[etherlab-users] Beckhoff EL6001/EL6021 Issues

Graeme Foot Graeme.Foot at touchcut.com
Tue Jun 3 01:32:38 CEST 2014


Hi,

My PDO entries are:

ec_pdo_entry_info_t EL6021_pdoEntries[] = {
    {0x3003, 0x01, 16}, /* Ctrl */
    {0x3003, 0x02, 8}, /* Data Out 0 */
    {0x3003, 0x03, 8}, /* Data Out 1 */
    {0x3003, 0x04, 8}, /* Data Out 2 */
    {0x3003, 0x05, 8}, /* Data Out 3 */
    {0x3003, 0x06, 8}, /* Data Out 4 */
    {0x3003, 0x07, 8}, /* Data Out 5 */
    {0x3003, 0x08, 8}, /* Data Out 6 */
    {0x3003, 0x09, 8}, /* Data Out 7 */
    {0x3003, 0x0a, 8}, /* Data Out 8 */
    {0x3003, 0x0b, 8}, /* Data Out 9 */
    {0x3003, 0x0c, 8}, /* Data Out 10 */
    {0x3003, 0x0d, 8}, /* Data Out 11 */
    {0x3003, 0x0e, 8}, /* Data Out 12 */
    {0x3003, 0x0f, 8}, /* Data Out 13 */
    {0x3003, 0x10, 8}, /* Data Out 14 */
    {0x3003, 0x11, 8}, /* Data Out 15 */
    {0x3003, 0x12, 8}, /* Data Out 16 */
    {0x3003, 0x13, 8}, /* Data Out 17 */
    {0x3003, 0x14, 8}, /* Data Out 18 */
    {0x3003, 0x15, 8}, /* Data Out 19 */
    {0x3003, 0x16, 8}, /* Data Out 20 */
    {0x3003, 0x17, 8}, /* Data Out 21 */
    {0x3103, 0x01, 16}, /* Status */
    {0x3103, 0x02, 8}, /* Data In 0 */
    {0x3103, 0x03, 8}, /* Data In 1 */
    {0x3103, 0x04, 8}, /* Data In 2 */
    {0x3103, 0x05, 8}, /* Data In 3 */
    {0x3103, 0x06, 8}, /* Data In 4 */
    {0x3103, 0x07, 8}, /* Data In 5 */
    {0x3103, 0x08, 8}, /* Data In 6 */
    {0x3103, 0x09, 8}, /* Data In 7 */
    {0x3103, 0x0a, 8}, /* Data In 8 */
    {0x3103, 0x0b, 8}, /* Data In 9 */
    {0x3103, 0x0c, 8}, /* Data In 10 */
    {0x3103, 0x0d, 8}, /* Data In 11 */
    {0x3103, 0x0e, 8}, /* Data In 12 */
    {0x3103, 0x0f, 8}, /* Data In 13 */
    {0x3103, 0x10, 8}, /* Data In 14 */
    {0x3103, 0x11, 8}, /* Data In 15 */
    {0x3103, 0x12, 8}, /* Data In 16 */
    {0x3103, 0x13, 8}, /* Data In 17 */
    {0x3103, 0x14, 8}, /* Data In 18 */
    {0x3103, 0x15, 8}, /* Data In 19 */
    {0x3103, 0x16, 8}, /* Data In 20 */
    {0x3103, 0x17, 8}, /* Data In 21 */
};

ec_pdo_info_t EL6021_pdos[] = {
    {0x1602, 23, EL6021_pdoEntries + 0}, /* RxPDO-Map Outputs */
    {0x1a02, 23, EL6021_pdoEntries + 23}, /* TxPDO-Map Inputs */
};

ec_sync_info_t EL6021_syncs[] = {
    {0, EC_DIR_OUTPUT, 0, NULL, EC_WD_DISABLE},
    {1, EC_DIR_INPUT, 0, NULL, EC_WD_DISABLE},
    {2, EC_DIR_OUTPUT, 1, EL6021_pdos + 0, EC_WD_DISABLE},
    {3, EC_DIR_INPUT, 1, EL6021_pdos + 1, EC_WD_DISABLE},
    {0xff}
};



When I first compared them to yours they looked the same.

Regards,
Graeme.


-----Original Message-----
From: Derrill Vezina [mailto:dvezina at caron-eng.com] 
Sent: Saturday, 31 May 2014 05:44
To: Richard Hacker
Cc: Graeme Foot
Subject: RE: [etherlab-users] Beckhoff EL6001/EL6021 Issues

Hi Richard,

I know I posted on the mailing list recently about getting some help with the EL6021 / EL6001 modules with some sample code. Unfortunately, I still am unable to prove out a process we are trying to accomplish with the EL6021 due to the device not sending data (I just used the example with the EL6001 since its easier to debug the output with a terminal and they are just about identical except for the rts and cts and point to point / duplex type).

