Clocks
> >>
> >> Hi,
> >>
> >> I build and patch against revision 2526, so don’t know what patches /
> >> fixes have made it through to the latest release. However for my
> >> revision I need fixes for reference clock selections and dc
> >> synchronization issues.
> >>
> >> I’ve attached the dc related patches I use, but these are applied after
> >> some other patches so you may get some conflicts or offsetting.
> >>
> >> *01 - Distributed Clock fixes and helpers.patch*
> >>
> >> This sorts out some ref slave issues, allowing a user selected ref
> >> slave. It also adds some helper functions:
> >>
> >> - ecrt_master_setup_domain_memory() : this allows me to set up the
> >> domain memory and do stuff with it before calling ecrt_master_activate()
> >> (for user space apps)
> >>
> >> - ecrt_master_deactivate_slaves() : this lets me deactivate the slaves
> >> while still in realtime to avoid the slaves getting some shutdown sync
> >> errors
> >>
> >> *02 - Distributed Clock fixes from Jun Yuan - dc sync issues.patch*
> >>
> >> This sorts out some timing issues to do with slave dc syncing. Without
> >> it they can start syncing from one cycle out causing a large syncing
> >> time overhead, one slave at a time.
> >>
> >> Regards,
> >>
> >> Graeme.
> >>
> >> *From:*Thomas Bitsky Jr [mailto:tbj at automateddesign.com]
> >> *Sent:* Sunday, 21 February 2016 10:27 a.m.
> >> *To:* Graeme Foot
> >> *Cc:* etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>
> >> *Subject:* Re: Distributed Clocks
> >>
> >> Graeme,
> >>
> >> Thank you so much for the detailed response. I'm away from my computer
> >> right now, so I can't try out your advice, but I noticed you asked about
> >> patches. I am not running any patches; which should I get?
> >>
> >> Thanks!
> >> Thomas Bitsky Jr
> >>
> >> On Feb 20, 2016, at 3:04 PM, Graeme Foot <Graeme.Foot at touchcut.com
> >> <mailto:Graeme.Foot at touchcut.com>> wrote:
> >>
> >> Hi,
> >>
> >> The slave clocks get synced via the distributed clock system using
> >> the master methods: ecrt_master_reference_clock_time(),
> >> ecrt_master_sync_slave_clocks(), ecrt_master_application_time(),
> >> ecrt_master_sync_reference_clock().
> >>
> >> However each individual slave can choose (if it is capable of it)
> >> whether to synchronize its reading and writing of data to a
> >> particular point in time within the dc cycle. If that slave does
> >> not choose to do so then the reading and writing of the data occurs
> >> at the time the EtherCAT frame goes past, resulting in a progressive
> >> update and application of data as the frame progresses through all
> >> of the slaves.
> >>
> >> If a slave is registered to use the dc clock then it caches the
> >> frame data until the sync0 interrupt so in theory all dc slaves
> >> apply the data at the same time. It also means you don’t have to
> >> worry about jitter as to the time the frame is sent over the wire.
> >> The only thing is to choose a good sync0 time to ensure your frames
> >> are always sent out and have reached all of the slaves before the
> >> sync0 time occurs, and that the next frame is not sent out before
> >> the previous sync0 time occurs.
> >>
> >> In my application my cycle time is 1000us. I choose a sync0 time of
> >> 500us. I also send my frame as close as possible to the beginning
> >> of the cycle. This gives the frame up to half the cycle time to
> >> reach all of the slaves and then the other half of the cycle for the
> >> frame to return in time for the master receive call. I could choose
> >> a sync0 time later than 500us but I want it processed as soon as
> >> possible after the frame is received while still allowing for a bus
> >> with a large number of terminals.
> >>
> >> So below where you are calculating loop_shift based on the current
> >> time is wrong. Just choose a time within the dc cycle and use that
> >> value for all slaves. Note: the beginning of the dc cycle is in
> >> phase with the first call to ecrt_master_application_time(), so all
> >> of your realtime looping should also be in phase with that initial time.
> >>
> >> Note, when selecting a slave to be the DC reference slave you should
> >> generally choose the first slave on your bus, regardless of whether
> >> it will be (or can be) registered to use the dc synchronization. At
> >> the very least it must be before, or be the, first slave that will
> >> be registered as a dc slave.
> >>
> >> Also note that some slaves clocks are not very stable and shouldn’t
> >> be used as the DC reference slave. My original testing was on a
> >> Beckhoff CX1020 with a CX1100-0004, this could not be used as a
> >> reference slave as its clock was not stable.
