[etherlab-users] Using EK1100 & EL2008 with DC

Oguz Dilmac odilmac at bilko.com.tr
Thu Jul 5 17:33:47 CEST 2012


Hi,

Thank you Ralf and Florian, for the answers.
I'll try to use something else.

Now I have another problems:

1. If I don't use DC, I can control the drive and IO devices at the same 
time.

2. If I use DC (without configuring IO devices), I can't go to 
operational at first initialisation. But If I re-run the config sequence 
I can control the drive.

3. If I connect and configure the IO devices next to the drive, at first 
I can set the outputs of the device. But due to the problem above I can 
not control the device.

4. If I re-run init sequence, this time my process domain information 
some how corrupts. IO device outputs are no longer in the process data.

5. Regarding to a post by Graeme, I introduced two domains. One for 
writing, one for reading. The behaviour remained same.
http://lists.etherlab.org/pipermail/etherlab-users/2012/001737.html

6. Then I seperated the domains one for IO device, one for motor driver. 
Now my controller task suspends with Trap Handler: vector 14 message.

What is it I'm missing? How should I use DC?

Best regards,
(and Iyi aksamlar :) )
Oguz.


03.07.2012 20:52 tarihinde, Ralf Roesch yazdı:
> Oguz,
>
> if you have a look at the Beckhoff site you will find the EL2008 
> technical data table:
>
> -- 
> Technical data    EL2808
> Connection technology    2-wire
> Number of outputs    8
> Rated load voltage    24 V DC (-15 %/+20 %)
> Load type    ohmic, inductive, lamp load
> Distributed clocks    –
> Max. output current    0.5 A (short-circuit-proof) per channel
> Short circuit current    typ. < 2 A
> ...
> -- 
>
> The distributed clocks is not available regarding the table.
>
> My estimation is:
> the module itself might have a DC capable EtherCAT slave controller 
> (ESC) which is detected by the EtherLab Master
> but the module does not support the logic (hard, soft) for DC operation.
>
> Regarding AssignActivate:
> you should use it for modules where DC is required and hardware I/O is 
> synchronized to the EtherCAT real time bus cycle.
> The EK1100 bus coupler  has no I/O and thus no need for an 
> AssignActivate setup.
> It only has the function (besides module extension) as a reference 
> clock slave in your setup because it is the first detected DC capable 
> slave device.
>
> I think you have to look for an other output module.
>
> regards and iye aksamlar
> Ralf
>
> On Tue Jul 03 2012 18:14:09 GMT+0200, Oguz Dilmac 
> <odilmac at bilko.com.tr>  wrote:
>> Hi Ralf,
>>
>> I checked again with etherlab master. It looks my devices support it.
>>
>> Then I checked from Beckoff site: I downloaded "EL20xx_EL2124en.chm" 
>> from, http://www.beckhoff.com/english.asp?download/elconfg.htm.
>> In the "Basic Communication" -> "Distributed Clock" section it 
>> suggests these devices support DC. But it is not so clear.
>>
>> I also downloaded the EL2xxx.xml with Beckhoff_EtherCAT_XML.zip.
>> There is no <AssignActivate> section for EL2008. But it does have 
>> this section for some other devices.
>> I also checked EK1100 from the xml files. There is no 
>> <assignActivate> section for it either. But I remember that some 
>> users of the list using this device as the reference clock.
>>
>> What am I missing?
>>
>> Best regards,
>> (and selamlar :) )
>> Oguz.
>>
>> By the way, here is the information I get from ethercat master:
>> When I type:
>> ethercat slaves -v
>>
>> I get:
>> === Master 0, Slave 0 ===
