[etherlab-users] Beckhoff encoder interface EL5101-0010 mapping issue

BUSSIERES Vincent vincent.bussieres at hemeria-group.com
Fri May 15 14:32:07 CEST 2020


Thanks Nico,

What’s you describe is for EL5101-0000 and EL5101-0090 modules, I am using EL5101-0010 with only Index 0x1600 and 0x1601.
Do you need to write something in encoder control register in order to read position ? Is the position always filled in?

[cid:image004.png at 01D62AC5.7CC02760]

Regards


Cordialement

Vincent BUSSIERES
Responsable Technique Logiciel

[1572337113342]
ZE Ma Campagne
36, Impasse Félix Nadar
16000 ANGOULEME
Tel: 33 (0)9.72.40.35.08
www.hemeria-group.com<https://webmail.nexeya.fr/owa/redir.aspx?C=GK_BqKCZef7LtPZnqnd_LGYr1NG9sz4Smy3iKIwO-pXqtJC7VgzXCA..&URL=http%3a%2f%2fwww.hemeria-group.com%2f>
P Afin de contribuer au respect de l'environnement, merci de n'imprimer ce courriel qu'en cas de nécessité.
Ce message et les fichiers pouvant être attachés sont confidentiels, réservés à l'usage unique des destinataires et n'engagent HEMERIA sous aucune forme que ce soit.
This email and any files transmitted with it are confidential, intented solely for the unique use of the recipients and don't commit HEMERIA.



De : Kivel Niko (PSI) <niko.kivel at psi.ch>
Envoyé : vendredi 15 mai 2020 14:14
À : Richard Hacker <ha at igh.de>; BUSSIERES Vincent <vincent.bussieres at hemeria-group.com>; etherlab-users at etherlab.org
Objet : Re: [etherlab-users] Beckhoff encoder interface EL5101-0010 mapping issue


Hi



here is what we map, only end of the lines from #14 ff. are interesting for you guys.



https://github.com/paulscherrerinstitute/ecmccfg/blob/19470cf1c9b71e52777a06f641394d85bc874918/hardware/Beckhoff_slaves/ecmcEL5101_32bit.cmd#L14



best

Niko


--
Paul Scherrer Institute
Dr. Niko Kivel
Forschungsstrasse 111
WBGB/017
5232 Villigen PSI
Switzerland

phone: +41 56 310 2226
email: niko.kivel at psi.ch<mailto:niko.kivel at psi.ch>
________________________________
From: etherlab-users <etherlab-users-bounces at etherlab.org<mailto:etherlab-users-bounces at etherlab.org>> on behalf of Richard Hacker <ha at igh.de<mailto:ha at igh.de>>
Sent: Friday, May 15, 2020 2:00:03 PM
To: BUSSIERES Vincent; etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
Subject: Re: [etherlab-users] Beckhoff encoder interface EL5101-0010 mapping issue

Don't be mislead by Beckhoff's XML description files. I've had numerous
fights with them about incorrect description files! "With TwinCAT it
works" is a standard response. Yeah right. That's because TwinCAT
typically ignores XML description files and reads the configuration
straight out of the slaves during a bus scan.

Usually we map RxPDO #x1601 and TxPDO #x1a01. There is quite a bit of
SDO configuration in #x800* to get right. You will need to check the
documentation.