Before I posted on the mailing list, I worked with one of our local Beckhoff application engineers and I feel like he was leading me in the wrong direction with PDO and SDO mappings. In his defense, he doesn't know really how the etherlab master works so I wasn't really getting anywhere. 

A couple months ago, Beckhoff hired a linux programmer in Germany for 'driver' support, and started writing there own ethernet device drivers for your etherlab master (I didn't know if you knew this or not), which work with their FPGA controller for the CX50XX PC line, but he also wasn't able to give support for the EL6021 or EL6001 regarding the etherlab master.

I believe my issue is my PDO mapping for writing data. I was wondering if there is anyway I could get an example of the PDO structure you map in the domain with your working EL6021 device. I would like to make sure I am writing to the correct PDOs (my status / control registers are working correctly).

Thank you for the support you have given so far on the mailing list and I appreciate your time. You guys have done an excellent job with the master and the support has been awesome. If a solution is reached, I will post it on the mailing list incase someone else has the same issue I am having.

Best Regards,
Derrill Vezina

-----Original Message-----
From: etherlab-users-bounces at etherlab.org [mailto:etherlab-users-bounces at etherlab.org] On Behalf Of Richard Hacker
Sent: Saturday, May 24, 2014 8:32 AM
To: etherlab-users at etherlab.org
Subject: Re: [etherlab-users] Beckhoff EL6001/EL6021 Issues

Firstly, I only have experience with EL6022, but the EL6001 is not much different.

Start with small steps:
Connect TxD to RxD on the slave with a wire bridge to create a loopback.

Initialization:
PDO mapping:
	RxPdo = 0x1604 (CW and OutData: 24 bytes) to SyncManager 2
	TxPdo = 0x1a04 (SW and InData: 24 bytes) to SyncManager 3

	SW is byte[0] of TxPdo
	CW is byte[0] of RxPdo
	OutLength is byte[1] of RxPdo
	OutData = byte[2..24] of RxPdo
SDO settings:
	0x8000:0x01 = 0  (disable RTS/CTS)
	0x8000:0x05 = 0  (disable transfer rate optimization)
	0x8000:0x11 = 10 (115200 baud)
	0x8000:0x15 = 3  (8N1)
CW.InitRequest = 1
wait for SW.InitAccepted == 1
CW.InitRequest = 0
CW.OutLength = 10
Data[0..9] = random

Cyclic:
CW.TransmitRequest = !SW.TransmitAccepted CW.ReceiveAccepted = SW.ReceiveRequest sleep 1ms

By setting TransmitRequest to be inverse of TransmitAccepted, the slave will continuously transmit 10 bytes which are received again due to the loopback, causing TxD and RxD LED's to flicker. If they don't, there is something wrong in your program! Try to get this working first.

The above program should be a 50-liner (or so) for the actual coding. 
You could implement this using state machines, but for a short test program, I would attempt without first.

