[Etherlab-users] Timeout while setting state INIT.

Bilko AS, Oguz Dilmac odilmac at bilko-automation.com
Wed Mar 18 12:31:16 CET 2026


Hi Graeme, James,

I tried the "enable-sii-override" option just in case. But I'm not sure 
if I did it correctly. Here is what I did:

* I installed the master version from Mr James Benway: 
https://github.com/DSI-Gleeble/ethercat/tree/sii-from-file. I used the 
"--enable-sii-override=/lib/firmware/ethercat" option.

* I created the ethercat folder under /lib/firmware

* I copied the binary file (ec_6167656d_00000000.bin) from twincat to 
/lib/firmware/ethercat folder.

When I checked the debug messages, I noticed that master tries to open 
the ethercat/ec_6167656d_00000000.bin but couldn't find it. This file is 
copied under /lib/firmware/ethercat.

Then I checked the config.log. It seems, the path is correct:

...

configure:19137: checking whether to assign the SII to PDI
configure:19163: result: yes
configure:19174: checking whether to load SII locally if available
configure:19210: result: yes, from /lib/firmware/ethercat

...

Why do you think the master can't find the file?

By the way, this is the dmesg output:

[   49.650743] ec_r8169 0000:02:00.0 enp2s0: Link is Down
[   51.697773] EtherCAT 0: Master debug level set to 1.
[   52.336230] ec_r8169 0000:01:00.0 ecm0 (uninitialized): Link is Up - 
100Mbps/Full - flow control rx/tx
[   53.255968] EtherCAT 0: Link state of ecm0 changed to UP.
[   53.257011] EtherCAT 0: 1 slave(s) responding on main device. 
Re-scanning on next possibility.
[   53.257014] EtherCAT 0: Slave states on main device: INIT.
[   53.257015] EtherCAT 0: Re-scanning now.
[   53.257063] EtherCAT DEBUG 0: Sending broadcast-write to measure 
transmission delays on main link.
[   53.257098] EtherCAT DEBUG 0: 1 slaves responded to delay measuring 
on main link.
[   53.257099] EtherCAT 0: Scanning bus.
[   53.257100] EtherCAT DEBUG 0: Scanning slave 0 on main link.
[   53.257233] EtherCAT DEBUG 0-0: Slave has the System Time register.
[   53.257300] EtherCAT DEBUG 0-0: Assigning SII access to EtherCAT.
[   53.296413] EtherCAT DEBUG 0-0: Trying to load SII firmware: 
ethercat/ec_6167656d_00000000_00000000.bin
[   53.296414] EtherCAT DEBUG 0-0:                        then: 
ethercat/ec_6167656d_00000000.bin
[   53.296444] EtherCAT DEBUG 0-0: request_firmware_direct: 
ethercat/ec_6167656d_00000000_00000000.bin.
[   53.301871] EtherCAT DEBUG 0-0: request_firmware_direct: 