Am 15/05/2020 um 12.00 schrieb BUSSIERES Vincent:
> Dear all,
>
> Finally, I mapped PDO like configurutation obtained using ethercat xml command.
> Mapping seems to be quite different from xml Beckhoff description file.
>
> Now I have no more problem with mapping, slave is in OP state.
> But I try to read encoder value using TxPdo 0x1a00 (0x6000:0x11:32) but I read always 0. Led status of inputs signal A,B, C are OK and change of states when I manually turned motor axis.
> When I write a value in counter value using TxPdo 0x1600 (0x7000:0x11:32), I read the good value with TxPdo.
>
> I don't know why I can't read the true counter value. Does someone have an idea?
>
> Regards
>
> Vincent BUSSIERES
> Responsable Technique Logiciel
>
>
> ZE Ma Campagne
> 36, Impasse Félix Nadar
> 16000 ANGOULEME
> Tel: 33 (0)9.72.40.35.08
> www.hemeria-group.com<http://www.hemeria-group.com>
> • Afin de contribuer au respect de l'environnement, merci de n'imprimer ce courriel qu'en cas de nécessité.
> Ce message et les fichiers pouvant être attachés sont confidentiels, réservés à l'usage unique des destinataires et n'engagent HEMERIA sous aucune forme que ce soit.
> This email and any files transmitted with it are confidential, intented solely for the unique use of the recipients and don't commit HEMERIA.
>
>
>
> -----Message d'origine-----
> De : Richard Hacker <ha at igh.de<mailto:ha at igh.de>>
> Envoyé : jeudi 14 mai 2020 17:05
> À : BUSSIERES Vincent <vincent.bussieres at hemeria-group.com<mailto:vincent.bussieres at hemeria-group.com>>; etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org>
> Objet : Re: [etherlab-users] Beckhoff encoder interface EL5101-0010 mapping issue
>
> [10918.274957] EtherCAT ERROR 0-main-5: AL status message 0x001E:
> "Invalid input configuration".
>
> Pls check your configuration... there is something wrong
>
> Restart your EC Network and before you start _any_ application, scan the bus for the available PDO's and use that for a start.
>
> Am 14/05/2020 um 16.59 schrieb BUSSIERES Vincent:
>> I map the inputs RxPdo and slave doesn't go in OP state and stay in PREOP.
>> You can see 2 errors in log file below:
>>
>> [10918.266966] EtherCAT ERROR 0-main-5: Failed to set SAFEOP state, slave refused state change (PREOP + ERROR).
>> [10918.274957] EtherCAT ERROR 0-main-5: AL status message 0x001E: "Invalid input configuration".
>>
>>
>> [10917.969204] EtherCAT: Requesting master 0...
>> [10917.969209] EtherCAT DEBUG 0: IDLE -> OPERATION.
>> [10917.969213] EtherCAT: Successfully requested master 0.
>> [10917.969222] EtherCAT DEBUG 0: ecrt_master_create_domain(master =
>> 0xffff895554eb6000) [10917.969226] EtherCAT DEBUG 0: Created domain 0.
>> [10917.969239] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969244] EtherCAT DEBUG 0: Creating slave configuration for 0:5, 0x00000002/0x13ED3052.
>> [10917.969251] EtherCAT DEBUG 0 0:5: Attached slave main-5.
>> [10917.969278] EtherCAT DEBUG 0 0:5: ecrt_slave_config_sync_manager(sc
>> = 0xffff895551db3000, sync_index = 0, dir = 1, watchdog_mode = 2)
>> [10917.969287] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_assign_clear(sc = 0xffff895551db3000, sync_index
>> = 0) [10917.969294] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_sync_manager(sc = 0xffff895551db3000, sync_index =
>> 1, dir = 2, watchdog_mode = 2) [10917.969300] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_assign_clear(sc = 0xffff895551db3000, sync_index = 1) [10917.969307] EtherCAT DEBUG 0 0:5: ecrt_slave_config_sync_manager(sc = 0xffff895551db3000, sync_index = 2, dir = 1, watchdog_mode = 1) [10917.969313] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_assign_clear(sc = 0xffff895551db3000, sync_index = 2) [10917.969324] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_assign_add(sc = 0xffff895551db3000, sync_index = 2, pdo_index = 0x1601) [10917.969327] EtherCAT DEBUG 0 0:5: Loading default mapping for PDO 0x1601.
>> [10917.969331] EtherCAT DEBUG 0 0:5: Entry 0x7000:01.
>> [10917.969334] EtherCAT DEBUG 0 0:5: Entry 0x7000:02.
>> [10917.969337] EtherCAT DEBUG 0 0:5: Entry 0x7000:03.
>> [10917.969339] EtherCAT DEBUG 0 0:5: Entry 0x7000:04.
>> [10917.969342] EtherCAT DEBUG 0 0:5: Entry 0x7000:11.
>> [10917.969349] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_clear(sc = 0xffff895551db3000, pdo_index
>> = 0x1601) [10917.969358] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1601, entry_index = 0x7000, entry_subindex = 0x01, entry_bit_length
>> = 1) [10917.969364] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1601, entry_index = 0x7000, entry_subindex = 0x02, entry_bit_length
>> = 1) [10917.969370] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1601, entry_index = 0x7000, entry_subindex = 0x03, entry_bit_length = 1) [10917.969376] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1601, entry_index = 0x7000, entry_subindex = 0x04, entry_bit_length = 1) [10917.969383] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1601, entry_index = 0x7000, entry_subindex = 0x11, entry_bit_length = 16) [10917.969388] EtherCAT DEBUG 0 0:5: ecrt_slave_config_sync_manager(sc = 0xffff895551db3000, sync_index = 3, dir = 2, watchdog_mode = 1) [10917.969393] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_assign_clear(sc = 0xffff895551db3000, sync_index = 3) [10917.969400] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_assign_add(sc = 0xffff895551db3000, sync_index = 3, pdo_index = 0x1A01) [10917.969403] EtherCAT DEBUG 0 0:5: Loading default mapping for PDO 0x1A01.
>> [10917.969408] EtherCAT DEBUG 0 0:5: Entry 0x6000:01.
>> [10917.969411] EtherCAT DEBUG 0 0:5: Entry 0x6000:02.
>> [10917.969413] EtherCAT DEBUG 0 0:5: Entry 0x6000:03.
>> [10917.969416] EtherCAT DEBUG 0 0:5: Entry 0x6000:06.
>> [10917.969418] EtherCAT DEBUG 0 0:5: Entry 0x6000:07.
>> [10917.969421] EtherCAT DEBUG 0 0:5: Entry 0x6000:09.
>> [10917.969423] EtherCAT DEBUG 0 0:5: Entry 0x6000:0A.
>> [10917.969426] EtherCAT DEBUG 0 0:5: Entry 0x6000:0B.
>> [10917.969429] EtherCAT DEBUG 0 0:5: Entry 0x6000:0C.
