[Etherlab-users] Timeout while setting state INIT.

Richard Hacker ha at igh.de
Thu Feb 19 16:08:12 CET 2026


That is a strange behaviour of the slave.

Have you tried to set the timeout longer:
ecrt_slave_config_state_timeout()

On Thu, 2026-02-19 at 17:27 +0300, Bilko AS, Oguz Dilmac wrote:
>  
> Hi,
>  
> I have a special slave with a strange behaviour. It's located at the
> end of the bus after a few servo motor drives.
>  
> At the startup, it doesn't go to OP mode with the rest of the slaves.
> But if I remove the power of this slave, before startup, and replug
> after everything else is in OP mode, this slave goes to OP mode too.
>  
> When I checked the dmesg output I noticed that it gives a timeout
> error for going to state INIT.
>  
> Here is the ethercat slaves -v output:
>  ethercat slaves -v
>  === Master 0, Slave 0 ===
>  Device: Main
>  State: PREOP
>  Flag: E
>  Identity:
>    Vendor Id:       0x6167656d
>    Product code:    0x00000000
>    Revision number: 0x00000000
>    Serial number:   0x00000000
>  DL information:
>    FMMU bit operation: no
>    Distributed clocks: yes, 64 bit
>    DC system time transmission delay: 0 ns
>  Port  Type  Link  Loop    Signal  NextSlave  RxTime [ns]  Diff [ns] 
>  NextDc [ns]
>     0  MII   up    open    yes             -   1795181876         
>  0           0
>     1  MII   down  closed  no              -            -           -
>            -
>     2  N/A   down  closed  no              -            -           -
>            -
>     3  N/A   down  closed  no              -            -           -
>            -
>  Mailboxes:
>    Bootstrap RX: 0x1000/1024, TX: 0x1400/1024
>    Standard  RX: 0x1000/1024, TX: 0x1400/1024
>    Supported protocols: CoE, FoE
>  General:
>    Group: SSC_Device
>    Image name: 
>    Order number: Megatec_ESC_NLCH
>    Device name: Megatec_ESC_NLCH
>    CoE details:
>      Enable SDO: yes
>      Enable SDO Info: yes
>      Enable PDO Assign: no
>      Enable PDO Configuration: no
>      Enable Upload at startup: no
>      Enable SDO complete access: yes
>    Flags:
>      Enable SafeOp: no
>      Enable notLRW: no
>    Current consumption: 0 mA 
> And this is the dmesg output with Ethercat debug 1 configuration
>  
> [  186.189225] EtherCAT: Requesting master 0...
>  [  186.189232] EtherCAT DEBUG 0: IDLE -> OPERATION.
>  [  186.189234] EtherCAT: Successfully requested master 0.
>  [  186.189236] EtherCAT DEBUG 0: ecrt_master_create_domain(master =
> 0x0000000086b530b0)
>  [  186.189240] EtherCAT DEBUG 0: Created domain 0.
>  [  186.189243] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
> 0x0000000086b530b0, alias = 0, position = 0, vendor_id = 0x6167656d,
> product_code = 0x00000000)
>  [  186.189246] EtherCAT DEBUG 0: Creating slave configuration for
> 0:0, 0x6167656D/0x00000000.
>  [  186.189250] EtherCAT DEBUG 0 0:0: Attached slave 0.
>  [  186.189300] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_sync_manager(sc = 0x0000000071c188e2, sync_index =
> 0, dir = 1, watchdog_mode = 2)
>  [  186.189305] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_clear(sc = 0x0000000071c188e2,
> sync_index = 0)
>  [  186.189308] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_sync_manager(sc = 0x0000000071c188e2, sync_index =
> 1, dir = 2, watchdog_mode = 2)
>  [  186.189311] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_clear(sc = 0x0000000071c188e2,
> sync_index = 1)
>  [  186.189314] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_sync_manager(sc = 0x0000000071c188e2, sync_index =
> 2, dir = 1, watchdog_mode = 1)
>  [  186.189316] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_clear(sc = 0x0000000071c188e2,
> sync_index = 2)
>  [  186.189322] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_add(sc = 0x0000000071c188e2, sync_index
> = 2, pdo_index = 0x1600)
>  [  186.189325] EtherCAT DEBUG 0 0:0: Loading default mapping for PDO
> 0x1600.