ethercat/ec_6167656d_00000000.bin.
[   53.301886] EtherCAT DEBUG 0-0: SII firmware file not found; reading 
SII data from slave.
[   53.306417] EtherCAT DEBUG 0-0: Found category type 10 with size 401. 
Proceeding to offset 467.
[   53.311433] EtherCAT DEBUG 0-0: Found category type 30 with size 16. 
Proceeding to offset 485.
[   53.316425] EtherCAT DEBUG 0-0: Found category type 40 with size 2. 
Proceeding to offset 489.
[   53.321430] EtherCAT DEBUG 0-0: Found category type 41 with size 16. 
Proceeding to offset 507.
[   53.326411] EtherCAT DEBUG 0-0: Found category type 50 with size 160. 
Proceeding to offset 669.
[   53.331403] EtherCAT DEBUG 0-0: Found category type 51 with size 160. 
Proceeding to offset 831.
[   53.336482] EtherCAT DEBUG 0-0: Found category type 60 with size 12. 
Proceeding to offset 845.
[   55.421478] EtherCAT DEBUG 0-0: Slave announces to support CoE, FoE.
[   55.421541] EtherCAT DEBUG 0-0: Unknown category type 0x003C.
[   55.421543] EtherCAT DEBUG 0-0: Slave is not in the state to do 
mailbox com (INIT), setting to PREOP.
[   55.421544] EtherCAT DEBUG 0-0: Configuring...
*[   55.421940] EtherCAT DEBUG 0-0: Now in INIT.*
[   55.421942] EtherCAT DEBUG 0-0: Clearing FMMU configurations...
[   55.422051] EtherCAT DEBUG 0-0: Clearing sync manager configurations...
[   55.422135] EtherCAT DEBUG 0-0: Clearing DC assignment...
[   55.422205] EtherCAT DEBUG 0-0: Configuring mailbox sync managers...
[   55.422206] EtherCAT DEBUG 0-0: SM0: Addr 0x1000, Size 1024, Ctrl 
0x26, En 1
[   55.422207] EtherCAT DEBUG 0-0: SM1: Addr 0x1400, Size 1024, Ctrl 
0x22, En 1
[   55.422277] EtherCAT DEBUG 0-0: Assigning SII access to PDI.
*[   55.431498] EtherCAT DEBUG 0-0: Now in PREOP.*
[   55.431500] EtherCAT DEBUG 0-0: Assigning SII access back to EtherCAT.
[   55.431570] EtherCAT DEBUG 0-0: Finished configuration.
[   55.431571] EtherCAT DEBUG 0-0: Scanning PDO assignment and mapping.
[   55.431572] EtherCAT DEBUG 0-0: Reading PDO assignment of SM2.
[   55.431573] EtherCAT DEBUG 0-0: Uploading SDO 0x1C12:00.
[   55.431575] EtherCAT DEBUG 0-0: Upload request:
[   55.431575] EtherCAT DEBUG: 00 20 40 12 1C 00 00 00 00 00
[   55.441795] EtherCAT DEBUG 0-0: Upload response:
[   55.441797] EtherCAT DEBUG: 00 30 4F 12 1C 00 01 00 00 00
[   55.441802] EtherCAT DEBUG 0-0: Uploaded data:
[   55.441803] EtherCAT DEBUG: 01
[   55.441803] EtherCAT DEBUG 0-0: 1 PDOs assigned.