>> State: PREOP
>> Flag: +
>> Identity:
>> Vendor Id: 0x00000002
>> Product code: 0x044c2c52
>> Revision number: 0x00110000
>> Serial number: 0x00000000
>> DL information:
>> FMMU bit operation: no
>> Distributed clocks: yes, 64 bit
>> DC system time transmission delay: 0 ns
>> Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
>> 0 MII up open yes - 1281615183 0 0
>> 1 EBUS up open yes 1 1281615783 600 145
>> 2 MII down closed no - - - -
>> 3 N/A down closed no - - - -
>> General:
>> Group: SystemBk
>> Image name:
>> Order number: EK1100
>> Device name: EK1100 EtherCAT-Koppler (2A E-Bus)
>> Flags:
>> Enable SafeOp: no
>> Enable notLRW: no
>> Current consumption: -2000 mA
>> === Master 0, Slave 1 ===
>> State: PREOP
>> Flag: +
>> Identity:
>> Vendor Id: 0x00000002
>> Product code: 0x07d83052
>> Revision number: 0x00100000
>> Serial number: 0x00000000
>> DL information:
>> FMMU bit operation: no
>> Distributed clocks: yes, 64 bit
>> DC system time transmission delay: 145 ns
>> Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
>> 0 EBUS up open yes 0 1299932986 0 145
>> 1 EBUS up open yes 2 1299933296 310 155
>> 2 N/A down closed no - - - -
>> 3 N/C down closed no - - - -
>> General:
>> Group: DigOut
>> Image name:
>> Order number: EL2008
>> Device name: EL2008 8K. Dig. Ausgang 24V, 0.5A
>> Flags:
>> Enable SafeOp: no
>> Enable notLRW: no
>> Current consumption: 110 mA
>> === Master 0, Slave 2 ===
>> State: PREOP
>> Flag: +
>> Identity:
>> Vendor Id: 0x00000002
>> Product code: 0x03f03052
>> Revision number: 0x00100000
>> Serial number: 0x00000000
>> DL information:
>> FMMU bit operation: no
>> Distributed clocks: yes, 64 bit
>> DC system time transmission delay: 300 ns
>> Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
>> 0 EBUS up open yes 1 1311888425 0 155
>> 1 EBUS down closed no - - - -
>> 2 N/A down closed no - - - -
>> 3 N/C down closed no - - - -
>> General:
>> Group: DigIn
>> Image name: TERM_DI
>> Order number: EL1008
>> Device name: EL1008 8K. Dig. Eingang 24V, 3ms
>> Flags:
>> Enable SafeOp: no
>> Enable notLRW: no
>> Current consumption: 90 mA
>>
>>
>>
>> 03.07.2012 17:05 tarihinde, Ralf Roesch yazdı:
>>> Oguz,
>>>
>>> I don't think that the EL2008 supports DC.
>>> You can check it with the
>>> ethercat slaves -pXXX -v
>>>
>>> I have a EL2004 which shows:
>>>
>>> ethercat slaves -p3 -v
>>> ...
>>> DL information:
>>> FMMU bit operation: no
>>> Distributed clocks: no
>>> ...
>>>
>>> If you have a DC-capable Module you can find the <AssignActivate> 
>>> mode in the ESI-File (XML).
>>> You would find it in the EL2xxx.xml - File from Beckhoff if it would 
>>> support DC.
>>>
>>> selamlar
>>> Ralf
>>>
>>> On Tue Jul 03 2012 15:27:41 GMT+0200, Oguz Dilmac 
>>> <odilmac at bilko.com.tr> wrote:
>>>> Hi,
>>>>
>>>> I want to use Distrubuted Clocks.
>>>> And to test it, I want to create a square wave on one of the 
>>>> digital outputs and watch it on an ossiloscope to see the jitter.
>>>> I'm using RTAI with kernel modules.
>>>>
>>>> I looked to the dc_rtai_sample.c.
>>>> I don't have an IDS counter. But I have an EK1100 and EL2008
>>>> How can I modify the sample code to activate DC on EK1100 and EL2008
>>>>
>>>> I know they support DC. But I don't know what to write to 
>>>> "assignActivate" code.
>>>>
>>>> Best regards,
>>>> Oguz.
>>>> _______________________________________________
>>>> etherlab-users mailing list
>>>> etherlab-users at etherlab.org
>>>> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>>>
>>>
>>>
>>
>>
>
>
>