>  
>  [  186.189331] EtherCAT DEBUG 0 0:0: Entry 0x7000:01.
>  [  186.189333] EtherCAT DEBUG 0 0:0: Entry 0x7000:02.
>  [  186.189334] EtherCAT DEBUG 0 0:0: Entry 0x7000:03.
>  [  186.189336] EtherCAT DEBUG 0 0:0: Entry 0x7000:04.
>  [  186.189337] EtherCAT DEBUG 0 0:0: Entry 0x7000:05.
>  [  186.189338] EtherCAT DEBUG 0 0:0: Entry 0x7000:06.
>  [  186.189339] EtherCAT DEBUG 0 0:0: Entry 0x7000:07.
>  [  186.189340] EtherCAT DEBUG 0 0:0: Entry 0x7000:08.
>  [  186.189341] EtherCAT DEBUG 0 0:0: Entry 0x7000:09.
>  [  186.189343] EtherCAT DEBUG 0 0:0: Entry 0x7000:0A.
>  [  186.189344] EtherCAT DEBUG 0 0:0: Entry 0x7000:0B.
>  [  186.189345] EtherCAT DEBUG 0 0:0: Entry 0x7000:0C.
>  [  186.189346] EtherCAT DEBUG 0 0:0: Entry 0x7000:0D.
>  [  186.189347] EtherCAT DEBUG 0 0:0: Entry 0x7000:0E.
>  [  186.189349] EtherCAT DEBUG 0 0:0: Entry 0x7000:0F.
>  [  186.189350] EtherCAT DEBUG 0 0:0: Entry 0x7000:10.
>  [  186.189351] EtherCAT DEBUG 0 0:0: Entry 0x7000:11.
>  [  186.189352] EtherCAT DEBUG 0 0:0: Entry 0x7000:12.
>  [  186.189354] EtherCAT DEBUG 0 0:0: Entry 0x7000:13.
>  [  186.189355] EtherCAT DEBUG 0 0:0: Entry 0x7000:14.
>  [  186.189356] EtherCAT DEBUG 0 0:0: Entry 0x7000:15.
>  [  186.189357] EtherCAT DEBUG 0 0:0: Entry 0x7000:16.
>  [  186.189358] EtherCAT DEBUG 0 0:0: Entry 0x7000:17.
>  [  186.189360] EtherCAT DEBUG 0 0:0: Entry 0x7000:18.
>  [  186.189361] EtherCAT DEBUG 0 0:0: Entry 0x7000:19.
>  [  186.189362] EtherCAT DEBUG 0 0:0: Entry 0x7000:1A.
>  [  186.189363] EtherCAT DEBUG 0 0:0: Entry 0x7000:1B.
>  [  186.189364] EtherCAT DEBUG 0 0:0: Entry 0x7000:1C.
>  [  186.189365] EtherCAT DEBUG 0 0:0: Entry 0x7000:1D.
>  [  186.189367] EtherCAT DEBUG 0 0:0: Entry 0x7000:1E.
>  [  186.189368] EtherCAT DEBUG 0 0:0: Entry 0x7000:1F.
>  [  186.189369] EtherCAT DEBUG 0 0:0: Entry 0x7000:20.
>  [  186.189370] EtherCAT DEBUG 0 0:0: Entry 0x7000:21.
>  [  186.189371] EtherCAT DEBUG 0 0:0: Entry 0x7000:22.
>  [  186.189372] EtherCAT DEBUG 0 0:0: Entry 0x7000:23.
