[etherlab-users] Control loop at higher frequencies
Gavin Lambert
gavin.lambert at tomra.com
Thu Nov 14 00:10:00 CET 2019
If you’re on the default branch (and not stable-1.5), you can enable overlapped mapping for a slave via ecrt_slave_config_overlapping_pdos. By default it assumes that the slave doesn’t support overlapped data. (Or the master app doesn’t --- bear in mind that with overlapped data you must rewrite all outputs every cycle or it will transmit garbage data, whereas with non-overlapped data you only need to rewrite the data that has changed. You have to be similarly careful with interpreting “inputs” from non-responsive slaves, which can affect how you deal with partial-WC frames.)
Having said that, it also looks like some of the related code has been commented out with a “FIXME”, so it’s possible that it doesn’t actually work. I haven’t tested this myself.
Gavin Lambert
Senior Software Developer
[cid:logo_compac_5dcf97ef-52f5-498c-8b9b-728410ddffaf.png]
[cid:compacicon_82e8a8c7-154a-4a32-9720-a5badb6258e0.png]<http://www.compacsort.com> [cid:facebook_fa85b924-53b9-45cc-8162-0564f64ec3a3.png] <https://www.facebook.com/Compacsort> [cid:linkedin_4ec016ad-84fa-443c-85a3-b9615a4ccef8.png] <https://www.linkedin.com/company/compac-sorting-equipment/> [cid:youtube_32142163-fc27-4aed-b14d-e8a377f98a6d.png] <https://vimeo.com/compacsort> [cid:twitter_d89338d8-98c8-4b65-9a9e-7b1333160b0d.png] <https://twitter.com/compacsort> [cid:insta2_1cd85de9-b3a2-4971-9904-52b2481a7c82.png] <https://www.instagram.com/compacsort/>
COMPAC SORTING EQUIPMENT LTD | 4 Henderson Pl | Onehunga | Auckland 1061 | New Zealand
Switchboard: +64 96 34 00 88 | tomra.com<http://www.tomra.com>
The information contained in this communication and any attachment is confidential and may be legally privileged. It should only be read by the person(s) to whom it is addressed. If you have received this communication in error, please notify the sender and delete the communication.
From: Jordan Palacios <jordan.palacios at pal-robotics.com>
Sent: Thursday, 14 November 2019 04:46
To: Gavin Lambert <gavin.lambert at tomra.com>
Cc: Graeme Foot <Graeme.Foot at touchcut.com>; etherlab-users at etherlab.org
Subject: Re: [etherlab-users] Control loop at higher frequencies
Hi again.
Thank you both for your answers.
We've been waiting for the CU1128 and ET2000 to arrive before continuing our tests. Here are our findings.
As for the CU1128 it is as both of you predicted, the improvement over the CX-JC06 is negligible.
Using the ET2000 and Wireshark we could finally obtain a reliable measure of the EtherCAT frame round trip time. The Time column is set to show time since previous captured packet.
[cid:image002.jpg at 01D59AE1.8CB0BE10]
This confirms the delay introduced by the slaves to be around 40us,
Then we tried to measure the delay caused by the network card. This has proved to be tricky since we can't measure it reliably. In the end what we did is finding how fast could we send consecutive frames. We did this by gradually increasing the frequency of the control loop. Finally, for a datagram of length 1216 (our full slave configuration) we can't go over 100us.
100us is the delay we assume for the network card. This delay is directly related to the frame length, i.e., if we reduce the datagram length we can go over 100us. We did some tests, and we have found out that if we can manage to reduce to datagram to around 650 we can actually control at 4KHz reliably.
By the way, here is some network card information.
EtherCAT: Master driver 1.5.2 551c87788b5e+
EtherCAT: 1 master waiting for devices.
e1000e 0000:03:00.0 eth0: removed PHC
e1000e: eth0 NIC Link is Down
e1000e 0000:00:19.0 eth1: removed PHC
ec_e1000e: EtherCAT-capable Intel(R) PRO/1000 Network Driver - 3.2.6-k-EtherCAT
ec_e1000e: Copyright(c) 1999 - 2015 Intel Corporation.
ec_e1000e 0000:00:19.0: Interrupt Throttling Rate (ints/sec) set to dynamic conservative mode
ec_e1000e 0000:00:19.0 0000:00:19.0 (uninitialized): registered PHC clock
EtherCAT: Accepting 00:13:95:23:67:A1 as main device for master 0.