I noticed, in the log there are messages stating it is in the INIT and 
PREOP states. Is this the slave device?

Best regards,

Oguz.


On 18-Mar-26 1:04 AM, Graeme Foot wrote:
> Hi Oguz,
>
> You can check if you have the patch by looking in configure.ac.  If it has the "--enable-sii-override" option you have it and you can select to use it with your preferred firmware directory.
>
> Re below:
> I didn't notice any major differences between the generated and downloaded SII files.
>
> Regards,
> Graeme.
>
> -----Original Message-----
> From: Etherlab-users<etherlab-users-bounces at etherlab.org> On Behalf Of Bilko AS, Oguz Dilmac
> Sent: Wednesday, 18 March 2026 02:59
> To: Richard Hacker<ha at igh.de>;etherlab-users at etherlab.org
> Subject: Re: [Etherlab-users] Timeout while setting state INIT.
>
> Hi Richard,
>
> Here is the output of "ethercat slave -v" command:
>
> ~$ ethercat slave -v
> === Master 0, Slave 0 ===
> Device: Main
> State: PREOP
> Flag: +
> Identity:
>     Vendor Id:       0x6167656d
>     Product code:    0x00000000
>     Revision number: 0x00000000
>     Serial number:   0x00000000
> DL information:
>     FMMU bit operation: no
>     Distributed clocks: yes, 64 bit
>     DC system time transmission delay: 0 ns Port  Type  Link  Loop    Signal  NextSlave  RxTime [ns]  Diff [ns]
>    NextDc [ns]
>      0  MII   up    open    yes             -    316752436    0           0
>      1  MII   down  closed  no              -            -    -           -
>      2  N/A   down  closed  no              -            -    -           -
>      3  N/A   down  closed  no              -            -    -           -
> Mailboxes:
>     Bootstrap RX: 0x1000/1024, TX: 0x1400/1024
>     Standard  RX: 0x1000/1024, TX: 0x1400/1024
>     Supported protocols: CoE, FoE
> General:
>     Group: SSC_Device
>     Image name:
>     Order number: Megatec_ESC_NLCH
>     Device name: Megatec_ESC_NLCH
>     CoE details:
>       Enable SDO: yes
>       Enable SDO Info: yes
>       Enable PDO Assign: no
>       Enable PDO Configuration: no
>       Enable Upload at startup: no
>       Enable SDO complete access: yes
>     Flags:
>       Enable SafeOp: no
>       Enable notLRW: no
>     Current consumption: 0 mA
>
> Also you can check the "ethercat sii_read" command output and the twincat sii file as binary files. I think the twincat version doesn't have the PDO mapping.
>
> https://we.tl/t-0aPRUmH6FG
>
> By the way, I tried to write the same registers I mentioned on my previous mails. Just before activating the master. It didn't affect anything.
>
> One more thing I noticed is, usually if I try to configure the device second time without a power cycle, the vendor ID at the response of the "ethercat slaves" command becomes 0.
>
> So far the vendor just claims the different devices (The one works perfectly with IgH and the one which doesn't reply to INIT command) are same in sense of ethercat communication.
>
> I would really appreciate if you can notice something.
>
> Best regards,
>
> Oguz.
>
>
>
> On 17-Mar-26 3:12 PM, Richard Hacker wrote:
>> Hi Oguz
>>
>> Our ethercat master does not support "SII firmware injection". We
>> rather work according to the maxime: fix the slave.
>>
>> Although we focus on Beckhoff slaves, we have worked with many
>> different slave vendors in the past and have yet to encounter a slave
>> with a behaviour like yours.
>>
>> We have encountered slaves with a broken SII in the past. Usually we
>> would confront the vendor. If that didn't work, we fixed it and
>> flashed the slave ourselves. But that requires intimate knowledge of
>> ethercat slave implementation beyond that of a regular slave user.
>>
>> I am not convinced that you have an SII problem. What does
>> 	ethercat slave -v
>> report when you have just plugged in the bus and before starting your