> >>
> >> I see you are configuring the slaves via ecrt_slave_config_*()then
> >> calling ecrt_slave_config_pdos()at the end. If you call
> >> ecrt_slave_config_pdos() at the beginning you don’t need all the
> >> other config calls. However I hear AKD drives and some other slaves
> >> prefer explicit slave config calls but most slaves are happy with
> >> just the ecrt_slave_config_reg_pdo_entry()methods.
> >>
> >> This also leads to another issue. One of the configured PDO items
> >> is the “mode of operation” value (0x6060 0x00). You are also
> >> configuring this with: ecrt_slave_config_sdo8( sc, 0x6060, 0, 8 ).
> >> This value should be instead be set via the PDO value. Use
> >> ecrt_slave_config_reg_pdo_entry()to get the offset to the value and
> >> set the value there.
> >>
> >> Sorry if that was a bit long but DC’s is not an easy topic to get
> >> your head around. Here’s a bit of a summary:
> >>
> >> - You can choose which slaves get registered with
> >> ecrt_slave_config_dc(). But each slave you want synced must get its
> >> own call to ecrt_slave_config_dc().
> >>
> >> - If your yaskawa drives get to OP without
> >> ecrt_slave_config_dc()then they should get to OP with
> >> ecrt_slave_config_dc().
> >>
> >> - The yaskawa drives require a very stable reference slave time,
> >> which is why we sync the EtherCAT master to the reference slave
> >> rather than the other way around.
> >>
> >> And some other comments:
> >>
> >> - Never use anEL9010 endcap module. These break the distributed
> >> clock calculations. I don’t think they are available anymore though.
> >>
> >> - There are some patches out there that fix various DC clock issues,
> >> are you using any of these?
> >>
> >> Regards,
> >>
> >> Graeme.
> >>
> >> *From:*Thomas Bitsky Jr [mailto:tbj at automateddesign.com]
> >> *Sent:* Sunday, 21 February 2016 7:15 a.m.
> >> *To:* Graeme Foot; etherlab-users at etherlab.org
> >> <mailto:etherlab-users at etherlab.org>
> >> *Subject:* Re: Distributed Clocks
> >>
> >> [snip]
> >>
> >> I’ve never been able to get the EL7041 stepper modules to work in dc
> >> mode.
> >>
> >> [/snip]
> >>
> >> Is it all or nothing? I need the servo drives, the LVDT and the
> >> EL3356 tied to a distributed clock. The EL7041 is optional for me.
> >>
> >> [snip]
> >>
> >> I don’t see in your code calls to ecrt_slave_config_dc().
> >>
> >> For the yaskawa drive, during the config stage, I use the following
> >> calls…
> >>
> >> [/snip]
> >>
> >> Forgot to put that part; my bad. This is what I had for the
> >> Yaskawa/AKD, although I was only doing it to one of the drives. I
> >> thought I was supposed to set up one distributed clock, and it
> >> became the master and handled the rest. Am I supposed to do this for
> >> all the cards, or do I select?
> >>
> >> Yaskawa(AKD drive code is pretty much the same):
> >>
> >> if (!(sc = ecrt_master_slave_config(
> >>
> >> master,
> >>
> >> slavePosDomain,
> >>
> >> slavePosIndex,
> >>
> >> vendorId, productCode)))
> >>
> >> {
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1C12, 0, 0 ); /* clear sm pdo 0x1c12 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1C13, 0, 0 ); /* clear sm pdo 0x1c12 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A00, 0, 0 ); /* clear TxPDO0 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A01, 0, 0 ); /* clear TxPDO1 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A02, 0, 0 ); /* clear TxPDO2 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A03, 0, 0 ); /* clear TxPDO3 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1600, 0, 0 ); /* number of var in this
> >> PDO */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1601, 0, 0 ); /* clear RxPdo 0x1601 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1602, 0, 0 ); /* clear RxPdo
> >> 0x1602 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1603, 0, 0 ); /* clear RxPdo
> >> 0x1603 */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A00, 0, 0 ); /* clear TxPDO0 */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 1, 0x60410010 ); // Status word
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 2,0x60640020 );// Position
> >> actual value, per encoder
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 3,0x60770010 );// Torque,
> >> actual value
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 4,0x60F40020 );// Following
> >> error, actual value
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 5,0x60610008 );// Modes of
> >> operation display
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 6,0x00000008 );// GAP
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 7,0x60B90010 );// Touch probe
> >> status
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A00, 8, 0x60BA0020 ); // Touch probe
> >> 1 position