EtherCAT 0: Starting EtherCAT-IDLE thread.
ec_e1000e 0000:00:19.0 ecm0 (uninitialized): (PCI Express:2.5GT/s:Width x1) 00:13:95:23:67:a1
ec_e1000e 0000:00:19.0 ecm0 (uninitialized): Intel(R) PRO/1000 Network Connection
ec_e1000e 0000:00:19.0 ecm0 (uninitialized): MAC: 10, PHY: 11, PBA No: FFFFFF-0FF
ec_e1000e 0000:03:00.0: Interrupt Throttling Rate (ints/sec) set to dynamic conservative mode
ec_e1000e 0000:03:00.0 0000:03:00.0 (uninitialized): registered PHC clock
ec_e1000e 0000:03:00.0 eth0: (PCI Express:2.5GT/s:Width x1) 00:0c:8b:20:05:1f
ec_e1000e 0000:03:00.0 eth0: Intel(R) PRO/1000 Network Connection
ec_e1000e 0000:03:00.0 eth0: MAC: 3, PHY: 8, PBA No: FFFFFF-0FF
ec_e1000e: ecm0 NIC Link is Up 100 Mbps Full Duplex, Flow Control: None
ec_e1000e 0000:00:19.0 ecm0 (uninitialized): 10/100 speed: disabling TSO
So now we have switched to looking into reducing the datagram size. After removing some non essential slaves we are left with 32 Elmo Gold Twitter boards. With this configuration the datagram length is 1132 with LRW taking 1088.
This is the PDO mapping for each Elmo slave:
SM0: PhysAddr 0x1800, DefaultSize 140, ControlRegister 0x26, Enable 1
SM1: PhysAddr 0x1900, DefaultSize 140, ControlRegister 0x22, Enable 1
SM2: PhysAddr 0x1100, DefaultSize 32, ControlRegister 0x64, Enable 1
RxPDO 0x1600 ""
PDO entry 0x607a:00, 32 bit, ""
PDO entry 0x60fe:01, 32 bit, ""
PDO entry 0x6040:00, 16 bit, ""
RxPDO 0x1607 ""
PDO entry 0x6060:00, 8 bit, ""
PDO entry 0x6071:00, 16 bit, ""
RxPDO 0x160e ""
PDO entry 0x6073:00, 16 bit, ""
SM3: PhysAddr 0x1180, DefaultSize 32, ControlRegister 0x20, Enable 1
TxPDO 0x1a07 ""
PDO entry 0x6041:00, 16 bit, ""
PDO entry 0x6061:00, 8 bit, ""
PDO entry 0x6078:00, 16 bit, ""
PDO entry 0x6064:00, 32 bit, ""
PDO entry 0x606c:00, 32 bit, ""
PDO entry 0x2205:01, 16 bit, ""
PDO entry 0x20a0:00, 32 bit, ""
We use 15 bytes for RxPDO and 19 bytes for TxPDO. This adds to 34 bytes for each slave. 34 * 32 = 1088 which is our current LRW.
AFAIK shouldn't the input and output share the same space in the datagram? We expected the size used by each slave to be max(RxPDO, TxPDO) instead of the sum.
At least this is what we understand from EtherCAT documentation.
[cid:image004.png at 01D59AE1.8CB0BE10]
We did a quick setup using TwinCAT and the LRW is in fact optimized there.
On our application we use ecrt_slave_config_pdos for PDO configuration. I looked into etherlab documentation and the rest of the PDO configuration functions but could not find nothing related to this.
If the space used for input and output could be shared our issues would be solved. Maybe we are doing something wrong?
Once again, thanks for your help.
Kind regards.
Jordán.
On Fri, 1 Nov 2019 at 00:04, Gavin Lambert <gavin.lambert at tomra.com<mailto:gavin.lambert at tomra.com>> wrote:
FYI, the CU1128 has three internal ESCs:
[cid:image005.png at 01D59AE1.8CB0BE10]
Due to the internal port ordering, the packets traverse the ports in their numeric order (a packet arriving at 1 will be sent to 2; when it returns back through 2 it will be sent to 3, etc).
I haven’t personally tested the port latency of the CU1128, but I think I remember it being negligible.
Regarding using a switch for monitoring: the only configuration which is officially supported is to put the monitoring switch between the master and first slave. (The entire slave network is conceptually one big Ethernet device.) Doing it elsewhere may or may not work depending on your particular layout, and it will certainly cause higher latency (and some switches are better than others).