>> [10917.969431] EtherCAT DEBUG 0 0:5: Entry 0x6000:0D.
>> [10917.969434] EtherCAT DEBUG 0 0:5: Entry 0x6000:0E.
>> [10917.969436] EtherCAT DEBUG 0 0:5: Entry 0x6000:0F.
>> [10917.969439] EtherCAT DEBUG 0 0:5: Entry 0x6000:10.
>> [10917.969442] EtherCAT DEBUG 0 0:5: Entry 0x6000:11.
>> [10917.969444] EtherCAT DEBUG 0 0:5: Entry 0x6000:12.
>> [10917.969449] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_clear(sc = 0xffff895551db3000, pdo_index
>> = 0x1A01) [10917.969457] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1A01, entry_index = 0x6000, entry_subindex = 0x01, entry_bit_length
>> = 1) [10917.969463] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1A01, entry_index = 0x6000, entry_subindex = 0x02, entry_bit_length
>> = 1) [10917.969469] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1A01, entry_index = 0x6000, entry_subindex = 0x03, entry_bit_length
>> = 1) [10917.969475] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1A01, entry_index = 0x6000, entry_subindex = 0x06, entry_bit_length
>> = 1) [10917.969481] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index =
>> 0x1A01, entry_index = 0x6000, entry_subindex = 0x07, entry_bit_length
>> = 1) [10917.969487] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x09, entry_bit_length = 1) [10917.969493] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0A, entry_bit_length = 1) [10917.969499] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0B, entry_bit_length = 1) [10917.969505] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0C, entry_bit_length = 1) [10917.969511] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0D, entry_bit_length = 1) [10917.969517] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0E, entry_bit_length = 1) [10917.969523] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0F, entry_bit_length = 1) [10917.969529] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x10, entry_bit_length = 1) [10917.969535] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x11, entry_bit_length = 2) [10917.969541] EtherCAT DEBUG 0 0:5: ecrt_slave_config_pdo_mapping_add(sc = 0xffff895551db3000, pdo_index = 0x1A01, entry_index = 0x6000, entry_subindex = 0x12, entry_bit_length = 2) [10917.969550] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969558] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x7000, subindex = 0x01, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969562] EtherCAT DEBUG 0: Domain 0: Added 3 bytes at 0.
>> [10917.969567] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>> product_code = 0x13ed3052) [10917.969573] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x7000, subindex = 0x02, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969579] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052)
>> [10917.969585] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x7000, subindex = 0x03, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969590] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969597] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x7000, subindex = 0x04, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969602] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969609] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x7000, subindex = 0x11, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969614] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969620] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x01, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969623] EtherCAT DEBUG 0: Domain 0: Added 3 bytes at 3.
>> [10917.969629] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>> product_code = 0x13ed3052) [10917.969635] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x6000, subindex = 0x02, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969640] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052)
>> [10917.969646] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x6000, subindex = 0x03, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969651] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052)
>> [10917.969658] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x6000, subindex = 0x06, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969663] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052)
>> [10917.969669] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x6000, subindex = 0x07, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969675] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052)
>> [10917.969681] EtherCAT DEBUG 0 0:5:
>> ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index =
>> 0x6000, subindex = 0x09, domain = 0xffff895556dde3c0, bit_position =
>> 0xffffa33a0574bd64) [10917.969686] EtherCAT DEBUG 0:
>> ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0,
>> position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969693] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0A, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969698] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969704] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0B, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969711] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969718] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0C, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969723] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969729] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0D, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969735] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969741] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0E, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969747] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969753] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x0F, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969758] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969765] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x10, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969770] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969776] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x11, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969781] EtherCAT DEBUG 0: ecrt_master_slave_config(master = 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002, product_code = 0x13ed3052) [10917.969788] EtherCAT DEBUG 0 0:5: ecrt_slave_config_reg_pdo_entry(sc = 0xffff895551db3000, index = 0x6000, subindex = 0x12, domain = 0xffff895556dde3c0, bit_position = 0xffffa33a0574bd64) [10917.969826] EtherCAT DEBUG 0: ecrt_domain_external_memory(domain = 0xffff895556dde3c0, mem = 0xffffa33a01ba1000) [10917.969830] EtherCAT DEBUG 0: ecrt_master_callbacks(master = 0xffff895554eb6000, send_cb = 0xffffffffc09feff0, receive_cb = 0xffffffffc09ffc60, cb_data = 0xffff895554eb6000) [10917.969833] EtherCAT DEBUG 0: ecrt_master_activate(master = 0xffff895554eb6000) [10917.969837] EtherCAT DEBUG 0: Adding datagram pair with expected WC 3.