>  [  186.189373] EtherCAT DEBUG 0 0:0: Entry 0x7000:24.
>  [  186.189374] EtherCAT DEBUG 0 0:0: Entry 0x7000:25.
>  [  186.189376] EtherCAT DEBUG 0 0:0: Entry 0x7000:26.
>  [  186.189377] EtherCAT DEBUG 0 0:0: Entry 0x7000:27.
>  [  186.189379] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_clear(sc = 0x0000000071c188e2,
> pdo_index = 0x1600)
>  [  186.189386] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x01,
> entry_bit_length = 16)
>  [  186.189390] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x02,
> entry_bit_length = 16)
>  [  186.189393] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x03,
> entry_bit_length = 16)
>  [  186.189396] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x04,
> entry_bit_length = 16)
>  [  186.189399] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x05,
> entry_bit_length = 16)
>  [  186.189402] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x06,
> entry_bit_length = 16)
>  [  186.189404] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x07,
> entry_bit_length = 16)
>  [  186.189407] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x08,
> entry_bit_length = 16)
>  [  186.189410] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x09,
> entry_bit_length = 16)
>  [  186.189412] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0A,
> entry_bit_length = 16)
>  [  186.189415] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0B,
> entry_bit_length = 16)
>  [  186.189418] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0C,
> entry_bit_length = 16)
>  [  186.189420] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0D,
> entry_bit_length = 16)
>  [  186.189423] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0E,
> entry_bit_length = 16)
>  [  186.189426] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x0F,
> entry_bit_length = 16)
>  [  186.189428] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x10,
> entry_bit_length = 16)
>  [  186.189431] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x11,
> entry_bit_length = 16)
>  [  186.189434] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x12,
> entry_bit_length = 16)
>  [  186.189437] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x13,
> entry_bit_length = 16)
>  [  186.189440] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x14,
> entry_bit_length = 16)
>  [  186.189442] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x15,
> entry_bit_length = 16)
>  [  186.189445] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x16,
> entry_bit_length = 16)
>  [  186.189448] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x17,
> entry_bit_length = 16)
>  [  186.189450] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x18,
> entry_bit_length = 16)
>  [  186.189453] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x19,
> entry_bit_length = 16)
>  [  186.189456] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1A,
> entry_bit_length = 16)
>  [  186.189458] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1B,
> entry_bit_length = 16)
>  [  186.189461] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1C,
> entry_bit_length = 16)
>  [  186.189464] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1D,
> entry_bit_length = 16)
>  [  186.189466] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1E,
> entry_bit_length = 16)
>  [  186.189469] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x1F,
> entry_bit_length = 16)
>  [  186.189472] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x20,
> entry_bit_length = 16)
>  [  186.189474] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x21,
> entry_bit_length = 16)
>  [  186.189477] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x22,
> entry_bit_length = 16)
>  [  186.189480] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x23,
> entry_bit_length = 16)
>  [  186.189482] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x24,
> entry_bit_length = 16)
>  [  186.189485] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x25,
> entry_bit_length = 16)
>  [  186.189488] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x26,
> entry_bit_length = 16)
>  [  186.189490] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1600, entry_index = 0x7000, entry_subindex = 0x27,
> entry_bit_length = 16)
>  [  186.189494] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_sync_manager(sc = 0x0000000071c188e2, sync_index =
> 3, dir = 2, watchdog_mode = 2)
>  [  186.189496] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_clear(sc = 0x0000000071c188e2,
> sync_index = 3)
>  [  186.189502] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_assign_add(sc = 0x0000000071c188e2, sync_index
> = 3, pdo_index = 0x1A00)
>  [  186.189504] EtherCAT DEBUG 0 0:0: Loading default mapping for PDO
> 0x1A00.
>  
>  [  186.189512] EtherCAT DEBUG 0 0:0: Entry 0x6000:01.