>> application (i.e. idle mode)?
>>
>> If there is sensible output from that command, your SII is OK.
>>
>> Richard
>>
>> On Tue, 2026-03-17 at 10:56 +0300, Bilko AS, Oguz Dilmac wrote:
>>>    
>>> Hi Richard and Graeme,
>>>    
>>> Richard, do you know if the feature Graeme mentioned is included in
>>> official branch?
>>>    
>>> And thank you Graeme for your message. What should I check if the
>>> version I used has this patch? It was some time ago when my colleague
>>> created an image of the system, and I'm not sure where is the source
>>> code of the EtherCAT master that was used.
>>>    
>>> Best regards,
>>>    
>>> Oguz.
>>>    
>>> On 15-Mar-26 11:28 PM, Graeme Foot wrote:
>>>    
>>>    
>>>>       
>>>>    Hi Oguz,
>>>>     
>>>>    I haven’t looked at all closely to the issue (and a couple of
>>>> emails got blocked by our spam/virus filter), but if you suspect
>>>> that the slaves SII information is incorrect then you can try
>>>> supplying the SII information yourself, rather than the master
>>>> downloading if from the slave.  If that then works, you can check
>>>> for the differences between the SII on the slave and the data
>>>> provided by the esi file.  If confirmed you can request the vendor
>>>> provides an update for the slave with the correct SII information
>>>> (or continue using the manual SII file).
>>>>     
>>>>    We use quite an old EtherLab master with patches to allow loading
>>>> your own SII file instead of the master downloading it from the
>>>> slave (from gavinl’s patchset “0001-load-sii-from-file.patch”).  I
>>>> don’t know what’s available in your master configuration, but in
>>>> ours we copy the SII file to “/lib/firmware/ethercat”
>>>>     
>>>>    To create an SII file:
>>>>     * Start a new TwinCAT project (TwinCAT XAE Project (XML Format))
>>>>    * Under I/O, Devices add an EtherCAT Master device
>>>>    * If you don’t have the correct esi (.xml) file loaded: copy the
>>>> slaves esi (.xml) file into:
>>>> C:\TwinCAT\3.1\Config\Io\EtherCATSelect the TwinCAT, EtherCAT
>>>> Devices, Reload Device Descriptions menu option
>>>>    * Add you EtherCAT slave to the EtherCAT master device
>>>>    * Open your slave
>>>>    * Select the EtherCAT tab
>>>>    * Select Advanced Settings...
>>>>    * Select the ESC Access, E2PROM, Hex Editor item
>>>>    * Confirm the SII contains the expected values (for Vendor ID ,
>>>> Product Code etc)
>>>>    * Select the Write to File... button
>>>>    * Save with a filename in the format
>>>> “ec_{vendor_id_hex}_{product_code_hex}[_{revision_hex}].bin” The
>>>> revision part is optional.e.g.: ec_00000539_02200001_00010000.bin
>>>>     
>>>>    Regards,
>>>>    Graeme.
>>>>     
>>>>      From: Etherlab-users<etherlab-users-bounces at etherlab.org> On
>>>> Behalf Of Bilko AS, Oguz Dilmac
>>>>    Sent: Saturday, 7 March 2026 02:30
>>>>    To: Richard Hacker<ha at igh.de>;etherlab-users at etherlab.org
>>>>    Subject: Re: [Etherlab-users] Timeout while setting state INIT.
>>>>    
>>>>    
>>>>     
>>>>    Hi,
>>>>    We are still working on the problematic slave which doesn't go to
>>>> INIT. I'm trying to understand the difference by examining wireshark
>>>> logs.
>>>>    I noticed these following messages are sent at the beginning. And
>>>> the device changed to INIT itself. It seems as if there is something
>>>> wrong with SM configuration?
>>>>    FPRD: 0x80d Return value: 0x30 (SM error / sm enable acknowledged)
>>>>
>>>> FPWR: 0x800 16 byte data: 0    (Clear SM0 and 1?)
>>>> FPWR: 0x800 8 byte data: 0010000426000100  (Re write SM according to
>>>> XML file?)
>>>> FPWR: 0x808 8 byte data: 0014000422000100
>>>> FPWR: 0x810 16 byte data: 0     (Clear SM2 and 3?)
>>>>
>>>> FPWR: 0x620 16 byte data: 00000009010000000d08000101000000 (define
>>>> FMMU?)
>>>> FPWR: 0x500 1 byte data: 01
>>>>