- Richard


On 05/23/2014 03:01 PM, Derrill Vezina wrote:
> I have 3 state machines in my code, initialization, write, and read. 
> The write and read state machines cannot be incremented until the 
> initialization state machine has completed.
>
> Everything I have done seems to match your data flow, the only 
> difference was I was setting the 0x407x registers for the SDO 
> configuration (the Beckhoff docs said from hardware version 03 so I 
> wanted it to be compatible). I changed my SDO writes to the 8000:xx 
> registers, but this did not change the data not pushing out the port. 
> I am running the EL6021 in half duplex mode so I have tx+ tied to rx+ 
> and
> tx- tied to tx-. Since I am seeing the issue with the EL6021 and the 
> EL6001, I am just trying to get the EL6001 working first since I have 
> the other side of the transmission line hooked up to PC.
>
> My system is setup through a configuration file which is parsed on 
> startup and the system adapts to what was in the contents of the file. 
> I currently have 10 or so Beckhoff cards which are mostly I/O modules.
> Therefore, the SDO registers are only set on startup and do not need 
> to have their own state machine in realtime since they can't really 
> change dynamically. I write all SDO registers before I configure the PDOs / domain.
>
>
> Here's how I am writing my SDO registers for the EL6001 and EL6021:
>
> // do all of the write requests....
> // the write value will change with respect to the data set in the 
> configuration file // // send xon xoff tx data[0] = 
> ecat.device[i].EL60xx_xon_xoff_tx ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x02, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_WARNING/) << "Failed to upload xon xoff tx SDO with code 
> "<< abort_code;
>
> // check xon xoff rx
> data[0] = ecat.device[i].EL60xx_xon_xoff_rx ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x03, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_WARNING/) << "Failed to upload xon xoff rx SDO with code 
> "<< abort_code;
>
> // check the baud rate
> *switch* (ecat.device[i].EL60xx_baud_rate){
> case 2400: data[0] = EL60XX_BAUD_2400; *break*;
> *case* 4800: data[0] = EL60XX_BAUD_4800; *break*;
> *case* 9600: data[0] = EL60XX_BAUD_9600; *break*;
> *default*:
> *case* 19200: data[0] = EL60XX_BAUD_19200; *break*;
> *case* 38400: data[0] = EL60XX_BAUD_38400; *break*;
> *case* 57600: data[0] = EL60XX_BAUD_57600; *break*;
> *case* 115200: data[0] = EL60XX_BAUD_115200; *break*; }
>
> // upload the baud rate
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x11, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload baud rate with code "<< 
> abort_code;
>
> // check the data frame
> *if* (ecat.device[i].EL60xx_data_bits == 7 && 
> ecat.device[i].EL60xx_stop_bits == 1 && ecat.device[i].EL60xx_parity 
> == 1) data[0] = EL60XX_DATA_7E1;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 7 && 
> ecat.device[i].EL60xx_stop_bits == 1 && ecat.device[i].EL60xx_parity 
> == 2) data[0] = EL60XX_DATA_7O1;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 1 && ecat.device[i].EL60xx_parity == 0)
>          data[0] = EL60XX_DATA_8N1;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 1 && ecat.device[i].EL60xx_parity == 1)
>          data[0] = EL60XX_DATA_8E1;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 1 && ecat.device[i].EL60xx_parity == 2)
>          data[0] = EL60XX_DATA_8O1;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 7 && 
> ecat.device[i].EL60xx_stop_bits == 2 && ecat.device[i].EL60xx_parity == 2)
>          data[0] = EL60XX_DATA_7O2;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 2 && ecat.device[i].EL60xx_parity == 0)
>          data[0] = EL60XX_DATA_8N2;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 2 && ecat.device[i].EL60xx_parity == 1)
>          data[0] = EL60XX_DATA_8E2;
> *else* *if* (ecat.device[i].EL60xx_data_bits == 8 && 
> ecat.device[i].EL60xx_stop_bits == 2 && ecat.device[i].EL60xx_parity == 2)
>          data[0] = EL60XX_DATA_8O2;
> *else*
>          data[0] = EL60XX_DATA_7E2;
>
> // upload the data frame
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x15, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload data frame with code "<< 
> abort_code;
>
> // check send fifo data continuous
> data[0] = ecat.device[i].EL60xx_send_fifo_continuous ? 1 : 0; if 
> (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x04, data, 1,
> &abort_code) < 0)
>          LOGMSG(/LOG_INFO/) << "Failed to upload send fifo cont. SDO 
> with code "<< abort_code;
>
> // check send transfer rate opt.
> data[0] = ecat.device[i].EL60xx_transfer_rate_opt ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x05, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload transfer rate opt. SDO with 
> code "<< abort_code;
>
> // check the device type
> *if* (ecat.device[i].dev_type == /DEV_EL6021/){ // send duplex data[0] 
> = ecat.device[i].EL6021_duplex ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x06, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload duplex type SDO with code "<< 
> abort_code;
>
> // check point to point communications
>          data[0] = ecat.device[i].EL6021_point_to_point ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x07, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload point to point SDO with code 
> "<< abort_code; }
> *else* {