>  [  186.189513] EtherCAT DEBUG 0 0:0: Entry 0x6000:02.
>  [  186.189514] EtherCAT DEBUG 0 0:0: Entry 0x6000:03.
>  [  186.189515] EtherCAT DEBUG 0 0:0: Entry 0x6000:04.
>  [  186.189517] EtherCAT DEBUG 0 0:0: Entry 0x6000:05.
>  [  186.189518] EtherCAT DEBUG 0 0:0: Entry 0x6000:06.
>  [  186.189519] EtherCAT DEBUG 0 0:0: Entry 0x6000:07.
>  [  186.189520] EtherCAT DEBUG 0 0:0: Entry 0x6000:08.
>  [  186.189521] EtherCAT DEBUG 0 0:0: Entry 0x6000:09.
>  [  186.189522] EtherCAT DEBUG 0 0:0: Entry 0x6000:0A.
>  [  186.189523] EtherCAT DEBUG 0 0:0: Entry 0x6000:0B.
>  [  186.189524] EtherCAT DEBUG 0 0:0: Entry 0x6000:0C.
>  [  186.189525] EtherCAT DEBUG 0 0:0: Entry 0x6000:0D.
>  [  186.189526] EtherCAT DEBUG 0 0:0: Entry 0x6000:0E.
>  [  186.189528] EtherCAT DEBUG 0 0:0: Entry 0x6000:0F.
>  [  186.189529] EtherCAT DEBUG 0 0:0: Entry 0x6000:10.
>  [  186.189530] EtherCAT DEBUG 0 0:0: Entry 0x6000:11.
>  [  186.189531] EtherCAT DEBUG 0 0:0: Entry 0x6000:12.
>  [  186.189532] EtherCAT DEBUG 0 0:0: Entry 0x6000:13.
>  [  186.189533] EtherCAT DEBUG 0 0:0: Entry 0x6000:14.
>  [  186.189534] EtherCAT DEBUG 0 0:0: Entry 0x6000:15.
>  [  186.189535] EtherCAT DEBUG 0 0:0: Entry 0x6000:16.
>  [  186.189537] EtherCAT DEBUG 0 0:0: Entry 0x6000:17.
>  [  186.189538] EtherCAT DEBUG 0 0:0: Entry 0x6000:18.
>  [  186.189539] EtherCAT DEBUG 0 0:0: Entry 0x6000:19.
>  [  186.189540] EtherCAT DEBUG 0 0:0: Entry 0x6000:1A.
>  [  186.189541] EtherCAT DEBUG 0 0:0: Entry 0x6000:1B.
>  [  186.189542] EtherCAT DEBUG 0 0:0: Entry 0x6000:1C.
>  [  186.189543] EtherCAT DEBUG 0 0:0: Entry 0x6000:1D.
>  [  186.189544] EtherCAT DEBUG 0 0:0: Entry 0x6000:1E.
>  [  186.189546] EtherCAT DEBUG 0 0:0: Entry 0x6000:1F.
>  [  186.189547] EtherCAT DEBUG 0 0:0: Entry 0x6000:20.
>  [  186.189548] EtherCAT DEBUG 0 0:0: Entry 0x6000:21.
>  [  186.189549] EtherCAT DEBUG 0 0:0: Entry 0x6000:22.
>  [  186.189550] EtherCAT DEBUG 0 0:0: Entry 0x6000:23.
>  [  186.189551] EtherCAT DEBUG 0 0:0: Entry 0x6000:24.
>  [  186.189553] EtherCAT DEBUG 0 0:0: Entry 0x6000:25.
>  [  186.189554] EtherCAT DEBUG 0 0:0: Entry 0x6000:26.
>  [  186.189555] EtherCAT DEBUG 0 0:0: Entry 0x6000:27.