>> [10917.969840] EtherCAT 0: Domain0: Logical address 0x00000000, 6 byte, expected working counter 3.
>> [10917.969844] EtherCAT 0:   Datagram domain0-0-main: Logical offset 0x00000000, 6 byte, type LRW at ffff895556dded98.
>> [10917.969846] EtherCAT DEBUG 0: Stopping master thread.
>> [10917.969866] EtherCAT DEBUG 0: Master IDLE thread exiting...
>> [10917.969930] EtherCAT 0: Master thread exited.
>> [10917.969936] EtherCAT 0: Stopping EoE thread.
>> [10917.969988] EtherCAT DEBUG 0: EoE thread exiting...
>> [10917.970056] EtherCAT 0: EoE thread exited.
>> [10917.970059] EtherCAT DEBUG 0: FSM datagram is ffff895554eb6350.
>> [10917.970061] EtherCAT 0: Starting EoE thread.
>> [10917.970258] EtherCAT 0: Starting EtherCAT-OP thread.
>> [10917.970268] EtherCAT DEBUG 0: EoE thread running.
>> [10917.970451] EtherCAT DEBUG 0: Operation thread running with fsm
>> interval = 4000 us, max data size=45000 [10917.970454] EtherCAT DEBUG
>> 0: mmap() [10917.970458] EtherCAT WARNING 0: 1 datagram UNMATCHED!
>> [10917.970467] EtherCAT DEBUG 0: Vma fault, virtual_address =
>> 00007fffec02a000, offset = 0, page = fffffd0e8eb07c40 [10917.978870] EtherCAT DEBUG 0: Configuration changed (aborting state check).
>> [10917.978871] EtherCAT DEBUG 0-main-0: Checking system time offset.
>> [10917.986899] EtherCAT WARNING 0: No app_time received up to now, abort DC time offset calculation.
>> [10917.986900] EtherCAT DEBUG 0: Requesting OP...
>> [10917.986904] EtherCAT DEBUG 0-main-5: Changing state from PREOP to OP.
>> [10917.986905] EtherCAT DEBUG 0-main-5: Configuring...
>> [10918.006913] EtherCAT DEBUG 0-main-5: Now in INIT.
>> [10918.006914] EtherCAT DEBUG 0-main-5: Clearing FMMU configurations...
>> [10918.006915] EtherCAT DEBUG 0-main-5: Clearing mailbox check flag...
>> [10918.014910] EtherCAT DEBUG 0-main-5: Clearing sync manager configurations...
>> [10918.027012] EtherCAT DEBUG 0-main-5: Clearing DC assignment...
>> [10918.034985] EtherCAT DEBUG 0-main-5: Configuring mailbox sync managers...
>> [10918.034986] EtherCAT DEBUG 0-main-5: SM0: Addr 0x1000, Size 128,
>> Ctrl 0x26, En 1 [10918.034987] EtherCAT DEBUG 0-main-5: SM1: Addr
>> 0x1080, Size 128, Ctrl 0x22, En 1 [10918.042915] EtherCAT DEBUG 0-main-5: Assigning SII access to PDI.
>> [10918.058916] EtherCAT 0: Slave states on main device: INIT, PREOP.
>> [10918.070949] EtherCAT DEBUG 0-main-5: Now in PREOP.
>> [10918.070951] EtherCAT DEBUG 0-main-5: Assigning SII access back to EtherCAT.
>> [10918.078925] EtherCAT DEBUG 0-main-5: Setting PDO assignment of SM2:
>> [10918.078926] EtherCAT DEBUG 0-main-5: Currently assigned PDOs:
>> 0x1601. PDOs to assign: 0x1601 [10918.078930] EtherCAT DEBUG 0-main-5: Setting number of assigned PDOs to zero.
>> [10918.078932] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:00.
>> [10918.078932] EtherCAT DEBUG: 00
>> [10918.078935] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.078935] EtherCAT DEBUG: 00 20 2F 12 1C 00 00 00 00 00
>> [10918.102953] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.102953] EtherCAT DEBUG: 00 30 60 12 1C 00 00 00 00 00
>> [10918.102961] EtherCAT DEBUG 0-main-5: Assigning PDO 0x1601 at position 1.
>> [10918.102963] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:01.
>> [10918.102963] EtherCAT DEBUG: 01 16
>> [10918.102965] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.102966] EtherCAT DEBUG: 00 20 2B 12 1C 01 01 16 00 00
>> [10918.122875] EtherCAT 0: Slave states on main device: PREOP.
>> [10918.126963] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.126964] EtherCAT DEBUG: 00 30 60 12 1C 01 01 16 00 00
>> [10918.126973] EtherCAT DEBUG 0-main-5: Setting number of assigned PDOs to 1.
>> [10918.126975] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:00.
>> [10918.126979] EtherCAT DEBUG: 01
>> [10918.126986] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.126986] EtherCAT DEBUG: 00 20 2F 12 1C 00 01 00 00 00
>> [10918.154920] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.154921] EtherCAT DEBUG: 00 30 60 12 1C 00 01 00 00 00
>> [10918.154930] EtherCAT DEBUG 0-main-5: Successfully configured PDO assignment of SM2.
>> [10918.154939] EtherCAT DEBUG 0-main-5: Setting PDO assignment of SM3:
>> [10918.154939] EtherCAT DEBUG 0-main-5: Currently assigned PDOs:
>> 0x1A01. PDOs to assign: 0x1A01 [10918.154942] EtherCAT DEBUG 0-main-5: Setting number of assigned PDOs to zero.
>> [10918.154944] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:00.
>> [10918.154944] EtherCAT DEBUG: 00
>> [10918.154946] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.154947] EtherCAT DEBUG: 00 20 2F 13 1C 00 00 00 00 00
>> [10918.178920] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.178921] EtherCAT DEBUG: 00 30 60 13 1C 00 00 00 00 00
>> [10918.178931] EtherCAT DEBUG 0-main-5: Assigning PDO 0x1A01 at position 1.
>> [10918.178932] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:01.
>> [10918.178933] EtherCAT DEBUG: 01 1A
>> [10918.178935] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.178936] EtherCAT DEBUG: 00 20 2B 13 1C 01 01 1A 00 00
>> [10918.202933] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.202934] EtherCAT DEBUG: 00 30 60 13 1C 01 01 1A 00 00