Gavin Lambert
Senior Software Developer
[cid:image006.png at 01D59AE1.8CB0BE10]
[cid:image007.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.compacsort.com&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693114194&sdata=boWt1J%2B6UB68ORPWQHwGf9wqM3MYThVz7k9bc2p4XhY%3D&reserved=0>[cid:image008.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693114194&sdata=ahwzGnx96JbWMzvBbW4Zh6%2FLvqb3fcTLJ9V%2FiLfRMe8%3D&reserved=0>[cid:image009.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcompac-sorting-equipment%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693124148&sdata=CCK5SsfN96gqLZMm3f823IYSPJ5QqkvmWIz9argoD8A%3D&reserved=0>[cid:image010.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fvimeo.com%2Fcompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693124148&sdata=ySgYm9hLPJda6XtwyUn3q24HkabX%2BD6dEaUdCiWRkBo%3D&reserved=0>[cid:image011.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fcompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693124148&sdata=vwzif4avUqLnPFz2oJMu7hBrjTmREGrdqsmmbux8uy8%3D&reserved=0>[cid:image012.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Fcompacsort%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693134105&sdata=vUOu5r7Xx5seFchQ%2F0QZ2XrNqpe0dB5NlgFowNP990o%3D&reserved=0>
COMPAC SORTING EQUIPMENT LTD | 4 Henderson Pl | Onehunga | Auckland 1061 | New Zealand
Switchboard: +64 96 34 00 88 | tomra.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.tomra.com&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693134105&sdata=X1qhegTYCeAMTPFbOA2G3zp8%2FoYfEAX09VDbmPkRx9I%3D&reserved=0>
The information contained in this communication and any attachment is confidential and may be legally privileged. It should only be read by the person(s) to whom it is addressed. If you have received this communication in error, please notify the sender and delete the communication.
From: Graeme Foot
Sent: Friday, 1 November 2019 11:20
To: Jordan Palacios <jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>>
Cc: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: Re: [etherlab-users] Control loop at higher frequencies
Hi Jordan,
The GX-JC06 is a 6 port junction. The timings with and without the GX-JC06 look about correct. Just to be sure you know how they work, the EtherCAT frames are passed to each port of the junction sequentially, not in parallel. It will also pass each port of the junction regardless of whether it is open or not, with a time overhead per port. I don't have the documentation for the GX-JC06, but here is a diagram from the EK1100:
[cid:image013.png at 01D59AE1.8CB0BE10]
So with your example where one branch is connect direct to the master vs via the GX-JC06 I would expect the time to increase by approx. 620ns per MII port and 135ns per EBUS port (from your info below). It looks like the junction is made up of two 4 port chips joined by the EBUS ports, something like this:
[cid:image014.png at 01D59AE1.8CB0BE10]
So you need to add the overhead of:
- branch slave return to CX-JC06 (1 x 620ns)
- EBUS to EBUS link (2 x 135)
- MII ports (8 x 620)
That adds up to approx. 4610ns extra, totalling 8070ns (within ballpark of your 8220ns value, also based on a few assumptions).
Adding each new branch will add the overhead of the entire branch (the time taken for the frame to get to the last slave of the branch, and return).
I would expect the a Beckhoff CU1128 to behave very similarly, except that it sounds like the per port overhead is slightly slower (1000ns vs 620ns).
I'm still picking it's something at the master / device driver end.
Maybe you could check the ethercat version of the e1000e driver is in use correctly. I'm still running kernel 2.6.32 and connect via a CX2100 so not sure if there's any differences to your kernel and using the e1000e, but from my dmesg I can see:
EtherCAT: 1 master waiting for devices.
ec_cx2100: EtherCAT-capable Beckhoff CX2100 EtherCAT Network Driver (Revision 2)
ec_cx2100: Found EtherCAT Master (0x0014), Revision: 0x0000, txDMA: 0x01, rxDMA: 0x00
ec_cx2100: EtherCAT Master, MAC address: 00:01:05:13:7e:d0, Link: Connected
EtherCAT: Accepting 00:01:05:13:7E:D0 as main device for master 0.
I do also have the ec_e1000e driver for the other ports...
ec_e1000e: Ethercat-capable Intel(R) PRO/1000 Network Driver - 1.0.2-k2(ethercat)
Doing a "lspci -k" also shows that the ethercat versions of the drivers are correctly loaded:
02:00.0 Class 0200: 8086:10d3 ec_e1000e
03:00.0 Class 0200: 8086:10d3 ec_e1000e
04:00.0 Class ff00: 15ec:5000 ec_cx2100
Not sure what else to check for.
Regards,
Graeme.
From: Jordan Palacios <jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>>
Sent: Friday, 1 November 2019 1:23 AM
To: Gavin Lambert <gavin.lambert at tomra.com<mailto:gavin.lambert at tomra.com>>
Cc: Graeme Foot <Graeme.Foot at touchcut.com<mailto:Graeme.Foot at touchcut.com>>; etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: Re: [etherlab-users] Control loop at higher frequencies
Hi,
Thanks both of you for your answers. I'll try to address all your points.