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A00, 0, 8 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A01, 0, 0 ); /* clear TxPDO1 */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A01,1,0x60410010 ); // Status word
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A01,2,0x60640020 );// Position
> >> actual value, per encoder
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A01, 0, 2 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A02, 0, 0 ); /* clear TxPDO2 */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A02,1,0x60410010 ); // Status word
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A02,2,0x60640020 );// Position
> >> actual value, per encoder
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A02, 0, 2 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A03, 0, 0 ); /* clear TxPDO2 */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A03,1,0x60410010 ); // Status word
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A03,2,0x60640020 );// Position
> >> actual value, per encoder
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1A03,3,0x60770010 );// Torque, actual
> >> value
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1A03, 0, 3 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1600, 0, 0 ); /* clear entries */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 1, 0x60400010 ); /* control
> >> word */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 2, 0x607A0020 ); /* target
> >> position */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 3, 0x60FF0020 ); /* target
> >> velocity */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 4, 0x60710010 ); /* target
> >> torque */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 5, 0x60720010 ); /* max torque */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 6, 0x60600008 ); /* modes of
> >> operation */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 7, 0x00000008 ); /* gap */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1600, 8, 0x60B80010 ); /* touch
> >> probe function */
> >>
> >> ecrt_slave_config_sdo8(sc, 0x1600, 0, 8 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1601, 0, 0 ); /* clear entries */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1601, 1, 0x60400010 ); /* control
> >> word */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1601, 2, 0x607A0020 ); /* target
> >> position */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1601, 0, 2 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1602, 0, 0 ); /* clear entries */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1602, 1, 0x60400010 ); /* control
> >> word */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1602, 2, 0x60FF0020 ); /* target
> >> position */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1602, 0, 2 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1603, 0, 0 ); /* clear entries */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1603, 1, 0x60400010 ); /* control
> >> word */
> >>
> >> ecrt_slave_config_sdo32( sc, 0x1603, 2, 0x60710020 ); /* target
> >> position */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1603, 0, 2 ); /* pdo entries */
> >>
> >> ecrt_slave_config_sdo16( sc, 0x1C12, 1, 0x1601 ); /* download pdo
> >> 1C12 index */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1C12, 0, 1 ); /* set number of RxPDO */
> >>
> >> ecrt_slave_config_sdo16( sc, 0x1C13, 1, 0x1A01 ); /* download pdo
> >> 1C13 index */
> >>
> >> ecrt_slave_config_sdo8( sc, 0x1C13, 0, 1 ); /* set number of TxPDO */
> >>
> >> // OPMODE
> >>
> >> // Yaskawa recommends 8
> >>
> >> ecrt_slave_config_sdo8( sc, 0x6060, 0, 8 );
> >>
> >> unsigned char interpolationTime = 0xFF;
> >>
> >> // 250
> >>
> >> unsigned char cycleExponent = 0xFA;
> >>
> >> // microseconds
> >>
> >> // globalSCanRate_us equals either 250 or 125.
> >>
> >> unsigned int us = globalScanRate_us;
> >>
> >> size_t i;
> >>
> >> for ( i=0;i<6, us > 0xFF;++i )
> >>
> >> {
> >>
> >> us /= 10;
> >>
> >> cycleExponent += 1;
> >>
> >> }
> >>
> >> interpolationTime = us;
> >>
> >> ecrt_slave_config_sdo8( akd->sc_akd, 0x60C2, 1, interpolationTime );
> >> /* Interpolation time */
> >>
> >> ecrt_slave_config_sdo8( akd->sc_akd, 0x60C2, 2, cycleExponent ); /*
> >> Cycle exponent */
> >>
> >> PRINT("Configuring PDOs...\n");
> >>
> >> if (ecrt_slave_config_pdos(sc, EC_END, slave_syncs))
> >>
> >> {
> >>
> >> PRINT("Failed to configure Yaskawa Sigma PDOs.\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> *struct timespec cur_time;*
> >>
> >> *clock_gettime(CLOCK_REALTIME, &cur_time);*
> >>
> >> *size_t loop_period = globalScanRate_us * 1000;*
> >>
> >> *if ( loop_period == 0 ) loop_period = 1;*
> >>
> >> *size_t loop_shift *
> >>
> >> *= loop_period - (cur_time.tv_nsec % loop_period);*
> >>
> >> *ecrt_slave_config_dc(*
> >>
> >> *sc, *
> >>
> >> *0x0300, *
> >>
> >> *loop_period, *
> >>
> >> *loop_shift, *
> >>
> >> *0, *
> >>
> >> *0);*
> >>
> >> For the EL3356, would I then?
