[Etherlab-users] Timeout while setting state INIT.

Bilko AS, Oguz Dilmac odilmac at bilko-automation.com
Tue Mar 24 08:36:43 CET 2026


Hi Richard, Graeme,

I was out of the office. Thank you for the suggestions. Graeme I'll try 
to look into it.

Mr Richard, here are the outputs of the commands after I powered both PC 
and the slave:

lynca at lynca:~$ sudo /usr/local/etc/init.d/ethercat restart
Shutting down EtherCAT master 1.6.8  done
Starting EtherCAT master 1.6.8  done
lynca at lynca:~$ ethercat slave
0  0:0  PREOP  +  Megatec_ESC_NLCH
lynca at lynca:~$ ethercat slaves
0  0:0  PREOP  +  Megatec_ESC_NLCH
lynca at lynca:~$ sudo ethercat state -p0 init
lynca at lynca:~$ ethercat slave
0  0:0  PREOP  E  Megatec_ESC_NLCH
lynca at lynca:~$ sudo ethercat state -p0 preop
lynca at lynca:~$ ethercat slave
0  0:0  PREOP  +  Megatec_ESC_NLCH
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint32 0x900
0x0af50b04 183831300
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint64 0x910
0x00000051a7927504 350703744260
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint16 0x120
0x0001 1
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint16 0x130
0x0002 2
lynca at lynca:~$

And these are executed while the application is running:

lynca at lynca:~$ sudo ethercat slave
0  0:0  PREOP  E  Megatec_ESC_NLCH
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint16 0x120
0x0001 1
lynca at lynca:~$ sudo ethercat reg_read -p0 -tuint16 0x130
0x0002 2

The installed ethercat master is 1.6.8 with Mr James Benway's patch  for 
reading sii from a 
file (https://github.com/DSI-Gleeble/ethercat/tree/sii-from-file). But I 
removed the binary sii files so that the master can read from slave as 
normal.

Can you see something?

Best regards,

Oguz.