>  [  186.189557] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_clear(sc = 0x0000000071c188e2,
> pdo_index = 0x1A00)
>  [  186.189562] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x01,
> entry_bit_length = 16)
>  [  186.189565] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x02,
> entry_bit_length = 16)
>  [  186.189568] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x03,
> entry_bit_length = 16)
>  [  186.189571] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x04,
> entry_bit_length = 16)
>  [  186.189574] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x05,
> entry_bit_length = 16)
>  [  186.189577] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x06,
> entry_bit_length = 16)
>  [  186.189579] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x07,
> entry_bit_length = 16)
>  [  186.189582] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x08,
> entry_bit_length = 16)
>  [  186.189585] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x09,
> entry_bit_length = 16)
>  [  186.189588] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0A,
> entry_bit_length = 16)
>  [  186.189591] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0B,
> entry_bit_length = 16)
>  [  186.189593] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0C,
> entry_bit_length = 16)
>  [  186.189596] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0D,
> entry_bit_length = 16)
>  [  186.189599] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0E,
> entry_bit_length = 16)
>  [  186.189601] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x0F,
> entry_bit_length = 16)
>  [  186.189604] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x10,
> entry_bit_length = 16)
>  [  186.189607] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x11,
> entry_bit_length = 16)
>  [  186.189610] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x12,
> entry_bit_length = 16)
>  [  186.189612] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x13,
> entry_bit_length = 16)
>  [  186.189615] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x14,
> entry_bit_length = 16)
>  [  186.189618] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x15,
> entry_bit_length = 16)
>  [  186.189621] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x16,
> entry_bit_length = 16)
>  [  186.189624] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x17,
> entry_bit_length = 16)
>  [  186.189626] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x18,
> entry_bit_length = 16)
>  [  186.189629] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x19,
> entry_bit_length = 16)
>  [  186.189632] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1A,
> entry_bit_length = 16)
>  [  186.189635] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1B,
> entry_bit_length = 16)
>  [  186.189637] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1C,
> entry_bit_length = 16)
>  [  186.189640] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1D,
> entry_bit_length = 16)
>  [  186.189643] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1E,
> entry_bit_length = 16)
>  [  186.189646] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x1F,
> entry_bit_length = 16)
>  [  186.189649] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x20,
> entry_bit_length = 16)
>  [  186.189651] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x21,
> entry_bit_length = 16)
>  [  186.189654] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x22,
> entry_bit_length = 16)
>  [  186.189656] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x23,
> entry_bit_length = 16)
>  [  186.189659] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x24,
> entry_bit_length = 16)
>  [  186.189662] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x25,
> entry_bit_length = 16)
>  [  186.189664] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x26,
> entry_bit_length = 16)
>  [  186.189667] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_pdo_mapping_add(sc = 0x0000000071c188e2, pdo_index
> = 0x1A00, entry_index = 0x6000, entry_subindex = 0x27,
> entry_bit_length = 16)
>  [  186.189671] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
> 0x0000000086b530b0, alias = 0, position = 0, vendor_id = 0x6167656d,
> product_code = 0x00000000)
>  [  186.189676] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_reg_pdo_entry(sc = 0x0000000071c188e2, index =
> 0x7000, subindex = 0x01, domain = 0x00000000b451bb74, bit_position =
> 0x000000002facf3e1)
>  [  186.189680] EtherCAT DEBUG 0: Domain 0: Added 78 bytes, total 78.
>  [  186.189683] EtherCAT DEBUG 0: ecrt_master_slave_config(master =
> 0x0000000086b530b0, alias = 0, position = 0, vendor_id = 0x6167656d,
> product_code = 0x00000000)
>  [  186.189686] EtherCAT DEBUG 0 0:0:
> ecrt_slave_config_reg_pdo_entry(sc = 0x0000000071c188e2, index =
> 0x7000, subindex = 0x05, domain = 0x00000000b451bb74, bit_position =
> 0x000000006507b978)
>  [  186.189707] EtherCAT DEBUG 0: ecrt_domain_external_memory(domain
> = 0x00000000b451bb74, mem = 0x000000006263e939)
>  [  186.189710] EtherCAT DEBUG 0: ecrt_master_callbacks(master =
> 0x0000000086b530b0, send_cb = 0x00000000a7d24716, receive_cb =
> 0x0000000062142df5, cb_data = 0x0000000086b530b0)
>  [  186.189713] EtherCAT DEBUG 0: ecrt_master_activate(master =
> 0x0000000086b530b0)
>  [  186.189716] EtherCAT DEBUG 0: Adding datagram pair with expected
> WC 1.