>> [10918.202941] EtherCAT DEBUG 0-main-5: Setting number of assigned PDOs to 1.
>> [10918.202942] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:00.
>> [10918.202943] EtherCAT DEBUG: 01
>> [10918.202945] EtherCAT DEBUG 0-main-5: Expedited download request:
>> [10918.202945] EtherCAT DEBUG: 00 20 2F 13 1C 00 01 00 00 00
>> [10918.226914] EtherCAT DEBUG 0-main-5: Download response:
>> [10918.226915] EtherCAT DEBUG: 00 30 60 13 1C 00 01 00 00 00
>> [10918.226925] EtherCAT DEBUG 0-main-5: Successfully configured PDO assignment of SM3.
>> [10918.226930] EtherCAT DEBUG 0-main-5: SM2: Addr 0x1100, Size   3, Ctrl 0x64, En 1
>> [10918.226933] EtherCAT DEBUG 0-main-5: SM3: Addr 0x1180, Size   3, Ctrl 0x60, En 1
>> [10918.238918] EtherCAT DEBUG 0 0:5: FMMU: LogOff 0x00000000, Size   3, PhysAddr 0x1100, SM2, Dir out
>> [10918.238921] EtherCAT DEBUG 0 0:5: FMMU: LogOff 0x00000003, Size   3, PhysAddr 0x1180, SM3, Dir in
>> [10918.266966] EtherCAT ERROR 0-main-5: Failed to set SAFEOP state, slave refused state change (PREOP + ERROR).
>> [10918.274957] EtherCAT ERROR 0-main-5: AL status message 0x001E: "Invalid input configuration".
>> [10918.294969] EtherCAT DEBUG 0-main-5: PREOP + ERROR -> PREOP.
>> [10918.294972] EtherCAT 0-main-5: Acknowledged state PREOP.
>>
>> Regards
>>
>> Vincent BUSSIERES
>> Responsable Technique Logiciel
>>
>>
>> ZE Ma Campagne
>> 36, Impasse Félix Nadar
>> 16000 ANGOULEME
>> Tel: 33 (0)9.72.40.35.08
>> www.hemeria-group.com<http://www.hemeria-group.com>
>> • Afin de contribuer au respect de l'environnement, merci de n'imprimer ce courriel qu'en cas de nécessité.
>> Ce message et les fichiers pouvant être attachés sont confidentiels, réservés à l'usage unique des destinataires et n'engagent HEMERIA sous aucune forme que ce soit.
>> This email and any files transmitted with it are confidential, intented solely for the unique use of the recipients and don't commit HEMERIA.
>>
>>
>>
>>
>> -----Message d'origine-----
>> De : Richard Hacker <ha at igh.de<mailto:ha at igh.de>>
>> Envoyé : jeudi 14 mai 2020 16:27
>> À : BUSSIERES Vincent <vincent.bussieres at hemeria-group.com<mailto:vincent.bussieres at hemeria-group.com>>;
>> etherlab-users at etherlab.org<mailto:etherlab-users at etherlab.org> Objet : Re: [etherlab-users] Beckhoff
>> encoder interface EL5101-0010 mapping issue
>>
>> Did you map the inputs (RxPDO)? I remember that you must map them as well, even though you might not need them!
>>
>> Am 14/05/2020 um 16.17 schrieb BUSSIERES Vincent:
>>> Dear Etherlab users,
>>>
>>> I have got problems with Beckhoff encoder interface EL5101-0010 PDO mapping.
>>>
>>> I try to map only TxPDO 0x1a01 (SM3), I haven’t got any errors in
>>> init, everything seems to be fine.
>>>
>>> I read encoder value in a loop with 1ms period, return value is always 0.
>>>
>>> In dmesg, slave doesn’t reach OP state,  and stay in PREOP state.
>>>
>>> In Ethercat xml description file, some entries have got 0x0 as index
>>> value, and subindex are not completed (strange). I don’t know if I
>>> need to take them into account.
>>>
>>> <Entry>
>>>
>>> <Index>#x0</Index>
>>>
>>>                   <BitLen>2</BitLen>
>>>
>>>                   <Name>Status__</Name>
>>>
>>> </Entry>
>>>
>>> You can see below dmesg :
>>>
>>> [ 7033.920685] EtherCAT: Requesting master 0...
>>>
>>> [ 7033.920686] EtherCAT DEBUG 0: IDLE -> OPERATION.
>>>
>>> [ 7033.920687] EtherCAT: Successfully requested master 0.
>>>
>>> [ 7034.872900] EtherCAT DEBUG 0: ecrt_master_create_domain(master =
>>> 0xffff895554eb6000)
>>>
>>> [ 7034.872901] EtherCAT DEBUG 0: Created domain 0.
>>>
>>> [ 7035.835219] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7035.835220] EtherCAT DEBUG 0: Creating slave configuration for
>>> 0:5, 0x00000002/0x13ED3052.
>>>
>>> [ 7035.835222] EtherCAT DEBUG 0 0:5: Attached slave main-5.
>>>
>>> [ 7036.592742] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_sync_manager(sc = 0xffff895552309000, sync_index =
>>> 3, dir = 2, watchdog_mode = 1)
>>>
>>> [ 7036.592745] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_assign_clear(sc = 0xffff895552309000,
>>> sync_index = 3)
>>>
>>> [ 7036.592749] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_assign_add(sc
>>> = 0xffff895552309000, sync_index = 3, pdo_index = 0x1A01)
>>>
>>> [ 7036.592750] EtherCAT DEBUG 0 0:5: Loading default mapping for PDO 0x1A01.
>>>
>>> [ 7036.592753] EtherCAT DEBUG 0 0:5: Entry 0x6000:01.
>>>
>>> [ 7036.592754] EtherCAT DEBUG 0 0:5: Entry 0x6000:02.
>>>
>>> [ 7036.592754] EtherCAT DEBUG 0 0:5: Entry 0x6000:03.
>>>
>>> [ 7036.592755] EtherCAT DEBUG 0 0:5: Entry 0x6000:06.
>>>
>>> [ 7036.592756] EtherCAT DEBUG 0 0:5: Entry 0x6000:07.
>>>
>>> [ 7036.592756] EtherCAT DEBUG 0 0:5: Entry 0x6000:09.
>>>
>>> [ 7036.592757] EtherCAT DEBUG 0 0:5: Entry 0x6000:0A.
>>>
>>> [ 7036.592758] EtherCAT DEBUG 0 0:5: Entry 0x6000:0B.
>>>
>>> [ 7036.592758] EtherCAT DEBUG 0 0:5: Entry 0x6000:0C.
>>>
>>> [ 7036.592759] EtherCAT DEBUG 0 0:5: Entry 0x6000:0D.
>>>
>>> [ 7036.592759] EtherCAT DEBUG 0 0:5: Entry 0x6000:0E.
>>>
>>> [ 7036.592760] EtherCAT DEBUG 0 0:5: Entry 0x6000:0F.
>>>
>>> [ 7036.592761] EtherCAT DEBUG 0 0:5: Entry 0x6000:10.
>>>
>>> [ 7036.592761] EtherCAT DEBUG 0 0:5: Entry 0x6000:11.
>>>
>>> [ 7036.592762] EtherCAT DEBUG 0 0:5: Entry 0x6000:12.
>>>
>>> [ 7036.592764] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_clear(sc = 0xffff895552309000,
>>> pdo_index =
>>> 0x1A01)
>>>