> >>
> >> KL3356StrainGauge* sg = (KL3356StrainGauge*)slave->instance;
> >>
> >> printf( "Begin kl3356_ecConfigure...\n");
> >>
> >> //
> >>
> >> // Create the slave configuration
> >>
> >> //
> >>
> >> if (!(sg->sc = ecrt_master_slave_config(
> >>
> >> master,
> >>
> >> slavePosDomain, slavePosIndex, // Bus position
> >>
> >> vendorId, productCode
> >>
> >> // Slave type
> >>
> >> )))
> >>
> >> {
> >>
> >> printf(
> >>
> >> "kl3356_ecConfigure -- Failed to get slave configuration.\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> //
> >>
> >> // Register startup configuration for the hardware
> >>
> >> //
> >>
> >> ecrt_slave_config_sdo8( sg->sc, 0x1C12, 0, 0 ); /* clear sm pdo
> >> 0x1c12 */
> >>
> >> ecrt_slave_config_sdo8( sg->sc, 0x1C13, 0, 0 ); /* clear sm pdo
> >> 0x1c12 */
> >>
> >> ecrt_slave_config_sdo16( sg->sc, 0x1C12, 1, 0x1600 ); /* download
> >> pdo 1C12 index */
> >>
> >> ecrt_slave_config_sdo8( sg->sc, 0x1C12, 0, 1 ); /* set number of
> >> RxPDO */
> >>
> >> ecrt_slave_config_sdo16( sg->sc, 0x1C13, 1, 0x1A00 ); /* download
> >> pdo 1C13 index */
> >>
> >> ecrt_slave_config_sdo16( sg->sc, 0x1C13, 2, 0x1A02 ); /* download
> >> pdo 1C13 index */
> >>
> >> ecrt_slave_config_sdo8( sg->sc, 0x1C13, 0, 2 ); /* set number of
> >> TxPDO */
> >>
> >> //
> >>
> >> // Configure the hardware's PDOs
> >>
> >> //
> >>
> >> if (ecrt_slave_config_pdos(sg->sc, EC_END, kl3356_syncs))
> >>
> >> {
> >>
> >> printf(
> >>
> >> "kl3356_ecConfigure -- Failed to configure PDOs.\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> *struct timespec cur_time;*
> >>
> >> *clock_gettime(CLOCK_REALTIME, &cur_time);*
> >>
> >> *size_t loop_period = globalScanRate_us * 1000;*
> >>
> >> *if ( loop_period == 0 ) loop_period = 1;*
> >>
> >> *size_t loop_shift *
> >>
> >> *= loop_period - (cur_time.tv_nsec % loop_period);*
> >>
> >> *ecrt_slave_config_dc(*
> >>
> >> *s**g->sc, *
> >>
> >> *0x0300, *
> >>
> >> *loop_period, *
> >>
> >> *loop_shift, *
> >>
> >> *0, *
> >>
> >> *0);*
> >>
> >> Thanks!
> >>
> >> Thomas C. Bitsky Jr. | Lead Developer
> >>
> >> ADC | automateddesign.com <http://automateddesign.com/>
> >>
> >> P: 630-783-1150 F: 630-783-1159 M: 630-632-6679
> >>
> >> Follow ADC news and media:
> >>
> >> Facebook <https://facebook.com/automateddesigncorp> | Twitter
> >> <https://twitter.com/ADCSportsLogic> | YouTube
> >> <https://www.youtube.com/user/ADCSportsLogic>
> >>
> >> *From: *Graeme Foot <Graeme.Foot at touchcut.com
> >> <mailto:Graeme.Foot at touchcut.com>>
> >> *Date: *Friday, February 19, 2016 at 7:24 PM
> >> *To: *Thomas Bitsky <tbj at automateddesign.com
> >> <mailto:tbj at automateddesign.com>>, "etherlab-users at etherlab.org
> >> <mailto:etherlab-users at etherlab.org>" <etherlab-users at etherlab.org
> >> <mailto:etherlab-users at etherlab.org>>
> >> *Subject: *RE: Distributed Clocks
> >>
> >> Hi,
> >>
> >> I don’t see in your code calls to ecrt_slave_config_dc().
> >>
> >> For the yaskawa drive, during the config stage, I use the following
> >> calls:
> >>
> >> // set interpolation time period (free run mode)
> >>
> >> // where 0x60C2 is time in seconds = (0x60C2, 0x01) x
> >> 10^(0x60C2, 0x02)
> >>
> >> // eg period of 1ms:
> >>
> >> // (0x60C2, 0x01) = 1
> >>
> >> // (0x60C2, 0x02) = -3
> >>
> >> // => 1 x 10^(-3) = 0.001s
> >>
> >> ecrt_slave_config_sdo8(dev->slaveConfig, 0x60C2, 0x01,
> >> (uint8_t)g_app.scanTimeMS);
> >>
> >> ecrt_slave_config_sdo8(dev->slaveConfig, 0x60C2, 0x02,
> >> (int8_t)(-3));
> >>
> >> // set up the distributed clock
> >>
> >> // 0x0000 = free run, 0x0300 = dc
> >>
> >> // (Supported DC cycle: 125us to 4ms (every 125us cycle))
> >>
> >> ecrt_slave_config_dc(dev->slaveConfig, 0x0300,
> >> g_app.scanTimeNS, 500000, 0, 0);
> >>
> >> 0x60C2 shouldn’t be necessary for dc mode, but I used it before I
> >> had dc mode working and have never tried it without and it doesn’t
> >> harm anything having it in.