We run our master in a PC with Ubuntu 16.04. Kernel 4.9.115 with the RT_PREEMPT patch. The network driver used by the master is the e1000e. Here are the details of the network card:
description: Ethernet interface
product: 82579LM Gigabit Network Connection
vendor: Intel Corporation
physical id: 19
bus info: pci at 0000:00:19.0<mailto:pci at 0000:00:19.0>
logical name: eth1
version: 04
serial: 00:13:95:2e:e1:b0
capacity: 1Gbit/s
width: 32 bits
clock: 33MHz
capabilities: bus_master cap_list ethernet physical tp 10bt 10bt-fd 100bt 100bt-fd 1000bt-fd autonegotiation
configuration: autonegotiation=on broadcast=yes driver=e1000e driverversion=3.2.6-k firmware=0.15-4 latency=0 link=no multicast=yes port=twisted pair
resources: irq:26 memory:f7f00000-f7f1ffff memory:f7f35000-f7f35fff ioport:f080(size=32)
The slaves are connected in a star topology using an OMROM GX-JC06 EtherCAT Junction<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ia.omron.com%2Fproducts%2Ffamily%2F3079%2Ffeature.html&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693144062&sdata=z8JISLCZiRSYSXMii90R21%2B5W2DJcVkUMzW4MMeAGeI%3D&reserved=0>. I didn't mention this in my previous mail but we had detected that this junction does indeed add considerable delay. For example, if we connect one of the branches directly to the control PC we measure a DC system time transmission delay of 3460ns. When the same branch is connected to the junction with no other slaves reports 8220ns. This gets worse when we start adding more slaves in different ports until we reach the 38995ns I wrote in my first mail.
Here is the info from the two slaves that comprise the junction:
=== Master 0, Slave 0 ===
Device: Main
State: PREOP
Flag: +
Identity:
Vendor Id: 0x00000083
Product code: 0x00000064
Revision number: 0x00010000
Serial number: 0x00000000
DL information:
FMMU bit operation: no
Distributed clocks: yes, 64 bit
DC system time transmission delay: 0 ns
Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
0* MII up open yes - 1316003530 0 0
1 MII up open yes 8 1316019530 16000 620
2 EBUS up open yes 15 1316043660 40130 135
3 MII up open yes 1 1316011570 8040 640
General:
Group: Junction Slave
Image name:
Order number: GX-JC06(IN,X2,X3)
Device name: GX-JC06(IN,X2,X3)�@6�|�[�g�����X���[�u
Flags:
Enable SafeOp: no
Enable notLRW: no
Current consumption: 0 mA
=== Master 0, Slave 15 ===
Device: Main
State: PREOP
Flag: +
Identity:
Vendor Id: 0x00000083
Product code: 0x00000065
Revision number: 0x00010000
Serial number: 0x00000000
DL information:
FMMU bit operation: no
Distributed clocks: yes, 64 bit
DC system time transmission delay: 16135 ns
Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
0* EBUS up open yes 0 1320871430 0 135
1 MII up open yes 24 1320892930 21500 620
2 MII up open yes 35 1320895290 23860 620
3 MII up open yes 16 1320880610 9180 630
General:
Group: Junction Slave
Image name:
Order number: GX-JC06(X4,X5,X6)
Device name: GX-JC06(X4,X5,X6)�@6�|�[�g�����X���[�u
Flags:
Enable SafeOp: no
Enable notLRW: no
Current consumption: 0 mA
We are now in the process of switching to a Beckhoff CU1128<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.beckhoff.com%2FCU1128%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693144062&sdata=32rc0rsNzLVLTghBq5yqBMa7EZNRNH2FKLLwjctHe4c%3D&reserved=0>. Their support has assured us that the delay introduced should be around 1us per port used and should remain constant independently of the number of slaves and frame size.
We tried a setup with a switch in the middle to capture the network traffic. Unfortunately we couldn't make it work. The master would simply fail to find any slaves in the network the moment the switch was plugged in. Even when there was no other PC/laptop connected to the switch to sniff the traffic. We'll give it another go.
We also took additional measures using two Beckhoff FB1111-0142<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.beckhoff.ee%2Fenglish.asp%3Fethercat%2Ffb1111.htm&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693144062&sdata=n1hwZvV9XnVKgC3VvzZezy%2BoxNekWvTl%2BvYreyphpd0%3D&reserved=0>. We connected one of them before the switch and the other after the last slave. Then took the measure of the delay between the signal of the SOF pins. The result was a delay of around 39.2us, something really close to the value reported by the DC system time transmission delay. Using this approach we took measures of different sections of the bus. So now we have an idea of the average delay introduced by each slave. This further confirmed the delay introduced by the OMROM junction.
The delay introduced by the PC network card is something we definitely haven't taken into account and may explain why we don't receive the frames on time. I don't think it as much as 550us though. If it was it wouldn't work at 2Khz neither.
Kind regards.
Jordán.
On Thu, 31 Oct 2019 at 00:07, Gavin Lambert <gavin.lambert at tomra.com<mailto:gavin.lambert at tomra.com>> wrote:
When you use the master debug interface (or the newly added “ethercat pcap” command, although you won’t have that in your version yet), the receive timestamps are the time that they are received by the master, which is the time that you called ecrt_master_receive.