>>>> FPWR: 0x120 2 byte data: 0012 (PreOP + Error ACK)
>>>> FPRD: 0x130 Return value: 0x0002 (PREOP)
>>>>
>>>> FPRD: 0x80D Return value: 0x00 (The error is gone!)
>>>>
>>>> FPRD: 0x1400 Return value: 0x00 (but WC is zero. I guess the slave
>>>> didn't processed it)
>>>>
>>>> FPRD: 0x130 Return value: 0x0001 (INIT) (Slave went to INIT. But I
>>>> didn't see a write to 0x120 to go to INIT)
>>>>
>>>> FPWR: 0x800 16 byte data: 0
>>>> FPRD: 0x1400 Return value: 0x5208
>>>> FPWR: 0x620 16 byte data: 0
>>>> FPRD: 0x1400 Return value: 1024 byte data...0x80
>>>>
>>>> ...
>>>>
>>>>     
>>>>    Could this be the reason why the slave don't go to INIT when IgH
>>>> master ask?
>>>>    By the way I tried to write the right values to 0x800 via
>>>> ecrt_reg_request_write. I tried to call this function right after
>>>> ecrt_master_activate. But it didn't work.
>>>>    You can find the log file at the attachments. I hope someone can
>>>> give me a suggestion.
>>>>    Best regards,
>>>>    Oguz.
>>>>     
>>>>     On 25-Feb-26 3:42 PM, Bilko AS, Oguz Dilmac wrote:
>>>>    
>>>>    
>>>>>    
>>>>> Hi Again,
>>>>>    
>>>>> I just sent some dmesg outputs and a test program using a new
>>>>> ethercat library. Unfortunately it hit a max 200KB attachment
>>>>> limit. Sorry I didn't notice this limit before. And could not
>>>>> cancel my message either.
>>>>>    
>>>>> Anyway, I uploaded the files to wetransfer. I also uploaded a
>>>>> wireshark log of twincat while the problem device goes to OP.
>>>>> Here is the link:
>>>>>    
>>>>> https://we.tl/t-Yl7iRMSadB
>>>>>    
>>>>> I also copy my previous message here:
>>>>>    
>>>>> Hello,
>>>>>    
>>>>>    We went to customer side and used a test PC with ethercat library
>>>>> 1.6.7. We also used slave timeout function with 10 seconds.
>>>>>    
>>>>>    We build a simple setup with only one device and one test PC.
>>>>> Still the old device is going OP, and the new device don't.
>>>>>    
>>>>>    At the attachments you can find some dmesg outputs. I also
>>>>> attached the simple test program I used.
>>>>>    
>>>>>    Some explanations for dmesg outputs:
>>>>>    
>>>>>    * dmesg.OK.txt: Output for the working device. I just put it here
>>>>> as a reference
>>>>>    
>>>>>    * dmesg.Problem.txt: Output of the problematic device.
>>>>>    
>>>>>    * dmesg.Problem.freerun.txt: I tried to activate freerun with
>>>>> ecrt_slave_config_dc(sc, 0, 0, 0, 0, 0); I put it right before
>>>>> ecrt_master_activate().
>>>>>    
>>>>>    * dmesg.Problem.ManualStateChange: I tried to change state via
>>>>> command line tool.
>>>>>    
>>>>>    We also checked and see that both devices are going to OP with
>>>>> twincat. If you suggest a way to get some log from twincat, we can
>>>>> try.
>>>>>    
>>>>>    We are stuck 🙁 If you have any idea It would be great.
>>>>>    
>>>>>    Best regards,
>>>>>    
>>>>>    Oguz.
>>>>>    
>>>>>    
>>>>>    
>>>>>    On 20-Feb-26 1:30 PM, Richard Hacker wrote:
>>>>>    
>>>>>    
>>>>>>    
>>>>>> On Fri, 2026-02-20 at 12:49 +0300, Bilko AS, Oguz Dilmac wrote:
>>>>>>    
>>>>>>>    
>>>>>>> Hi,
>>>>>>>    
>>>>>>>    
>>>>>>>    
>>>>>>> We will try to install the newest ethercat library version.
>>>>>>>    
>>>>>>>    
>>>>>>>    
>>>>>>> By the way, we tried one version older of this device. It goes to
>>>>>>> OP
>>>>>>>    
>>>>>>> with no problem.
>>>>>>>    
>>>>>>    
>>>>>> Well, this shows that your configuration is probably not the issue
>>>>>> and
>>>>>>    
>>>>>> is at the problem is at the slave's side
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>>    
>>>>>>> Also our customer has a bechoff controller as well, and they say
>>>>>>> that
>>>>>>>    
>>>>>>> with twincat both devices are going to OP without a problem.
>>>>>>>    
>>>>>>    
>>>>>> TwinCAT is not the standard, neither is our EtherCAT master.