> >>
> >> The second value that is being passed to the
> >> ecrt_slave_config_dcmethod is a value that is written to the ESC
> >> register 0x980. The Yaskawa SGDV doco says this value should be
> >> 0x0000 for free run mode and 0x0300 for dc mode. Other ESC’s may
> >> required different values.
> >>
> >> I’ve never been able to get the EL7041 stepper modules to work in dc
> >> mode.
> >>
> >> Graeme.
> >>
> >> *From:*etherlab-users [mailto:etherlab-users-bounces at etherlab.org]
> >> *On Behalf Of *Thomas Bitsky Jr
> >> *Sent:* Saturday, 20 February 2016 1:09 p.m.
> >> *To:* etherlab-users at etherlab.org <mailto:etherlab-users at etherlab.org>
> >> *Subject:* [etherlab-users] Distributed Clocks
> >>
> >> Hello.
> >>
> >> I’ve been using the EtherCAT master for years to great success, but
> >> I’m stuck on a problem I can’t figure out that I think several
> >> people here are doing successfully. I can’t implement distributed
> >> clocks in my application.
> >>
> >> I am having the same problem on two systems I have up and running:
> >>
> >> SYSTEM ONE:
> >>
> >> EtherLAB Master 1.52, E1000E Driver, Scan Rate 4Khz, Ubuntu Server
> >> 14.04LTS, RT-PREEMPT 3.12.50-rt68
> >>
> >> alias=0, position=0, device=EK1100
> >>
> >> alias=0, position=1, device=EL1104
> >>
> >> alias=0, position=2, device=EL2004
> >>
> >> alias=0, position=3, device=EL9510
> >>
> >> alias=0, position=4, device=EL3356
> >>
> >> alias=0, position=5, device=Kollmorgen AKD
> >>
> >> alias=0, position=6, device=MTS LVDT
> >>
> >> SYSTEM TWO:
> >>
> >> EtherLAB Master 1.52, E1000E Driver, Scan Rate 8Khz, Ubuntu Server
> >> 14.04LTS, RT-PREEMPT 3.12.50-rt68
> >>
> >> alias=0, position=0, device=EK1100
> >>
> >> alias=0, position=1, device=EL3001
> >>
> >> alias=0, position=2, device=EL1104
> >>
> >> alias=0, position=3, device=EL1104
> >>
> >> alias=0, position=4, device=EL1104
> >>
> >> alias=0, position=5, device=EL2004
> >>
> >> alias=0, position=6, device=EL2004
> >>
> >> alias=0, position=7, device=EL9505
> >>
> >> alias=0, position=8, device=EL7041
> >>
> >> alias=0, position=9, device=EL7041
> >>
> >> alias=0, position=10, device=EL7041
> >>
> >> alias=0, position=11, device=EL7041
> >>
> >> alias=0, position=12, device=EL7041
> >>
> >> alias=0, position=13, device=EL7041
> >>
> >> alias=0, position=14, device=EK1110
> >>
> >> alias=1, position=0, device=SIGMA5-05
> >>
> >> alias=2, position=0, device=Yaskawa SIGMA5-05
> >>
> >> alias=3, position=0, device=Yaskawa SIGMA5-05
> >>
> >> Both of the system are fully operational. However, for various
> >> reasons, I need to implement distributed clocks on these systems.
> >> I’ve never been able to get this to work.
> >>
> >> What follows is the code I used for both systems to try this. I read
> >> through examples on the mailing list, plus the examples, but I’m not
> >> seeing what I’m doing wrong. The result is always the same: all the
> >> fieldbus cards go into operation, but the servo drives won’t because
> >> of “bad configuration.” Take out the distributed clock code, and
> >> they work fine. I’m getting away with it for now, but I do need
> >> better clock resolution.
> >>
> >> The systems have an LRW domain, then a separate read domain and
> >> write domain for the servo drive(s) for a total of three domains
> >> (LRW, read, write). The yaskawa drives necessitate this. The scan
> >> rate is usually 4Khz, but I have tried it at both 1Khz and 8Khz and
> >> gotten the same results. Everything about the implementation is
> >> fairly straight-forward. There’s just something fundamental about
> >> the DC configuration that I’m not understanding.