> // check send rts cts
>          data[0] = ecat.device[i].EL6001_rts_cts_enable ? 1 : 0;
> *if* (*ecrt_master_sdo_download*(ecat.master, i, 0x8000, 0x01, data, 
> 1,
> &abort_code) < 0)
> LOGMSG(/LOG_INFO/) << "Failed to upload rts cts enable SDO with code 
> "<< abort_code; }
>
>
>
>
>
> Here is my initialization sm which finishes successfully:
>
> // check the state of the initialization
> *if* (ecat.device[device].EL60xx_init_status == 
> /EL6021_Init_Terminal/){ // read the control register first and set 
> initialization request bit to 1
> *int* control_byte = EC_READ_U8(ecat.domain_pd + 
> ecat.device[device].EL60xx_control_offset);
> control_byte |= EL60XX_CTRL_INIT_REQUEST; EC_WRITE_U8(ecat.domain_pd + 
> ecat.device[device].EL60xx_control_offset,
> control_byte);
>
> // wait for verification that the initialization succeed successfully 
> ecat.device[device].EL60xx_init_status = /EL6021_Init_Accepted/; }
> *else**if* (ecat.device[device].EL60xx_init_status == 
> /EL6021_Init_Accepted/){ // read the status register to see if the 
> device accepted the request uint16_t status = 
> EC_READ_U16(ecat.domain_pd + 
> ecat.device[device].EL60xx_status_offset);
> if (status & EL60XX_STAT_INIT_ACCEPTED){ // clear the init request 
> bit...
> *int* control_byte = EC_READ_U8(ecat.domain_pd + 
> ecat.device[device].EL60xx_control_offset);
> control_byte &= ~EL60XX_CTRL_INIT_REQUEST; EC_WRITE_U8(ecat.domain_pd 
> + ecat.device[device].EL60xx_control_offset,
> control_byte);
>
> // wait for the transmission success
> ecat.device[device].EL60xx_init_status = /EL6021_Init_Verified/; }
> *else* {
> // waiting for initialization accepted...
> *if* (ecat.device[device].EL60xx_init_print){
> LOGMSG(/LOG_INFO/) << "Still waiting for verification of transmission 
> on EL60xx"; ecat.device[device].EL60xx_init_print = *false*; } } }
> *else**if* (ecat.device[device].EL60xx_init_status ==
> /EL6021_Init_Verified/) {
> // check the status bit and wait for terminal to set the 
> initialization accepted bit to 0 uint16_t status = 
> EC_READ_U16(ecat.domain_pd + 
> ecat.device[device].EL60xx_status_offset);
> *if* (!(status & EL60XX_STAT_INIT_ACCEPTED)){ // everything is up and 
> running!
> ecat.device[device].EL60xx_init_status = /EL6021_Terminal_Ready/; // 
> notify the user
> LOGMSG(/LOG_INFO/) << "EL60xx device read / write terminal ready for 
> data"; } }
>
>
> My write state sm to be working correctly as well since when I set the 
> transmit request bit after filling the data bytes, the terminal sets 
> the transmit request accepted bit successfully, I am just not seeing 
> data coming out the port. This is happening with both the EL6021 and the EL6001.
>
> This is how my write sm works right now (I just created a temporary 
> array of 8 bytes and filled it with random data, TEST_SIZE = 8):
>
> // get the status used for write and write sm uint16_t status = 
> EC_READ_U16(ecat.domain_pd + 
> ecat.device[device].EL60xx_status_offset);
>
> // check the write state
> *if*(ecat.device[device].EL60xx_send_status== /EL6021_Send_Idle/){ // 
> map the data to the output registers
> *for* (*int* i=0;i<TEST_SIZE;i++)
> EC_WRITE_U8(ecat.domain_pd + ecat.device[device].EL60xx_out_offset[i],
> data[i]);
>
> // set the second byte of the control register to be the size of the 
> output size // mask with 255...
> uint16_tcontrol_byte = (TEST_SIZE & 255) << 8;// bit shift over by 8 
> and mask out the first byte control_byte |= 
> EL60XX_CTRL_TRANSMIT_REQUEST;
>
> // set the transmit request bit
> EC_WRITE_U8(ecat.domain_pd + 
> ecat.device[device].EL60xx_control_offset,
> control_byte);
>
> // set next step in the transaction process 
> ecat.device[device].EL60xx_send_status= /EL6021_Send_Request/; } 
> *else**if*(ecat.device[device].EL60xx_send_status== 
> /EL6021_Send_Request/){ // check the status bit for successful transition...
> *if* (status & EL60XX_STAT_TRANSMIT_ACCEPTED){ // transmit accepted 
> and bytes sent to transmission FIFO
> LOGMSG(/LOG_INFO/) << "Data transmission from EL6021 success with 
> status "<< status;
>
> // set the status back to idle
> ecat.device[device].EL60xx_send_status= /EL6021_Send_Idle/; }
> *else* {
> // check for additional errors.
> .
> .
> }
> }
>
> The transmit accepted status bit is set high, so my assumption is that 
> the terminal is receiving the data (my log prints "Data transmission 
> from EL6021 success with status " every time through).
>
>
> _______________________________________________
> etherlab-users mailing list
> etherlab-users at etherlab.org
> http://lists.etherlab.org/mailman/listinfo/etherlab-users
>

Mit freundlichem Gruß

Richard Hacker

--
------------------------------------------------------------------------

Richard Hacker M.Sc.
richard.hacker at igh-essen.com
Tel.: +49 201 / 36014-16

Ingenieurgemeinschaft IgH
Gesellschaft für Ingenieurleistungen mbH Heinz-Bäcker-Str. 34
D-45356 Essen

Amtsgericht Essen HRB 11500
USt-Id.-Nr.: DE 174 626 722
Geschäftsführung:
- Dr.-Ing. T. Finke,
- Dr.-Ing. W. Hagemeister
Tel.: +49 201 / 360-14-0
http://www.igh-essen.com

------------------------------------------------------------------------
_______________________________________________
etherlab-users mailing list
etherlab-users at etherlab.org
http://lists.etherlab.org/mailman/listinfo/etherlab-users



More information about the Etherlab-users mailing list