>  [  186.189717] EtherCAT 0: Domain0: Logical address 0x00000000, 78
> byte, expected working counter 1.
>  [  186.189720] EtherCAT 0:   Datagram domain0-0-main: Logical offset
> 0x00000000, 78 byte, type LWR.
>  [  186.189723] EtherCAT DEBUG 0: Stopping master thread.
>  [  186.189734] EtherCAT DEBUG 0: Master IDLE thread exiting...
>  [  186.189749] EtherCAT 0: Master thread exited.
>  [  186.189752] EtherCAT DEBUG 0: FSM datagram is 00000000cfd93c4c.
>  [  186.189753] EtherCAT 0: Starting EtherCAT-OP thread.
>  [  186.189947] EtherCAT DEBUG 0: Operation thread running with fsm
> interval = 4000 us, max data size=45000
>  [  186.190049] EtherCAT DEBUG 0: mmap()
>  [  186.190063] EtherCAT DEBUG 0: Vma fault, offset = 0, page =
> 00000000edcde822
>  [  186.195501] EtherCAT DEBUG 0: Configuration changed (aborting
> state check).
>  [  186.195506] EtherCAT WARNING 0: No application time received up
> to now, but master already active.
>  [  186.195508] EtherCAT DEBUG 0: Requesting OP...
>  [  186.203556] EtherCAT DEBUG 0-0: Changing state from PREOP to OP.
>  [  186.203564] EtherCAT DEBUG 0-0: Configuring...
>  [  191.215776] EtherCAT ERROR 0-0: Timeout while setting state INIT.
>  
>  
> And this a simple code part for my tests. This doesn't configures
> servo drives. Just one slave to see if it goes to OP mode
>  
>     if (!(sc_dig_out = ecrt_master_slave_config(
>                             master, BusCouplerPos, megatec))) {
>          fprintf(stderr, "Failed to get slave configuration.\n");
>          return -1;
>      }
>  
>      printf("Configuring PDOs...\n");
>      if (ecrt_slave_config_pdos(sc_dig_out, EC_END, slave_0_syncs)) {
>          fprintf(stderr, "Failed to configure PDOs.\n");
>          return -1;
>      }
>  
>      if (ecrt_domain_reg_pdo_entry_list(domain1, domain1_regs)) {
>          fprintf(stderr, "PDO entry registration failed!\n");
>          return -1;
>      }
>  
>      printf("Activating master...\n");
>      if (ecrt_master_activate(master))
>          return -1;
>  
>  
> Any ideas? Do you suggest something to try?
>  
> Best regards,
>  
> Oguz.
>  

-- 
Mit freundlichem Gruß / Best regards,
Richard Hacker
--  
-----------------------------------------------------------------------
Richard Hacker, M.Sc.
Entwicklungsingenieur / Development Engineer
ha at igh.de

Tel.: +49 201 / 36014-16

Ingenieurgemeinschaft IgH Gesellschaft für Ingenieurleistungen mbH
Nordsternstraße 66
D-45329 Essen

https://igh.de | https://etherlab.org

Amtsgericht Essen HRB 11500 | USt-Id.-Nr.: DE 174 626 722
Geschäftsführung:
Frederik Becker, Dr.-Ing. Siegfried Rotthäuser, Jost Braukmann
-----------------------------------------------------------------------


More information about the Etherlab-users mailing list