>>> [ 7036.592767] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x01,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592769] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x02,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592770] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x03,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592772] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x06,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592773] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x07,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592775] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x09,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592776] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0A,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592778] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0B,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592779] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0C,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592781] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0D,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592783] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0E,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592784] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x0F,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592786] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x10,
>>> entry_bit_length = 1)
>>>
>>> [ 7036.592788] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x11,
>>> entry_bit_length = 2)
>>>
>>> [ 7036.592789] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_pdo_mapping_add(sc = 0xffff895552309000, pdo_index
>>> = 0x1A01, entry_index = 0x6000, entry_subindex = 0x12,
>>> entry_bit_length = 2)
>>>
>>> [ 7037.153188] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153191] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x01, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153193] EtherCAT DEBUG 0: Domain 0: Added 3 bytes at 0.
>>>
>>> [ 7037.153194] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153195] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x02, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153196] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153198] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x03, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153199] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153200] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x06, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153201] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153202] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x07, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153203] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153205] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x09, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153206] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153207] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0A, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153208] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153209] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0B, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153211] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153212] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0C, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153213] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153214] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0D, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153215] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153216] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0E, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153218] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153219] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x0F, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153220] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153221] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x10, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153222] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153223] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x11, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.153224] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
>>> 0xffff895554eb6000, alias = 0, position = 5, vendor_id = 0x00000002,
>>> product_code = 0x13ed3052)
>>>
>>> [ 7037.153225] EtherCAT DEBUG 0 0:5:
>>> ecrt_slave_config_reg_pdo_entry(sc
>>> = 0xffff895552309000, index = 0x6000, subindex = 0x12, domain =
>>> 0xffff89555461e3c0, bit_position = 0xffffa33a0525bd64)
>>>
>>> [ 7037.720938] EtherCAT DEBUG 0: ecrt_domain_external_memory(domain =
>>> 0xffff89555461e3c0, mem = 0xffffa33a01b69000)
>>>
>>> [ 7037.720940] EtherCAT DEBUG 0: ecrt_master_callbacks(master =
>>> 0xffff895554eb6000, send_cb = 0xffffffffc09feff0, receive_cb =
>>> 0xffffffffc09ffc60, cb_data = 0xffff895554eb6000)
>>>
>>> [ 7037.720940] EtherCAT DEBUG 0: ecrt_master_activate(master =
>>> 0xffff895554eb6000)
>>>
>>> [ 7037.720941] EtherCAT DEBUG 0: Adding datagram pair with expected WC 1.
>>>
>>> [ 7037.720942] EtherCAT 0: Domain0: Logical address 0x00000000, 3
>>> byte, expected working counter 1.
>>>
>>> [ 7037.720943] EtherCAT 0:   Datagram domain0-0-main: Logical offset
>>> 0x00000000, 3 byte, type LRD at ffff89555461ef18.
>>>
>>> [ 7037.720943] EtherCAT DEBUG 0: Stopping master thread.
>>>
>>> [ 7037.720974] EtherCAT DEBUG 0: Master IDLE thread exiting...
>>>
>>> [ 7037.720978] EtherCAT 0: Master thread exited.
>>>
>>> [ 7037.720978] EtherCAT 0: Stopping EoE thread.
>>>
>>> [ 7037.721017] EtherCAT DEBUG 0: EoE thread exiting...
>>>
>>> [ 7037.721021] EtherCAT 0: EoE thread exited.
>>>
>>> [ 7037.721042] EtherCAT DEBUG 0: FSM datagram is ffff895554eb6350.
>>>
>>> [ 7037.721043] EtherCAT 0: Starting EoE thread.
>>>
>>> [ 7037.721152] EtherCAT 0: Starting EtherCAT-OP thread.
>>>
>>> [ 7037.721174] EtherCAT DEBUG 0: EoE thread running.
>>>
>>> [ 7037.721300] EtherCAT DEBUG 0: Operation thread running with fsm
>>> interval = 4000 us, max data size=45000
>>>
>>> [ 7037.721305] EtherCAT DEBUG 0: mmap()
>>>
>>> [ 7037.721308] EtherCAT DEBUG 0: Vma fault, virtual_address =
>>> 00007fffec02a000, offset = 0, page = fffffd0e908af680
>>>
>>> [ 7083.264568] EtherCAT DEBUG 0: Configuration changed (aborting
>>> state check).
>>>
>>> [ 7083.264570] EtherCAT DEBUG 0-main-0: Checking system time offset.
>>>
>>> [ 7118.368544] EtherCAT WARNING 0: No app_time received up to now,
>>> abort DC time offset calculation.
>>>