> >>
> >> Almost all the code below is taken right from the examples or the
> >> message boards (thanks, everybody!). If anyone could tell me what
> >> I’m going wrong or offer any insights, it’s greatly appreciated. For
> >> brevity, I tried to narrow it down to relevant parts, but please let
> >> me know any additional information or code I can provide.
> >>
> >> Thank you in advance,
> >>
> >> Tom
> >>
> >> **********************************************************
> >>
> >> // EtherCAT distributed clock variables
> >>
> >> #define DC_FILTER_CNT 1024
> >>
> >> #define SYNC_MASTER_TO_REF 1
> >>
> >> static uint64_t dc_start_time_ns = 0LL;
> >>
> >> static uint64_t dc_time_ns = 0;
> >>
> >> static uint8_t dc_started = 0;
> >>
> >> static int32_t dc_diff_ns = 0;
> >>
> >> static int32_t prev_dc_diff_ns = 0;
> >>
> >> static int64_t dc_diff_total_ns = 0LL;
> >>
> >> static int64_t dc_delta_total_ns = 0LL;
> >>
> >> static int dc_filter_idx = 0;
> >>
> >> static int64_t dc_adjust_ns;
> >>
> >> static int64_t system_time_base = 0LL;
> >>
> >> static uint64_t wakeup_time = 0LL;
> >>
> >> static uint64_t overruns = 0LL;
> >>
> >> /** Get the time in ns for the current cpu, adjusted by
> >> system_time_base.
> >>
> >> *
> >>
> >> * \attention Rather than calling rt_get_time_ns() directly, all
> >> application
> >>
> >> * time calls should use this method instead.
> >>
> >> *
> >>
> >> * \ret The time in ns.
> >>
> >> */
> >>
> >> uint64_t system_time_ns(void)
> >>
> >> {
> >>
> >> struct timespec ts;
> >>
> >> clock_gettime(GLOBAL_CLOCK_TO_USE, &ts);
> >>
> >> return TIMESPEC2NS(ts);
> >>
> >> }
> >>
> >> static
> >>
> >> void sync_distributed_clocks(void)
> >>
> >> {
> >>
> >> uint32_t ref_time = 0;
> >>
> >> uint64_t prev_app_time = dc_time_ns;
> >>
> >> dc_time_ns = system_time_ns();
> >>
> >> // set master time in nano-seconds
> >>
> >> ecrt_master_application_time(master_, dc_time_ns);
> >>
> >> // get reference clock time to synchronize master cycle
> >>
> >> ecrt_master_reference_clock_time(master_, &ref_time);
> >>
> >> dc_diff_ns = (uint32_t) prev_app_time - ref_time;
> >>
> >> // call to sync slaves to ref slave
> >>
> >> ecrt_master_sync_slave_clocks(master_);
> >>
> >> }
> >>
> >> /** Return the sign of a number
> >>
> >> *
> >>
> >> * ie -1 for -ve value, 0 for 0, +1 for +ve value
> >>
> >> *
> >>
> >> * \retval the sign of the value
> >>
> >> */
> >>
> >> #define sign(val) \
> >>
> >> ({ typeof (val) _val = (val); \
> >>
> >> ((_val > 0) - (_val < 0)); })
> >>
> >> /*****************************************************************************/
> >>
> >> /** Update the master time based on ref slaves time diff
> >>
> >> *
> >>
> >> * called after the ethercat frame is sent to avoid time jitter in
> >>
> >> * sync_distributed_clocks()
> >>
> >> */
> >>
> >> static unsigned int cycle_ns = 1000000; // 1 millisecond
> >>
> >> void update_master_clock(void)
> >>
> >> {
> >>
> >> // calc drift (via un-normalised time diff)
> >>
> >> int32_t delta = dc_diff_ns - prev_dc_diff_ns;
> >>
> >> prev_dc_diff_ns = dc_diff_ns;
> >>
> >> // normalise the time diff
> >>
> >> dc_diff_ns =
> >>
> >> ((dc_diff_ns + (cycle_ns / 2)) % cycle_ns) - (cycle_ns / 2);
> >>
> >> // only update if primary master
> >>
> >> if (dc_started) {
> >>
> >> // add to totals
> >>
> >> dc_diff_total_ns += dc_diff_ns;
> >>
> >> dc_delta_total_ns += delta;
> >>
> >> dc_filter_idx++;
> >>
> >> if (dc_filter_idx >= DC_FILTER_CNT) {
> >>
> >> // add rounded delta average
> >>
> >> dc_adjust_ns +=
> >>
> >> ((dc_delta_total_ns + (DC_FILTER_CNT / 2)) /
> >> DC_FILTER_CNT);
> >>
> >> // and add adjustment for general diff (to pull in drift)
> >>
