Dear Gavin,
thank you for the help. The Sync1 specification was completely obscure to
me. If it is something "general" (not slave specific) I think it should be
better described in the documentation.
Regarding my example, with EL3702 I think I'm starting to approach a
working solution: the slave is OP and oversampled data appears every cycle.
What I still don't completely understand is why if I run in the terminal
the command "ethercat master -v" I see that the DC reference time does not
increment.
To better understand this, I've tried to check the return values in my code
after calling "ecrt_master_sync_reference_clock_to()" or
"ecrt_master_sync_reference_clock()" (used exclusively one or the other)
and they both are 0.
Then, I tried to read the reference clock using the provided function
"ecrt_master_reference_clock_time()" and, in this case, I get the return -5
(-EIO) and the print message "Failed to get reference clock time:
Input/output error"
In another console, if I check the DC residual error by continuously watch
"ethercat reg_read -p1 -tsm32 0x92c", I see that the number starts big and
gradually reduces to ~<100.
This information seems to contradict each other: on the one end the
application seems to work, and the time error is minimal, on the other it
seems that the reference clock is not properly set...
I don't know who to trust :-)
Have you any idea why ecrt_master_reference_clock_time() could fail? Is it
an error in the slave configuration or in the master?
Thanks again, and best regards
Davide
On Sun, Feb 16, 2025 at 11:36 PM Gavin Lambert <gavin.lambert at tomra.com>
wrote:
>
> The EK1100 is DC-capable (it has a DC clock and can be assigned as
reference clock) but does not actually use DC-application functionality, so
you don’t call ecrt_slave_config_dc on it (thus it doesn’t need an
AssignActivate word).
>
>
>
> Note that if you have Sync0 = 1000000 and Sync1 = 1000000 then you are
not 1x sampling, you are 2x sampling (Sync0 pulses at 1000000ns and Sync1
pulses at 2000000ns, so your application cycle interval should be
2000000ns). Sync1 is an offset; it works differently than Sync0. Blame
Beckhoff.
>
>
>
> If you actually want 1x sampling at an application cycle rate of
1000000ns then you need to specify Sync0 = 1000000 and Sync1 = 0. For 4x
sampling at 1000000ns then Sync0 = 250000 and Sync1 = 750000. You may also
need a non-zero Sync0 shift value; for that you’ll need to check the
documentation of your slave.
>
>
>
> Gavin Lambert
>
> Software Engineer
>
>
>
>
>
> TOMRA Food (ANZ) Limited | 4 Henderson Place | PO Box 13 516 | Onehunga
1061 | New Zealand
>
> Phone: +64 96 34 00 88 | https://www.tomra.com/food
> The information contained in this communication and any attachment is
confidential and may be legally privileged. It should only be read by the
person(s) to whom it is addressed. If you have received this communication
in error, please notify the sender and delete the communication.
>
> From: dabbede at gmail.com <dabbede at gmail.com>
> Sent: Saturday, 15 February 2025 12:29 am
> To: Gavin Lambert <gavin.lambert at tomra.com>
> Cc: etherlab-users at etherlab.org
> Subject: Re: [Etherlab-users] DC and oversampling with EL2262
>
>
>
> Dear Gavin,
>
> thank you for your insight and sorry if I didn't reply earlier... your
message has been classified as spam and I missed it...
>
>
>
> Yes, I know that usually the reference clock is assigned to the first
DC-capable slave: in my simple setupthis slave is the bus coupler EK1100,
but other EtherCAT masters refuse to assign the reference to a coupler, and
generally use the first "normal" slave. This is the case for TwinCAT and
Koenig Pa., for example. Moreover, I don't have an "AssignActivate" word
for EK1100... Anyway, I've tried both with and without the specification of
"ecrt_master_select_reference_clock" and the result does not change: the
reference clock is always Slave 0, and the DC reference time does not
advance.
>
>
>
> Since I was having issues on sending EL2262 to "OP", later I've tried to
use a different slave with similar characteristics (DC capable and
oversampling), which is EL3702. With that, I could go "OP" without problem,
but all the other issues related to the reference clock staying assigned to
Slave 0 (despite ecrt_master_select_reference_clock ) and DC reference time
which does not advance remained the same.