You can get a better understanding of the “real” wire transfer time by connecting a separate monitoring device between the master and first slave – a proper network monitor is ideal, but you can made do with a standard Ethernet hub/switch with three ports connected (master, first slave, monitoring laptop running Wireshark), although for best results (especially if it’s a Windows laptop) you should disable all the network protocols on the laptop adapter other than the minimum it needs to do the Wireshark monitoring, so that it doesn’t inadvertently transmit packets of its own. (These won’t hurt the network itself, since both the master and slave will drop non-EtherCAT packets, but it may worsen the latency.) This will still be somewhat inaccurate since it’s still timestamping when the packet was processed rather than when it was actually received in hardware, but it’s likely to be more accurate than doing it on the master since it’s not waiting for the cycle delay.
As Graeme said, you can also put the monitoring device elsewhere in the network (all packets will always pass every point in the network – except the end), although then it becomes harder to meaningfully use the timestamps.
Gavin Lambert
Senior Software Developer
[cid:image006.png at 01D59AE1.8CB0BE10]
[cid:image007.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.compacsort.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693154019&sdata=fh43FInp4X4IUHE7gmD%2BkVwyeBNVapvzp9zodMwC6Kg%3D&reserved=0>[cid:image008.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693154019&sdata=6ionqStRxGFAjKcSLWHU9ffSF3QAqueXRDwRU%2By4yYo%3D&reserved=0>[cid:image009.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcompac-sorting-equipment%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693163976&sdata=ZXPPYRObBXQ32y9eB1HeSRW4VzBN2pPGdKabUDPOr4Y%3D&reserved=0>[cid:image010.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fvimeo.com%2Fcompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693163976&sdata=0uRmOh8s%2BdmVz5mrOy%2FLljVROFvdUnEn%2FNHDeMi6Gqw%3D&reserved=0>[cid:image011.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fcompacsort&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693173932&sdata=R3YValbz3zmFO0WD3XozJ%2Bw7C5oL17PvL4SAoxswB6E%3D&reserved=0>[cid:image012.png at 01D59AE1.8CB0BE10]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Fcompacsort%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693173932&sdata=5DyvEZWqgMMgGp8Itz%2Ba8pp1efwgSB3%2BVkK4GbjTJ3E%3D&reserved=0>
COMPAC SORTING EQUIPMENT LTD | 4 Henderson Pl | Onehunga | Auckland 1061 | New Zealand
Switchboard: +64 96 34 00 88 | tomra.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.tomra.com&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693173932&sdata=jNEOa75yvy2oHEZlgivpQE7mwYF3xMXXpTqoo%2BO3Vmo%3D&reserved=0>
The information contained in this communication and any attachment is confidential and may be legally privileged. It should only be read by the person(s) to whom it is addressed. If you have received this communication in error, please notify the sender and delete the communication.
From: Graeme Foot
Sent: Thursday, 31 October 2019 11:49
To: Jordan Palacios <jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>>
Cc: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: Re: [etherlab-users] Control loop at higher frequencies
Hi,
It is sounding like the data time on the wire is taking too long (> 250us).
Besides doubling the "DC system time transmission delay" of the last slave, you can also check the "Diff [ns]" value of your first slave. This may give you a more accurate idea if you have a star topology, as the return trip of the frame from the last slave bypasses the fingers of the stars. e.g.:
ethercat slaves -v -p0
=== Master 0, Slave 0 ===
Alias: 10001
Device: Main
State: OP
Flag: +
Identity:
Vendor Id: 0x00000002
Product code: 0x04562c52
Revision number: 0x00110000
Serial number: 0x00000000
DL information:
FMMU bit operation: no
Distributed clocks: yes, 64 bit
DC system time transmission delay: 0 ns
Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
0* EBUS up open yes - 3638440690 0 0
1 MII up open yes 1 3638442410 1720 560
2 N/A down closed no - - - -
3 N/C down closed no - - - -
You will also need to add on 2 * "master to first slave transmission delay" which you will probably need to guess. If you use a Beckhoff CX2020 (or similar) where the CX2100 is directly connected to the EBus this will likely be around 150us. If your master has an ethernet port and the first slave is an amp or a coupler this may be around 550us or more (depending on cable length). You could also calc the frame transmission time. Your frame length is 782 bytes. So that should take ~ 6 - 7us. Plus whatever other overheads the ethernet card / driver has.
Reducing the number of configured slaves (even with them still physically plugged in) will reduce the ec_master_domain_queue() and ec_master_send() overhead time, getting the frame to the wire quicker. It will also reduce the frame length and the related frame transmission time (especially if you remove slaves with bigger datagram overhead). It looks like this is enough to result in the total frame roundtrip time being reduce enough for it to return and be ready by the time that ec_master_receive() is called.