> >> dc_adjust_ns += sign(dc_diff_total_ns / DC_FILTER_CNT);
> >>
> >> // limit crazy numbers (0.1% of std cycle time)
> >>
> >> if (dc_adjust_ns < -1000) {
> >>
> >> dc_adjust_ns = -1000;
> >>
> >> }
> >>
> >> if (dc_adjust_ns > 1000) {
> >>
> >> dc_adjust_ns = 1000;
> >>
> >> }
> >>
> >> // reset
> >>
> >> dc_diff_total_ns = 0LL;
> >>
> >> dc_delta_total_ns = 0LL;
> >>
> >> dc_filter_idx = 0;
> >>
> >> }
> >>
> >> // add cycles adjustment to time base (including a spot
> >> adjustment)
> >>
> >> system_time_base += dc_adjust_ns + sign(dc_diff_ns);
> >>
> >> }
> >>
> >> else {
> >>
> >> dc_started = (dc_diff_ns != 0);
> >>
> >> if (dc_started)
> >>
> >> {
> >>
> >> // record the time of this initial cycle
> >>
> >> dc_start_time_ns = dc_time_ns;
> >>
> >> }
> >>
> >> }
> >>
> >> }
> >>
> >> struct timespec dcTime_;
> >>
> >> int
> >>
> >> ecatMain_process(void* lp)
> >>
> >> {
> >>
> >> ecrt_master_receive(master_);
> >>
> >> clock_gettime(CLOCK_REALTIME, &dcTime_);
> >>
> >> ecrt_master_application_time(master_, TIMESPEC2NS(dcTime_));
> >>
> >> ecrt_master_sync_reference_clock(master_);
> >>
> >> ecrt_master_sync_slave_clocks(master_);
> >>
> >> ecrt_domain_process(lrwDomainMgr_.domain);
> >>
> >> ecrt_domain_process(noLrwWriteDomainMgr_.domain);
> >>
> >> ecrt_domain_process(noLrwReadDomainMgr_.domain);
> >>
> >> … // handle my business
> >>
> >> // write application time to master
> >>
> >> clock_gettime(CLOCK_REALTIME, &dcTime_);
> >>
> >> ecrt_master_application_time(master_, TIMESPEC2NS(dcTime_));
> >>
> >> if (sync_ref_counter_)
> >>
> >> {
> >>
> >> sync_ref_counter_--;
> >>
> >> }
> >>
> >> else
> >>
> >> {
> >>
> >> sync_ref_counter_ = 1; // sync every cycle
> >>
> >> ecrt_master_sync_reference_clock(master_);
> >>
> >> }
> >>
> >> // send process data
> >>
> >> ecrt_domain_queue(lrwDomainMgr_.domain);
> >>
> >> ecrt_domain_queue(noLrwWriteDomainMgr_.domain);
> >>
> >> ecrt_domain_queue(noLrwReadDomainMgr_.domain);
> >>
> >> // sync distributed clock just before master_send to set
> >>
> >> // most accurate master clock time
> >>
> >> sync_distributed_clocks();
> >>
> >> // send EtherCAT data
> >>
> >> ecrt_master_send(master_);
> >>
> >> // update the master clock
> >>
> >> // Note: called after ecrt_master_send() to reduce time
> >>
> >> // jitter in the sync_distributed_clocks() call
> >>
> >> update_master_clock();
> >>
> >> return 1;
> >>
> >> }
> >>
> >> int
> >>
> >> ecatMain_start(void* lp)
> >>
> >> {
> >>
> >> //
> >>
> >> // domain regs must end in a null entry
> >>
> >> //
> >>
> >> lrwDomainMgr_.domainRegs = realloc(
> >>
> >> lrwDomainMgr_.domainRegs,
> >>
> >> sizeof(ec_pdo_entry_reg_t) * (lrwDomainMgr_.size + 1) );
> >>
> >> memset(
> >>
> >> &(lrwDomainMgr_.domainRegs[lrwDomainMgr_.size]),
> >>
> >> 0,
> >>
> >> sizeof(ec_pdo_entry_reg_t) );
> >>
> >> noLrwReadDomainMgr_.domainRegs = realloc(
> >>
> >> noLrwReadDomainMgr_.domainRegs,
> >>
> >> sizeof(ec_pdo_entry_reg_t) * (noLrwReadDomainMgr_.size + 1) );
> >>
> >> memset(
> >>
> >> &(noLrwReadDomainMgr_.domainRegs[noLrwReadDomainMgr_.size]),
> >>
> >> 0,
> >>
> >> sizeof(ec_pdo_entry_reg_t) );
> >>
> >> noLrwWriteDomainMgr_.domainRegs = realloc(
> >>
> >> noLrwWriteDomainMgr_.domainRegs,
> >>
> >> sizeof(ec_pdo_entry_reg_t) * (noLrwWriteDomainMgr_.size + 1) );
> >>
> >> memset(
> >>
> >> &(noLrwWriteDomainMgr_.domainRegs[noLrwWriteDomainMgr_.size]),
> >>
> >> 0,
> >>
> >> sizeof(ec_pdo_entry_reg_t) );
> >>
> >> //
> >>
> >> // NOTE: the Output Domain must be registered with
> >>
> >> // ecrt_domain_reg_pdo_entry_list before the Input Domain otherwise you
> >>
> >> // will not have any data exchanged even though the drive goes into OP
> >>
> >> // mode.