On 20-Mar-26 6:34 PM, Richard Hacker wrote:
> My suspicion is that your problem is way before the master tries to
> configure the slave, as I have said before.
>
> When the master is activated, it jogs the slave through the INIT,
> PREOP, SAFEOP and eventually OP states. A slave gets configured (SDO
> parameters, PDO setup) between the PREOP and SAFEOP state -- but your
> slave never gets there. Your slave might go into INIT, but somehow the
> master does not get this state change.
>
> Can you change the slave state from the command line? With your slave
> attached but without your application running (i.e. idle free-run bus),
> what is the output of:
> 	ethercat slave
> 	ethercat state -p0 init
> 	ethercat slave
> 	ethercat state -p0 preop
> 	ethercat slave
> 	ethercat reg_read -p0 -tuint32 0x900
> 	ethercat reg_read -p0 -tuint64 0x910
> 	ethercat reg_read -p0 -tuint16 0x120
> 	ethercat reg_read -p0 -tuint16 0x130
>
> Now start your application and:
> 	ethercat state
> 	ethercat reg_read -p0 -tuint16 0x120
> 	ethercat reg_read -p0 -tuint16 0x130
>
>
> -p0 assumes the affedted slave is the first slave in the network.
> Adjust accordingly if that is not the case.
>
> On Fri, 2026-03-20 at 00:02 +0000, Graeme Foot wrote:
>>
>> Hi Oguz,
>>   
>> If this is a potential fix for your slave, you would require more
>> separation, plus I’m not sure you got your reads vs writes assigned
>> quite right.  i.e. from your log 0x6000:01 is being assigned to
>> domain 0 when it looks like it should be assigned to domain 1.
>>   
>>   
>> The issue with the Texas Instruments ESC’s in particular is that if
>> you use one domain the writes (control) and reads (status) are too
>> close together for the ESC’s syncs to handle gracefully.  E.g.:
>>   
>> + domain 0 -------------------+
>> |[slave 0 write][slave 0 read]|
>>   
>> If you split them into two domains you get:
>>   
>> + domain 0 -----+ domain 1 ----+
>> |[slave 0 write]|[slave 0 read]|
>>   
>> Which timing wise is no real difference and still a problem.
>>   
>> But if you add a few more slaves (they don’t even need to be online)
>> you get:
>>   
>> + domain 0 -------------------------+ domain 1 ----------------------
>> --+
>> |[slave 0 write][slave 1 write][...]| [slave 0 read][slave 1
>> read][...]|
>>   
>> You can see you now have more separation between the slave 0 write
>> and read.
>>   
>> In your example (apart from the potential incorrect allocation which
>> could itself cause issues) I don’t think the EL2008 would be enough
>> to give a big enough separation (only 1 byte?).  Try adding two or
>> three more of your problem slaves (they’re around 78 bytes each).
>>   
>>   
>> Here’s some background info on the Texas Instruments
>> issue:https://www.ti.com/lit/an/spracj7/spracj7.pdf?ts=1669243747147
>>   * section 3.1.3 describes the TI ESC not working with non-
>> overlapping PDOs
>>   * Section 3.6 describes a malformed packet issue and its
>> workarounds, due to overlapping PDOs
>>   
>> In our cases where we’ve had problems with slaves our symptoms were:
>>     1. On assigning the FMMU configuration the slave would stop
>> forwarding on frames
>>     2. I think we had one that got stuck in INIT, but can’t remember
>> for sure
>>   
>> Regards,
>> Graeme.
>>   
>>   
>>
>>
>> From: Bilko AS, Oguz Dilmac <odilmac at bilko-automation.com>
>> Sent: Thursday, 19 March 2026 23:49
>> To: Graeme Foot <Graeme.Foot at touchcut.com>;
>> etherlab-users at etherlab.org
>> Subject: Re: [Etherlab-users] Timeout while setting state INIT.
>>   
>> Hi Graeme,
>> I connected a EK1100 bus coupler and a EL2008 digital output card.
>> The first slave is the EK1100, and my device stay at the end.
>> I created two domains
>> Unfortunately the device still don't go to INIT.
>> Here, I put my test code and the dmesg output:
>> https://we.tl/t-Dj1MtId6LA
>> Best regards,
>> Oguz.
>>   
>>
>> On 19-Mar-26 1:16 AM, Graeme Foot wrote:
>>> Hi Oguz,
>>>   
>>> It’s not looking likely to be an SII problem then.
>>>   
>>>  From the log it looks like you’re using a single Read/Write
>>> domain.  I don’t recall if you mentioned, have tried putting it in
>>> separate read and write domains?  If you try this, also ensure that
>>> there are at least two other separate read and write domain slaves
>>> also configured in your system.
>>>   
>>> I’ve had a few slaves in the past (generally with Texas Instruments
>>> ESC’s) that work well with overlapped PDO’s in a single Read/Write
>>> domain (TwinCat’s default method), but fail when the PDO’s are not
>>> overlapped (EtherLab’s default).  If this is the case you can put
>>> them in separate read and write domains to separate them within the
>>> EtherCat frame.  But, you need to ensure there’s a couple of other
>>> read and write domain devices also configured to ensure there’s
>>> enough separation in the frame.
>>>   
>>>   
>>> Graeme.
>>>   
>>>
>>>
>>> From: Bilko AS, Oguz Dilmac<odilmac at bilko-automation.com>
>>> Sent: Thursday, 19 March 2026 02:33
>>> To: Graeme Foot <Graeme.Foot at touchcut.com>; Richard
>>> Hacker<ha at igh.de>; etherlab-users at etherlab.org;
>>> james.benway at gleeble.com
>>> Subject: Re: [Etherlab-users] Timeout while setting state INIT.
>>>   
>>> Hi,
>>> I noticed, the correct path with option is: "--enable-sii-
>>> override=/lib/firmware"
>>> This way, the master can find my ec_xxx.bin file. But still at the
>>> end, slave doesn't respond to go INIT command.
>>> Here is the dmesg output:
>>> https://we.tl/t-BGDmNzZv2b
>>> Best regards,
>>> Oguz.
>> -- 
>> Oguz Dilmac
>>   
>> Bilko AS, R&D Manager
>> ====================================
>> Perpa Ticaret Merkezi B Blok Kat 13 Nr. 2536
>> TR-34384 Okmeydani Istanbul Turkey
>> Tel : +90 212 563 00 00
>> e-mail : odilmac at bilko-automation.com
>> web site : http://www.bilko-automation.com
>> https://www.youtube.com/@LyncaCNC

-- 