>>> [ 7118.368545] EtherCAT DEBUG 0: Requesting OP...
>>>
>>> [ 7118.368549] EtherCAT DEBUG 0-main-5: Changing state from PREOP to OP.
>>>
>>> [ 7118.368550] EtherCAT DEBUG 0-main-5: Configuring...
>>>
>>> [ 7118.384514] EtherCAT DEBUG 0-main-5: Now in INIT.
>>>
>>> [ 7118.384515] EtherCAT DEBUG 0-main-5: Clearing FMMU configurations...
>>>
>>> [ 7118.384515] EtherCAT DEBUG 0-main-5: Clearing mailbox check flag...
>>>
>>> [ 7118.392604] EtherCAT DEBUG 0-main-5: Clearing sync manager
>>> configurations...
>>>
>>> [ 7118.400551] EtherCAT DEBUG 0-main-5: Clearing DC assignment...
>>>
>>> [ 7118.408559] EtherCAT DEBUG 0-main-5: Configuring mailbox sync managers...
>>>
>>> [ 7118.408562] EtherCAT DEBUG 0-main-5: SM0: Addr 0x1000, Size 128,
>>> Ctrl 0x26, En 1
>>>
>>> [ 7118.408564] EtherCAT DEBUG 0-main-5: SM1: Addr 0x1080, Size 128,
>>> Ctrl 0x22, En 1
>>>
>>> [ 7118.416573] EtherCAT DEBUG 0-main-5: Assigning SII access to PDI.
>>>
>>> [ 7118.432522] EtherCAT 0: Slave states on main device: INIT, PREOP.
>>>
>>> [ 7118.444566] EtherCAT DEBUG 0-main-5: Now in PREOP.
>>>
>>> [ 7118.444567] EtherCAT DEBUG 0-main-5: Assigning SII access back to
>>> EtherCAT.
>>>
>>> [ 7118.456607] EtherCAT DEBUG 0-main-5: Setting PDO assignment of SM2:
>>>
>>> [ 7118.456608] EtherCAT DEBUG 0-main-5: Currently assigned PDOs: 0x1600.
>>> PDOs to assign: 0x1600
>>>
>>> [ 7118.456610] EtherCAT DEBUG 0-main-5: Setting number of assigned
>>> PDOs to zero.
>>>
>>> [ 7118.456611] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:00.
>>>
>>> [ 7118.456611] EtherCAT DEBUG: 00
>>>
>>> [ 7118.456612] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.456612] EtherCAT DEBUG: 00 20 2F 12 1C 00 00 00 00 00
>>>
>>> [ 7118.480613] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.480613] EtherCAT DEBUG: 00 30 60 12 1C 00 00 00 00 00
>>>
>>> [ 7118.480619] EtherCAT DEBUG 0-main-5: Assigning PDO 0x1600 at position 1.
>>>
>>> [ 7118.480620] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:01.
>>>
>>> [ 7118.480621] EtherCAT DEBUG: 00 16
>>>
>>> [ 7118.480623] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.480623] EtherCAT DEBUG: 00 20 2B 12 1C 01 00 16 00 00
>>>
>>> [ 7118.496551] EtherCAT 0: Slave states on main device: PREOP.
>>>
>>> [ 7118.504563] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.504564] EtherCAT DEBUG: 00 30 60 12 1C 01 00 16 00 00
>>>
>>> [ 7118.504572] EtherCAT DEBUG 0-main-5: Setting number of assigned
>>> PDOs to 1.
>>>
>>> [ 7118.504574] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C12:00.
>>>
>>> [ 7118.504574] EtherCAT DEBUG: 01
>>>
>>> [ 7118.504577] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.504577] EtherCAT DEBUG: 00 20 2F 12 1C 00 01 00 00 00
>>>
>>> [ 7118.528572] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.528573] EtherCAT DEBUG: 00 30 60 12 1C 00 01 00 00 00
>>>
>>> [ 7118.528586] EtherCAT DEBUG 0-main-5: Successfully configured PDO
>>> assignment of SM2.
>>>
>>> [ 7118.528596] EtherCAT DEBUG 0-main-5: Setting PDO assignment of SM3:
>>>
>>> [ 7118.528597] EtherCAT DEBUG 0-main-5: Currently assigned PDOs: 0x1A01.
>>> PDOs to assign: 0x1A01
>>>
>>> [ 7118.528602] EtherCAT DEBUG 0-main-5: Setting number of assigned
>>> PDOs to zero.
>>>
>>> [ 7118.528604] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:00.
>>>
>>> [ 7118.528605] EtherCAT DEBUG: 00
>>>
>>> [ 7118.528608] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.528608] EtherCAT DEBUG: 00 20 2F 13 1C 00 00 00 00 00
>>>
>>> [ 7118.552556] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.552557] EtherCAT DEBUG: 00 30 60 13 1C 00 00 00 00 00
>>>
>>> [ 7118.552569] EtherCAT DEBUG 0-main-5: Assigning PDO 0x1A01 at position 1.
>>>
>>> [ 7118.552571] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:01.
>>>
>>> [ 7118.552571] EtherCAT DEBUG: 01 1A
>>>
>>> [ 7118.552575] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.552575] EtherCAT DEBUG: 00 20 2B 13 1C 01 01 1A 00 00
>>>
>>> [ 7118.580562] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.580563] EtherCAT DEBUG: 00 30 60 13 1C 01 01 1A 00 00
>>>
>>> [ 7118.580573] EtherCAT DEBUG 0-main-5: Setting number of assigned
>>> PDOs to 1.
>>>
>>> [ 7118.580575] EtherCAT DEBUG 0-main-5: Downloading SDO 0x1C13:00.
>>>
>>> [ 7118.580575] EtherCAT DEBUG: 01
>>>
>>> [ 7118.580578] EtherCAT DEBUG 0-main-5: Expedited download request:
>>>
>>> [ 7118.580579] EtherCAT DEBUG: 00 20 2F 13 1C 00 01 00 00 00
>>>
>>> [ 7118.604557] EtherCAT DEBUG 0-main-5: Download response:
>>>
>>> [ 7118.604558] EtherCAT DEBUG: 00 30 60 13 1C 00 01 00 00 00
>>>
>>> [ 7118.604571] EtherCAT DEBUG 0-main-5: Successfully configured PDO
>>> assignment of SM3.
>>>
>>> [ 7118.604578] EtherCAT DEBUG 0-main-5: SM2: Addr 0x1100, Size   6,
>>> Ctrl 0x24, En 1
>>>
>>> [ 7118.604581] EtherCAT DEBUG 0-main-5: SM3: Addr 0x1180, Size   3,
>>> Ctrl 0x60, En 1
>>>
>>> [ 7118.612565] EtherCAT DEBUG 0 0:5: FMMU: LogOff 0x00000000, Size 3,
>>> PhysAddr 0x1180, SM3, Dir in
>>>
>>> [ 7118.636572] EtherCAT ERROR 0-main-5: Failed to set SAFEOP state,
>>> slave refused state change (PREOP + ERROR).
>>>
>>> [ 7118.644558] EtherCAT ERROR 0-main-5: AL status message 0x0024:
>>> "Invalid Input Mapping".
>>>
>>> [ 7118.664569] EtherCAT DEBUG 0-main-5: PREOP + ERROR -> PREOP.
>>>
>>> [ 7118.664573] EtherCAT 0-main-5: Acknowledged state PREOP.
>>>
>>> **
>>>
>>> You can see below, an extract of my source code which work correctly
>>> with other ethercat slaves
>>>
>>> static unsigned int offOutput[15];
>>>
>>> static unsigned int offBit[15];
>>>
>>> static ec_domain_state_t domain1_state = {};
>>>
>>> static ec_master_state_t master_state = {};
>>>
>>> static ec_pdo_entry_info_t slave_0_pdo_entries[] = {
>>>
>>>        /* TxPdo 0x1a01 */
>>>
>>>        {0x6000, 0x01, 1},      /* Status Latch C valid */
>>>
>>>        {0x6000, 0x02, 1},      /* Status Latch extern valid */
>>>
>>>        {0x6000, 0x03, 1},      /* Status set counter done */
>>>
>>>        {0x6000, 0x06, 1},      /* Status of input status */
>>>
>>>        {0x6000, 0x07, 1},      /* Status open circuit */
>>>