>>>>>> However,
>>>>>>    
>>>>>> both should implement the standard, but they do it differently
>>>>>>    
>>>>>> (naturally), especially regarding timing. The standard however
>>>>>> ensures
>>>>>>    
>>>>>> that EtherCAT masters and slaves are immune to timing issues, but
>>>>>> there
>>>>>>    
>>>>>> are always exceptions!
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>>    
>>>>>>> We will try to go to the customer and check with the newest
>>>>>>> ethercat
>>>>>>>    
>>>>>>> master version. We are also considering to connect the both
>>>>>>> devices
>>>>>>>    
>>>>>>> to
>>>>>>>    
>>>>>>> the twincat and see if the twincat behaves different. Do you
>>>>>>> think
>>>>>>>    
>>>>>>> checking the transmitted data via wireshark worth trying?
>>>>>>>    
>>>>>>    
>>>>>> You can try, but I do not see that you'll get much insight using
>>>>>>    
>>>>>> wireshark. The master commands the slave to go to INIT and there
>>>>>> is
>>>>>>    
>>>>>> simply no reply from the slave acknowledging the state change.
>>>>>> That is
>>>>>>    
>>>>>> why the master times out and gives up trying to bring the slave
>>>>>> online.
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>> Going to INIT is such a primitive state change for a slave that
>>>>>> there
>>>>>>    
>>>>>> should be absolutely _no_ reason it takes any amount of time.
>>>>>> So I am
>>>>>>    
>>>>>> not even convinced that ecrt_slave_config_state_timeout() would
>>>>>> work.
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>> I only know that some (complex) slaves may take time between
>>>>>> PREOP-
>>>>>>    
>>>>>>>    
>>>>>>> SAFEOP and SAFEOP->OP transition when certain hardware needs to
>>>>>>> be
>>>>>>>    
>>>>>>    
>>>>>> configured based on its configuration. But your slave is not there
>>>>>> yet.
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>> Before you use wireshark you can try switching debug to 1
>>>>>>    
>>>>>> `ethercat debug 1`
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>>    
>>>>>    
>>>>> --
>>>>>    
>>>>> Oguz Dilmac
>>>>>    
>>>>>    
>>>>>    
>>>>> Bilko AS, R&D Manager
>>>>>    
>>>>> ====================================
>>>>>    
>>>>> Perpa Ticaret Merkezi B Blok Kat 13 Nr. 2536
>>>>>    
>>>>> TR-34384 Okmeydani Istanbul Turkey
>>>>>    
>>>>> Tel : +90 212 563 00 00
>>>>>    
>>>>> e-mail :odilmac at bilko-automation.com
>>>>>    
>>>>> web site :http://www.bilko-automation.com
>>>>>    
>>>>> https://www.youtube.com/@LyncaCNC
>>>>>    
>>>>    --
>>>>    Oguz Dilmac
>>>>     
>>>>    Bilko AS, R&D Manager
>>>>    ====================================
>>>>    Perpa Ticaret Merkezi B Blok Kat 13 Nr. 2536
>>>>    TR-34384 Okmeydani Istanbul Turkey
>>>>    Tel : +90 212 563 00 00
>>>>    e-mail :odilmac at bilko-automation.com
>>>>    web site :http://www.bilko-automation.com
>>>>    https://www.youtube.com/@LyncaCNC
>>>>    
>>>>    
>>>    
> --
> Oguz Dilmac
>
> Bilko AS, R&D Manager
> ====================================
> Perpa Ticaret Merkezi B Blok Kat 13 Nr. 2536
> TR-34384 Okmeydani Istanbul Turkey
> Tel : +90 212 563 00 00
> e-mail :odilmac at bilko-automation.com
> web site :http://www.bilko-automation.com https://www.youtube.com/@LyncaCNC
>
>
> --
> Etherlab-users mailing list
> Etherlab-users at etherlab.org
> https://lists.etherlab.org/mailman/listinfo/etherlab-users

-- 
Oguz Dilmac

Bilko AS, R&D Manager
====================================
Perpa Ticaret Merkezi B Blok Kat 13 Nr. 2536
TR-34384 Okmeydani Istanbul Turkey
Tel : +90 212 563 00 00
e-mail :odilmac at bilko-automation.com
web site :http://www.bilko-automation.com
https://www.youtube.com/@LyncaCNC
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20260318/410d4abd/attachment-0001.htm>


More information about the Etherlab-users mailing list