[etherlab-users] AL States
Graeme Foot
Graeme.Foot at touchcut.com
Mon Jun 29 00:12:13 CEST 2020
Hi,
If you are using ecrt_master_state() the al_states parameter is filled in by all slaves with an OR operation. So for each bit that is set you can interpret that as at least one slave was in that state. If there is a state bit set you are not happy with (or expecting) then you will need to interrogate each slave individually to find out which slave(s) are in that state, using ecrt_slave_config_state().
On startup (or comms interruption and recovery) you can expect to see slaves at different stages on the way to OP mode. If you are fully operational and you have a PREOP bit set, then you likely have a device that is not known so is not configured, or has the wrong address so it is not being attached to correctly. If a slave stays in SAFEOP then you probably have a configuration error, check the logs to figure out the problem.
Regards,
Graeme.
From: etherlab-users <etherlab-users-bounces at etherlab.org> On Behalf Of BUSSIERES Vincent
Sent: Friday, 26 June 2020 9:25 PM
To: etherlab-users at etherlab.org
Subject: [etherlab-users] AL States
Hello,
I'd like to display AL state in my HMI.
AL states are :
* Bit0 : INIT
* Bit1 : PREOP
* Bit2 : SAFEOP
* Bit3 : OP
But when I read AL states, states are respetively :
* 0x02 (0010)
* 0x03 (0011)
* 0x0a (1010)
* 0x0e (1110)
* 0x0a (1010)
So, in some cases I don't know in which state I am ?
How can I determine AL State ?
Regards
Vincent BUSSIERES
Responsable Technique Logiciel
[1572337113342]
ZE Ma Campagne
36, Impasse Félix Nadar
16000 ANGOULEME
Tel: 33 (0)9.72.40.35.08
www.hemeria-group.com<https://webmail.nexeya.fr/owa/redir.aspx?C=GK_BqKCZef7LtPZnqnd_LGYr1NG9sz4Smy3iKIwO-pXqtJC7VgzXCA..&URL=http%3a%2f%2fwww.hemeria-group.com%2f>
P Afin de contribuer au respect de l'environnement, merci de n'imprimer ce courriel qu'en cas de nécessité.
Ce message et les fichiers pouvant être attachés sont confidentiels, réservés à l'usage unique des destinataires et n'engagent HEMERIA sous aucune forme que ce soit.
This email and any files transmitted with it are confidential, intented solely for the unique use of the recipients and don't commit HEMERIA.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20200628/93982b9f/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 5034 bytes
Desc: image001.png
URL: <http://lists.etherlab.org/pipermail/etherlab-users/attachments/20200628/93982b9f/attachment-0005.png>
More information about the Etherlab-users
mailing list