>>>        {0x6000, 0x09, 1},      /* Status of input A */
>>>
>>>        {0x6000, 0x0a, 1},      /* Status of input B */
>>>
>>>        {0x6000, 0x0b, 1},      /* Status of input C */
>>>
>>>        {0x6000, 0x0c, 1},      /* Status of input gate */
>>>
>>>        {0x6000, 0x0d, 1},      /* Status of extern latch */
>>>
>>>        {0x6000, 0x0e, 1},      /* Status sync error */
>>>
>>>        {0x6000, 0x0f, 1},      /* Status TxPDO state */
>>>
>>>        {0x6000, 0x10, 1},      /* Status TxPDO toogle */
>>>
>>>        {0x6000, 0x11, 2},      /* counter value */
>>>
>>>        {0x6000, 0x12, 2}       /* latch value */
>>>
>>> };
>>>
>>> static ec_pdo_info_t slave_0_pdos[] = {
>>>
>>>        {0x1a01, 15, &slave_0_pdo_entries[0]}
>>>
>>> };
>>>
>>> ec_sync_info_t slave_0_syncs[] = {
>>>
>>>        {3, EC_DIR_INPUT, 1, slave_0_pdos + 0, EC_WD_ENABLE},
>>>
>>>        {0xff}
>>>
>>> };
>>>
>>> const static ec_pdo_entry_reg_t domain1_regs[] = {
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x01, &offOutput[0],
>>> &offBit[0]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x02, &offOutput[1],
>>> &offBit[1]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x03, &offOutput[2],
>>> &offBit[2]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x06, &offOutput[3],
>>> &offBit[3]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x07, &offOutput[4],
>>> &offBit[4]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x09, &offOutput[5],
>>> &offBit[5]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0a, &offOutput[6],
>>> &offBit[6]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0b, &offOutput[7],
>>> &offBit[7]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0c, &offOutput[8],
>>> &offBit[8]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0d, &offOutput[9],
>>> &offBit[9]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0e, &offOutput[10],
>>> &offBit[10]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x0f, &offOutput[11],
>>> &offBit[11]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x10, &offOutput[12],
>>> &offBit[12]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x11, &offOutput[13],
>>> &offBit[13]},
>>>
>>>        {0, 5, 0x00000002, 0x13ed3052, 0x6000, 0x12, &offOutput[14],
>>> &offBit[14]},
>>>
>>>        {}
>>>
>>> };
>>>
>>> static ec_master_t *master = nullptr;
>>>
>>> static ec_domain_t *domain1 = nullptr;
>>>
>>> static uint8_t *domain1_pd = nullptr;
>>>
>>> static ec_slave_config_t *sc_el5101 = nullptr;
>>>
>>> static ec_slave_config_state_t sc_el2809_state = {};
>>>
>>> static ec_slave_info_t slaveInfo;
>>>
>>> bool Worker::init()
>>>
>>> {
>>>
>>>        master = ecrt_request_master(0);
>>>
>>>        if ( !master )
>>>
>>>            return false;
>>>
>>>        domain1 = ecrt_master_create_domain(master);
>>>
>>>        if ( !domain1 )
>>>
>>>            return false;
>>>
>>>        if ( !(sc_el5101 = ecrt_master_slave_config(master, 0, 5,
>>> 0x00000002, 0x13ed3052)) )
>>>
>>>        {
>>>
>>>            fprintf(stderr, "Failed to get slave configuration for
>>> AKD.\n");
>>>
>>>            return false;
>>>
>>>        }
>>>
>>>        if (ecrt_slave_config_pdos(sc_el5101, EC_END, slave_0_syncs))
>>>
>>>            return false;
>>>
>>>        if (ecrt_domain_reg_pdo_entry_list(domain1, domain1_regs))
>>>
>>>            return false;
>>>
>>>        if ( ecrt_master_activate( master ) )
>>>
>>>            return false;
>>>
>>>        if (!(domain1_pd = ecrt_domain_data(domain1)))
>>>
>>>            return false;
>>>
>>>        return true;
>>>
>>> }
>>>
>>> void Worker::loop()
>>>
>>> {
>>>
>>>        mMustStop = false;
>>>
>>>        while(!mMustStop)
>>>
>>>        {
>>>
>>>            QThread::usleep(1000);
>>>
>>>            if(!mIsCycleStopped)
>>>
>>>            {
>>>
>>>                // receive process data
>>>
>>>                ecrt_master_receive(master);
>>>
>>>                ecrt_domain_process(domain1);
>>>
>>>                uint16_t lCounterValue = EC_READ_U16(domain1_pd +
>>> offOutput[13]);
>>>
>>>                qDebug() << "counter value :" << lCounterValue;
>>>
>>>                ecrt_domain_queue(domain1);
>>>
>>>                ecrt_master_send(master);
>>>
>>>            }
>>>
>>>        }
>>>
>>>        ecrt_release_master(master);
>>>
>>>        master = nullptr;
>>>
>>>        emit finished();
>>>
>>> }
>>>
>>> Take care of yourself
>>>
>>> *Vincent BUSSIERES*
>>>
>>> *Responsable Technique Logiciel*
>>>
>>> **
>>>
>>> 1572337113342
>>>
>>> /ZE Ma Campagne/
>>>
>>> /36, Impasse Félix Nadar/
>>>
>>> /16000 ANGOULEME/
>>>
>>> /Tel: 33 (0)9.72.40.35.08/
>>>
>>> /www.hemeria-group.com
>>> <https://webmail.nexeya.fr/owa/redir.aspx?C=GK_BqKCZef7LtPZnqnd_LGYr1
>>> N
>>> G9sz4Smy3iKIwO-pXqtJC7VgzXCA..&URL=http%3a%2f%2fwww.hemeria-group.com
>>> %
>>> 2f>/ PAfin de contribuer au respect de l'environnement, merci de
>>> n'imprimer ce courriel qu'en cas de nécessité.
>>>
>>> Ce message et les fichiers pouvant être attachés sont confidentiels,
>>> réservés à l'usage unique des destinataires et n'engagent HEMERIA
>>> sous aucune forme que ce soit.
>>> This email and any files transmitted with it are confidential,
>>> intented solely for the unique use of the recipients and don't commit HEMERIA.
>>>
>>> **
>>>
>>> **
>>>
>>>
>>> _______________________________________________
>>> etherlab-users mailing list
>>> etherlab-users at etherlab.org
>>> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>>>
_______________________________________________
etherlab-users mailing list
etherlab-users at etherlab.org
http://lists.etherlab.org/mailman/listinfo/etherlab-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20200515/1d0ffda1/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 5034 bytes
Desc: image003.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20200515/1d0ffda1/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 137990 bytes
Desc: image004.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20200515/1d0ffda1/attachment-0009.png>


More information about the Etherlab-users mailing list