>
>
>
> Of course I strictly followed the example dc_user (that was my starting
point), and in fact my cyclic task has this form:
> clock_gettime(CLOCK_TO_USE, &time);
> ecrt_master_sync_reference_clock_to(master, TIMESPEC2NS(time));
> ecrt_master_sync_slave_clocks(master);
>
>
>
> I don't know if I'm allowed to attach files to this mailing list. I'm
going to try with a minimal example and, if it does not work, I'll copy in
the next message the content of the file.
>
> I don't know if anyone of you owns a EL3702 to try replicate the error,
but this is what I can see with the attached minimal example:
>
> - the file compiles properly, and does run "as expected" without printing
any "if-exception"
>
> - the output is
>
> Activating master...
> Using priority 97.
> Starting cyclic function.
> 2 slave(s).
> AL states: 0x02.
> Link is up.
> AL states: 0x08.
> Domain1: WC 1.
> Domain1: State 2.
>
>
>
>
>
> - the command ethercat config -v gives
>
> Alias: 0
> Position: 0
> Vendor Id: 0x00000002
> Product code: 0x044c2c52
> Attached slave: 0 (OP)
> Watchdog divider: (Default)
> Watchdog intervals: (Default)
> SDO configuration:
> None.
> IDN configuration:
> None.
> Feature flags:
> None.
>
> Alias: 0
> Position: 1
> Vendor Id: 0x00000002
> Product code: 0x0e763052
> Attached slave: 1 (OP)
> Watchdog divider: (Default)
> Watchdog intervals: (Default)
> SM0, Dir: Input, Watchdog: Default
> PDO 0x1b00
> PDO entry 0x6800:01, 16 bit
> PDO 0x1a00
> PDO entry 0x6000:01, 16 bit
> SM1, Dir: Input, Watchdog: Default
> PDO 0x1b01
> PDO entry 0x6800:02, 16 bit
> PDO 0x1a80
> PDO entry 0x6000:02, 16 bit
> SM2, Dir: Input, Watchdog: Default
> PDO 0x1b10
> PDO entry 0x1d09:98, 32 bit
> SDO configuration:
> None.
> IDN configuration:
> None.
> Feature flags:
> None.
> DC configuration:
> AssignActivate: 0x0730
> Cycle [ns] Shift [ns]
> SYNC0 1000000 0
> SYNC1 1000000 0
>
>
>
>
>
> - the command ethercat master -v gives
>
> Master0
> Phase: Operation
> Active: yes
> Slaves: 2
> Ethernet devices:
> Main: 00:12:cd:07:a3:4a (attached)
> Link: UP
> Tx frames: 2102849
> Tx bytes: 139702270
> Rx frames: 2102848
> Rx bytes: 139702206
> Tx errors: 0
> Tx frame rate [1/s]: 1000 1000 995
> Tx rate [KByte/s]: 64.2 64.2 63.9
> Rx frame rate [1/s]: 1000 1000 995
> Rx rate [KByte/s]: 64.2 64.2 63.9
> Common:
> Tx frames: 2102849
> Tx bytes: 139702270
> Rx frames: 2102848
> Rx bytes: 139702206
> Lost frames: 0
> Tx frame rate [1/s]: 1000 1000 995
> Tx rate [KByte/s]: 64.2 64.2 63.9
> Rx frame rate [1/s]: 1000 1000 995
> Rx rate [KByte/s]: 64.2 64.2 63.9
> Loss rate [1/s]: 0 0 0
> Frame loss [%]: 0.0 0.0 0.0
> Distributed clocks:
> Reference clock: Slave 0
> DC reference time: 6591555116393
> Application time: 6842454116393
> 2000-01-01 01:54:02.454116393
>
>
>
> Notice that DC reference time and application time are different and
that, while the latter updates at each call, the first does not.
>
>
>
> The original code was more complicated, to account for the oversampling
also in the PDOs, but even this minimal one with oversampling = 1 still
does not work, so I don't understand if I'm missing something or if these
types of slaves are not supported...
>
>
>
> Thank you all for your patience and for any guidance.