Just FYI, I have a machine downstairs at the moment with 42 slaves (14 of which are amps), linear topology. The last slaves transmission delay is 19560ns. The first slaves Diff is 39390ns. The EtherCAT frame size is 886 bytes. The ec_master_receive() to ec_master_send() time is approx 23us. So your values sound in line with what I have, except that the wireshark output is showing a large cycle time.
In general it's looking like the time on the wire is taking longer than it should. How are you capturing the EtherCAT frame data? e.g.: a switch between your master and first slave? If so, try moving it further down the chain, doing an "ethercat rescan" and check the transmission delays. See if the switch is causing a large delay between those slaves.
What is your network card and driver used by the master? What is your realtime system? If you are using tshark on the master PC there might be delays being introduced in the network card driver.
Regards,
Graeme.
From: etherlab-users <etherlab-users-bounces at etherlab.org<mailto:etherlab-users-bounces at etherlab.org>> On Behalf Of Jordan Palacios
Sent: Thursday, 31 October 2019 4:36 AM
To: etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: [etherlab-users] Control loop at higher frequencies
Hi.
We've been working with the etherlab master for some time now. On our current setup we have around 40 slaves and our control loop runs at 1Khz without any issues. We use the stable version of etherlab with the 20180622 patchset.
Recently we've tried increasing the loop frequency to achieve a better control. The target frequency is 4Khz. After some troubles we managed a stable control at 2Khz. Then we went for the 4Khz and this is where we have hit a roadblock.
A warning like this is generated each second:
[11547.183302] EtherCAT WARNING 0: 4000 datagrams UNMATCHED!
[11547.619399] EtherCAT WARNING: Datagram ffff88040b6bf318 (domain0-0-main) was SKIPPED 4004 times.
As per what Florian explained here<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.etherlab.org%2Fpipermail%2Fetherlab-users%2F2009%2F000386.html&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693183890&sdata=BZoAlHxCFNDCaCARiA6oR3IqleyLFawRPAkO8PRtKwY%3D&reserved=0> this means that the answer to the last datagram sent has not been received yet. I don't think this is related to the rate at which we execute the control loop. We have instrumented it and is steady at 250us with a jitter below 10us (see attachment). Furthermore, we have also enabled the ethercat master debug interface. Here is a sample of the traffic output using tshark:
7807 0.975750173 MS-NLB-PhysServer-19_95:2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 69
7808 0.975757725 Congatec_2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 0
7809 0.976000284 MS-NLB-PhysServer-19_95:2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 69
7810 0.976007872 Congatec_2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 0
7811 0.976252515 MS-NLB-PhysServer-19_95:2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 69
7812 0.976260050 Congatec_2e:e1:b0 → Broadcast ECAT 810 'LRW': Len: 782, Adp 0x0, Ado 0x0, Wc 0
The master received is done right at the beginning of the loop, and is followed by the domain process, domain queue and master send. The calculations are done after. We instrumented the received/send calls and we know together take around 20us.
We originally made our calculations before the domain queue and master send. After reading what Graeme explains here<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.etherlab.org%2Fpipermail%2Fetherlab-users%2F2018%2F003351.html&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693183890&sdata=x2Pa%2F8yXmFgW0olHEQCkhzkcCxXKUD91tKoZg1diZNA%3D&reserved=0> we changed the order to allow for more time for the data in the wire. This change helped achieving the 2Khz.
All of this means that the time at which the frames are received is another good indicator of the correct control loop periodicity. Note also how the next frame is sent right after.
Thing is, even though the WC is the expected (69 in this case), we think that these frames are always late. The datagram received is the one of the previous cycle. Hence the constant warning of 4000 datagrams skipped. The statistics reported by the "ethercat master" command show 4000 frames transmitted/received per second and no frames are lost.
Checking the "DC system time transmission delay" of the last slave we get a value of 38995 ns, which would translate to something like 80us for the frame to be in the wire. Keeping in mind we are allowing for 230us for the datagram to return (250us cycle minus 20us for receive/send) it should be more than enough. Yet something doesn't add up.
The only thing that seems to help is reducing the amount of slaves. If we switch to something like a 25 slave configuration then we manage to control at 4KHz without issues. We don't physically disconnect them though so the DC system time transmission delay remains the same. Obviously frame size is smaller.
We are not performing any calls related to distributed clocks in the master. If I understand correctly DC are used for synchronizing the data processing of the slaves. It should not affect the frame delay, right?
Any ideas are appreciated.
Kind regards.
Jordán.