> >>
> >> //
> >>
> >> PRINT("\nAttempting to register PDOs on WRITE ONLY domain...\n");
> >>
> >> if (ecrt_domain_reg_pdo_entry_list(
> >>
> >> noLrwWriteDomainMgr_.domain, noLrwWriteDomainMgr_.domainRegs))
> >>
> >> {
> >>
> >> PRINT("WRITE ONLY PDO entry registration failed!\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> PRINT("\nAttempting to register PDOs on READ ONLY domain...\n");
> >>
> >> if (ecrt_domain_reg_pdo_entry_list(
> >>
> >> noLrwReadDomainMgr_.domain, noLrwReadDomainMgr_.domainRegs))
> >>
> >> {
> >>
> >> PRINT("READ ONLY PDO entry registration failed!\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> //
> >>
> >> // And now we register the bi-directional domain.
> >>
> >> //
> >>
> >> PRINT("\nAttempting to register PDOs on LRW domain...\n");
> >>
> >> if (ecrt_domain_reg_pdo_entry_list(
> >>
> >> lrwDomainMgr_.domain, lrwDomainMgr_.domainRegs))
> >>
> >> {
> >>
> >> PRINT("LRW PDO entry registration failed!\n");
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> /*
> >>
> >> * Finishes the configuration phase and prepares for cyclic operation.
> >>
> >> * This function tells the master that the configuration phase
> >>
> >> * is finished and the realtime operation will begin.
> >>
> >> * The function allocates internal memory for the domains and calculates
> >>
> >> * the logical FMMU addresses for domain members.
> >>
> >> * It tells the master state machine that the bus configuration is
> >>
> >> * now to be applied
> >>
> >> */
> >>
> >> PRINT("\nAttempting to activate ECAT master...\n");
> >>
> >> if (ecrt_master_activate(master_))
> >>
> >> {
> >>
> >> PRINT(
> >>
> >> "%s Failed to activate master!\n",
> >>
> >> __FUNCTION__ );
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> /*
> >>
> >> * Returns the domain's process data.
> >>
> >> */
> >>
> >> PRINT( "%s getting LRW process data from master.\n", __FUNCTION__ );
> >>
> >> if (!(lrwDomainMgr_.processData
> >>
> >> = ecrt_domain_data(lrwDomainMgr_.domain)))
> >>
> >> {
> >>
> >> PRINT(
> >>
> >> "%s set ecProcessData -- domain data is NULL!\n",
> >>
> >> __FUNCTION__ );
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> if (!(noLrwReadDomainMgr_.processData
> >>
> >> = ecrt_domain_data(noLrwReadDomainMgr_.domain)))
> >>
> >> {
> >>
> >> PRINT(
> >>
> >> "%s set read ProcessData -- domain data is NULL!\n",
> >>
> >> __FUNCTION__ );
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> if (!(noLrwWriteDomainMgr_.processData
> >>
> >> = ecrt_domain_data(noLrwWriteDomainMgr_.domain)))
> >>
> >> {
> >>
> >> PRINT(
> >>
> >> "%s set write ProcessData -- domain data is NULL!\n",
> >>
> >> __FUNCTION__ );
> >>
> >> return FALSE;
> >>
> >> }
> >>
> >> … // blah blah blah
> >>
> >> doScan_ = TRUE;
> >>
> >> PRINT( "%s completed successfully.\n", __FUNCTION__ );
> >>
> >> return TRUE;
> >>
> >> }
> >>
> >>
> >>
> >> _______________________________________________
> >> etherlab-users mailing list
> >> etherlab-users at etherlab.org
> >> http://lists.etherlab.org/mailman/listinfo/etherlab-users
> >>
> >_______________________________________________
> >etherlab-users mailing list
> >etherlab-users at etherlab.org
> >http://lists.etherlab.org/mailman/listinfo/etherlab-users
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users
Outbound scan for Spam or Virus by Barracuda at Delta Tau
More information about the Etherlab-users
mailing list