>
>
>
> Regards,
>
>
>
> Davide
>
>
>
>
>
> On Tue, Feb 11, 2025 at 4:15 AM Gavin Lambert <gavin.lambert at tomra.com>
wrote:
>
> Typically, the reference clock should be the first DC-capable device on
the network (often an infrastructure device like a coupler, if present – as
in your case), because the DC time only flows downstream from that. It’s
unusual for it to be your DC-consuming device directly unless you don’t
have any others. Thus, it’s not usually necessary to call
ecrt_master_select_reference_clock unless you have special requirements
(such as DC synching across multiple networks).
>
>
>
> Since you’re using ecrt_master_sync_reference_clock_to and you’re saying
that the DC time doesn’t appear to be advancing, ensure that your code
actually does advance the time in your realtime loop – that’s your
responsibility when you use that method rather than the alternatives.
>
>
>
> There can be many reasons why a device refuses to transition to SAFEOP
(or does but then faults back to PREOP). You’ll need to review the syslog
to see what error codes it’s reporting, if any. (But it could just be due
to the DC time not advancing.)
>
>
>
> Try comparing your code against the existing examples such as dc_user,
and pay close attention to your slave’s documented requirements for
ecrt_slave_config_dc – in particular note that the SYNC1 time is specified
in an unusual way.
>
>
>
> Gavin Lambert
>
> Software Engineer
>
>
>
>
>
> TOMRA Food (ANZ) Limited | 4 Henderson Place | PO Box 13 516 | Onehunga
1061 | New Zealand
>
> Phone: +64 96 34 00 88 | https://www.tomra.com/food
> The information contained in this communication and any attachment is
confidential and may be legally privileged. It should only be read by the
person(s) to whom it is addressed. If you have received this communication
in error, please notify the sender and delete the communication.
>
> From: Etherlab-users <etherlab-users-bounces at etherlab.org> On Behalf Of
dabbede at gmail.com
> Sent: Monday, 10 February 2025 9:54 pm
> To: etherlab-users at etherlab.org
> Subject: [Etherlab-users] DC and oversampling with EL2262
>
>
>
> Dear Etherlab community,
>
> I have been using the EtherCAT master for a few days. I think I
understand more or less how to configure the PDOs and domains for one or
more slaves, but I'm having trouble with the distributed clock (DC).
> In particular, my setup is currently as follows:
> - master
> - Beckhoff EK1100
> - Beckhoff EL2262
>
> The latter is a digital output with oversampling capabilities. It can
output a sample every Sync0, which in turn can be set to trigger faster
than the application cycle. I used this slave successfully with other
EtherCAT masters, so I know it is working properly.
>
> In my code I've set the PDOs using "ecrt_slave_config_pdos" and assigned
them to the domain1 using "ecrt_slave_config_reg_pdo_entry".
>
> Then I've set this slave to be the reference clock using
> ecrt_master_select_reference_clock (master, sc); // Set this slave
to be reference clock
> and finally I've set the DC settings (and Sync0/1) using
"ecrt_slave_config_dc" (by the way, the AssignActivate data is 0x0730 for
this slave).
>
> Then, for every application cycle I call, in order:
> - ecrt_master_application_time
> - ecrt_master_receive
> - ecrt_domain_process
> - check_domain1_state
> - ecrt_master_sync_reference_clock_to
> - ecrt_master_sync_slave_clocks
> - ecrt_domain_queue
> - ecrt_master_send
>
> The problems I see are:
> - the outputs are constantly OFF, even if I've set an alternating pattern
of ON and OFF,
> - the slave stops at PREOP,
> - if I inspect the master from the cli using "ethercat master -v", I see
that the reference clock is set to Slave 0, instead of Slave 1. Moreover,
the DC reference time is set correctly every time I restart the
application, but it does not update during execution. Conversely, the
application time increase as expected
> - during " check_domain1_state", I see that the wc_state==EC_WC_ZERO (no
process data exchanged)
>
>
>
> I am willing to share my code if it is required.
> Thank you for your help and, especially, thank you for providing such
powerful software as open source.
>
> Best regards,
>
>
>
> Davide
>
> --
> Etherlab-users mailing list
> Etherlab-users at etherlab.org
> https://lists.etherlab.org/mailman/listinfo/etherlab-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://lists.etherlab.org/pipermail/etherlab-users/attachments/20250217/c2565207/attachment-0001.htm>
More information about the Etherlab-users
mailing list