--
Jordán Palacios
Software Engineer
[https://lh6.googleusercontent.com/mgsVJlQ9p5jN1eI-8SP0YOxUhv0BEXrjZFnqqzYgaopfqhinUDbC7abJqhSV9RmgauHBXoff-GMTrJpOL2B9iYbSUgQN3cY8gIFI1XzcMdqZ6nG_Qera_i9qg2VQk35dG0uR01Ut]
C/ Pujades 77-79, 4-4
08005 Barcelona, Spain
Skype jordanpalacios.pal-robotics
Tel +34 93 414 53 47<tel:%2B34%2093%20414%2053%2047>
jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>
www.pal-robotics.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693193845&sdata=7J%2B7Df3NCTQGZlCtqsBYk1bArzmEdVJ3NXL5Z8fjLkc%3D&reserved=0>
Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpalrobotics%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693193845&sdata=FgNpEnaMZOhKQdPl98nanfuEhpoLGIvhlsiiBY3zzKs%3D&reserved=0> | Twitter<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693193845&sdata=ENuK2Vp5o8qiEewBYDTepypE9Nu0UK9N6SAOlWa7mqc%3D&reserved=0> | YouTube<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.youtube.com%2Fuser%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693203804&sdata=Lhm9S%2FpFiEodDF08dU4ESAB8bSvg7NlsEOL%2FYIJDa%2F8%3D&reserved=0> | Blog<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fblog.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693203804&sdata=bKQjyh4LKSkabcwFcorbH4y4zDeAAUBe%2BeWENzK%2BUoo%3D&reserved=0>
AVISO DE CONFIDENCIALIDAD: Este mensaje y sus documentos adjuntos, pueden contener información privilegiada y/o confidencial que está dirigida exclusivamente a su destinatario. Si usted recibe este mensaje y no es el destinatario indicado, o el empleado encargado de su entrega a dicha persona, por favor, notifíquelo inmediatamente y remita el mensaje original a la dirección de correo electrónico indicada. Cualquier copia, uso o distribución no autorizados de esta comunicación queda estrictamente prohibida.
CONFIDENTIALITY NOTICE: This e-mail and the accompanying document(s) may contain confidential information which is privileged and intended only for the individual or entity to whom they are addressed. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of this e-mail and/or accompanying document(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender at the above e-mail address.
--
Jordán Palacios
Software Engineer
[https://lh6.googleusercontent.com/mgsVJlQ9p5jN1eI-8SP0YOxUhv0BEXrjZFnqqzYgaopfqhinUDbC7abJqhSV9RmgauHBXoff-GMTrJpOL2B9iYbSUgQN3cY8gIFI1XzcMdqZ6nG_Qera_i9qg2VQk35dG0uR01Ut]
C/ Pujades 77-79, 4-4
08005 Barcelona, Spain
Skype jordanpalacios.pal-robotics
Tel +34 93 414 53 47<tel:%2B34%2093%20414%2053%2047>
jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>
www.pal-robotics.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693213759&sdata=JsRbrx39l1HjQC6ThgXx7xMr4RklkBk9YW1cKj83ZK8%3D&reserved=0>
Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpalrobotics%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693213759&sdata=eU0pGqh%2FgvptaXdVZica%2Fo%2F0YW7FU5GoCE2r1aFLUA8%3D&reserved=0> | Twitter<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693223713&sdata=L5CRYjjPQvUkYaUhe82ygfU%2BXGyj5j%2F5c1zXlPPg2aQ%3D&reserved=0> | YouTube<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.youtube.com%2Fuser%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693223713&sdata=CQttbGa4dOohNgnVCgramT%2BJ5cwUHDh1hr88zspBJi8%3D&reserved=0> | Blog<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fblog.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693223713&sdata=TGqT5dEwNhy961YODpK%2FvhET18VK9Zc1facFwmI5uCA%3D&reserved=0>
AVISO DE CONFIDENCIALIDAD: Este mensaje y sus documentos adjuntos, pueden contener información privilegiada y/o confidencial que está dirigida exclusivamente a su destinatario. Si usted recibe este mensaje y no es el destinatario indicado, o el empleado encargado de su entrega a dicha persona, por favor, notifíquelo inmediatamente y remita el mensaje original a la dirección de correo electrónico indicada. Cualquier copia, uso o distribución no autorizados de esta comunicación queda estrictamente prohibida.
CONFIDENTIALITY NOTICE: This e-mail and the accompanying document(s) may contain confidential information which is privileged and intended only for the individual or entity to whom they are addressed. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of this e-mail and/or accompanying document(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender at the above e-mail address.
--
Jordán Palacios
Software Engineer
[https://lh6.googleusercontent.com/mgsVJlQ9p5jN1eI-8SP0YOxUhv0BEXrjZFnqqzYgaopfqhinUDbC7abJqhSV9RmgauHBXoff-GMTrJpOL2B9iYbSUgQN3cY8gIFI1XzcMdqZ6nG_Qera_i9qg2VQk35dG0uR01Ut]
C/ Pujades 77-79, 4-4
08005 Barcelona, Spain
Skype jordanpalacios.pal-robotics
Tel +34 93 414 53 47<tel:%2B34%2093%20414%2053%2047>
jordan.palacios at pal-robotics.com<mailto:jordan.palacios at pal-robotics.com>
www.pal-robotics.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693233670&sdata=3u9GXHB8tWUub0a6uYkJuS%2BSFPe8zAlTDGNSuT43lQo%3D&reserved=0>
Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpalrobotics%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693233670&sdata=MCwzDrKT%2BclUfqafY5GnJHjHGDuEFuUsBCgAaywOl34%3D&reserved=0> | Twitter<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693233670&sdata=UR8V418AbR5vFl%2FwAbQDKMdSfYco6d4dhCc1vGRnSmI%3D&reserved=0> | YouTube<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.youtube.com%2Fuser%2FPALRobotics&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693243627&sdata=mFEzBzUoWTdOonhGI8udTaeqTignjnAyQ0XVHTmXP4s%3D&reserved=0> | Blog<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fblog.pal-robotics.com%2F&data=02%7C01%7Cgavin.lambert%40tomra.com%7C6c3c34797eca4c5b52a908d7685097fe%7C4308d118edd143008a37cfeba8ad5898%7C0%7C0%7C637092567693243627&sdata=DdV4tLXnTGINmTsZDPz7dYX%2B5bpMno0KKt3WZGcBDvE%3D&reserved=0>
AVISO DE CONFIDENCIALIDAD: Este mensaje y sus documentos adjuntos, pueden contener información privilegiada y/o confidencial que está dirigida exclusivamente a su destinatario. Si usted recibe este mensaje y no es el destinatario indicado, o el empleado encargado de su entrega a dicha persona, por favor, notifíquelo inmediatamente y remita el mensaje original a la dirección de correo electrónico indicada. Cualquier copia, uso o distribución no autorizados de esta comunicación queda estrictamente prohibida.
CONFIDENTIALITY NOTICE: This e-mail and the accompanying document(s) may contain confidential information which is privileged and intended only for the individual or entity to whom they are addressed. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of this e-mail and/or accompanying document(s) is strictly prohibited. If you have received this e-mail in error, please immediately notify the sender at the above e-mail address.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 35195 bytes
Desc: image002.jpg
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 171761 bytes
Desc: image004.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0090.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 18857 bytes
Desc: image005.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0091.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 11438 bytes
Desc: image006.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0092.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1629 bytes
Desc: image007.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0093.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 1750 bytes
Desc: image008.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0094.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 1855 bytes
Desc: image009.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0095.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 1970 bytes
Desc: image010.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0096.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 20278 bytes
Desc: image011.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0097.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 1506 bytes
Desc: image012.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0098.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 31482 bytes
Desc: image013.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0099.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.png
Type: image/png
Size: 51254 bytes
Desc: image014.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0100.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_compac_5dcf97ef-52f5-498c-8b9b-728410ddffaf.png
Type: image/png
Size: 11438 bytes
Desc: logo_compac_5dcf97ef-52f5-498c-8b9b-728410ddffaf.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0101.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: compacicon_82e8a8c7-154a-4a32-9720-a5badb6258e0.png
Type: image/png
Size: 1629 bytes
Desc: compacicon_82e8a8c7-154a-4a32-9720-a5badb6258e0.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0102.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: facebook_fa85b924-53b9-45cc-8162-0564f64ec3a3.png
Type: image/png
Size: 1750 bytes
Desc: facebook_fa85b924-53b9-45cc-8162-0564f64ec3a3.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0103.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: linkedin_4ec016ad-84fa-443c-85a3-b9615a4ccef8.png
Type: image/png
Size: 1855 bytes
Desc: linkedin_4ec016ad-84fa-443c-85a3-b9615a4ccef8.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0104.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: youtube_32142163-fc27-4aed-b14d-e8a377f98a6d.png
Type: image/png
Size: 1970 bytes
Desc: youtube_32142163-fc27-4aed-b14d-e8a377f98a6d.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0105.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: twitter_d89338d8-98c8-4b65-9a9e-7b1333160b0d.png
Type: image/png
Size: 20278 bytes
Desc: twitter_d89338d8-98c8-4b65-9a9e-7b1333160b0d.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0106.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: insta2_1cd85de9-b3a2-4971-9904-52b2481a7c82.png
Type: image/png
Size: 1506 bytes
Desc: insta2_1cd85de9-b3a2-4971-9904-52b2481a7c82.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20191113/4117ab07/attachment-0107.png>
More information about the Etherlab-users
mailing list